  #16  
Old 4/3/07, 10:02 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

I can't perceive a blessed thing wrong with this panel, other than the one white conductor on the breaker that's not re-identified. Furthermore, I see 19 branch breakers installed, and 20 grounds on the ground bar. That 6-3 NM that feeds the panel must be the 20th ground on the bar.
Reply With Quote
  #17  
Old 4/3/07, 10:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by Marc D. Shunk
Furthermore, I see 19 branch breakers installed, and 20 grounds on the ground bar. That 6-3 NM that feeds the panel must be the 20th ground on the bar.
Good catch. I didn't think that far ahead.
Reply With Quote
  #18  
Old 4/3/07, 10:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

Quote:
Originally Posted by wrosario
Why I would not recommend a ground to the panel, why I have ground connections to a bar where there is no connection to Ground. I'm not saying to install a ground Rod but if you can provide ground cable from previous panel will this won't work?
There's already a ground. It's with the cable that's feeding this panel.
Reply With Quote
  #19  
Old 4/3/07, 10:10 PM
William A. Rosario's Avatar
William A. Rosario William A. Rosario is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Bayamon, PR
Posts: 43
Default Re: Distribution panel question

Quote:
Originally Posted by Marc D. Shunk
There's already a ground. It's with the cable that's feeding this panel.
Saw it already, at least my note for the white cable was ok..

Thanks Marc, also to you Petey...
Reply With Quote
  #20  
Old 4/3/07, 10:52 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Distribution panel question

I get 19 breakers and 19 grounds.
Reply With Quote
  #21  
Old 4/5/07, 6:02 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 211
Default Re: Distribution panel question

Hey Folks, Our job is not to offer advice on how to repair a problem in the system but to report there is a problem in the system and recommend a sparky. What if you recommend a fix, Johnny home owner repairs it and the house burns down or someone gets fried! Does your insurance cover that?
Ralph
Reply With Quote
  #22  
Old 4/5/07, 7:51 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Distribution panel question

Ralph,

I believe the advice given here is for Educational Purposes Only to aid in training the HI to be better awae of the many electrical issues found in electrical enclosures. As with Code and Advice from Electricians on this board.....it is meant to educate not procreate...



Paul W. Abernathy
Reply With Quote
  #23  
Old 4/10/07, 11:04 AM
rstringer rstringer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Bucyrus, MO
Posts: 10
Default Re: Distribution panel question

What about the "Over bundle" matter. Would you write that in the report?
Thanks, Robert
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Panel question bgraham Electrical Inspections 3 4/4/07 6:30 PM
Wiring question in panel dmacy Electrical Inspections 23 2/14/07 11:27 AM
Service panel Question cpetty Electrical Inspections 4 1/24/07 9:36 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 9:24 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts