This was being used in a convention center in Orlando, Florida where coffee was $5.00 per cup in a room for the electrical systems.
I am not too sure yet but is this is a recognized method or listed for this use? Maybe someone can do some research and find out for us. Last edited by jtedesco1; 3/4/06 at 8:28 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I doubt you could make a fill violation, that is a pretty big enclosure for 6 devices and a dozen conductors but there is certainly a 110.3(B)
BTW assuming a 8ga 4 wire feed and six 12ga to the duplexes. I get 41.25 cu/in of fill. You only count the grounding conductors once, using the largest size. Devices count 2 x the largest connected conductor. 4 x 3 =12 (the #8 feeder, also picks up the grounds) 3 x 3 = 9 (the breakers, using worst case ) 6 x 2.25 = 13.5 (the wire to the Duplexes) 3 x 2.25 = 6.75 (the duplexes) Last edited by Greg Fretwell; 2/5/06 at 12:03 PM.. |
![]() |