Saw a main breaker today on inspection. 200 amp breaker labeled for 1/0-4/0 copper SEC. Is 1/0 copper sufficient for a 200 amp breaker? I've seen it twice now and both times I've deferred it to an electrician to evaluate. Now, I see this breaker saying its ok to use 1/0 on this 200 amp but was always told (and taught) that 1/0 is for 100 amp and 2/0 is for 200 amp. What's the story??
|
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
1/0 copper can be OK up to 175a using the residential main feeder rule 310.15(B)(6) but not 200, Good call.
I doubt you will ever see a 175a panel so 1/0 is effectively 150a |
|
#3
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
and both times, the panel had the "approved" sticker by the electrical inspector when the house was built. I was starting to doubt myself which is why I am trying to find this out.
|
|
#4
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here is a pic of the breaker
|
|
#5
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
How would the electrician go about fixing this problem? Do they replace the 1/0 SEC with 2/0 or replace part of it? Not sure how this would work. thanks
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Replace the SE or replace the breaker. The tradeoff is labor vs cost. The breaker may be over $100 depending on what panel it is.
|
|
#8
|
|||
|
|||
|
Scott, I read that breaker label as ONE 4/0 cable, I could be wrong I have been before.
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#9
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bruce,
I can see how you can see it like that but that's gotta be wrong cause there's no way they'd say that you gotta use only a 4/0 for a measly 200 amp breaker. |
|
#10
|
|||
|
|||
|
so that would be a #1 up to a 4/0
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#11
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
The information is for the terminal lugs, showing you what size conductors you can use in those terminals, along with the specified torque. It is not there as an indication of what wire size is acceptable for a 200 amp load, it is there to indicate what size wire is acceptable for those terminals. The correct wire size for the load is determined by referring to the applicable code.
Any electrician who would size conductors to this label is not really an electrician. Last edited by brian winkle; 4/19/07 at 9:58 PM.. |
|
#12
|
|||
|
|||
|
Quote:
Paul W. Abernathy |
|
#13
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have a 30 horse power 240 volt three phase motor.
Looking at Table 430.250 this motor is rated at 80 Full Load Amps. Looking at 430.22 a 125% factor must be applied to the Full Load Amps of this motor in order to size the branch circuit supplying this motor. 80 times 125% equals 100 amps for the conductor. Looking at Table 310.16 for a TW copper conductor for this motor I find that it will require at least a #1 AWG conductor. Table 430.52 gives 250% as the multiplier for an inverse time circuit breaker and this will look a little like this 80 X 250% = 200 amps. Now I have a 200 amp breaker that will have a #1AWG conductor and all is legal. Thus the listing for 1 through 4/0 on the terminals. |
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey Mike, how you been?
|
|
#15
|
|||
|
|||
|
Quote:
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| How to Make Money with Infrared seminar in Rye Brook, New York on December 5, 2007. | gromicko | Inspection Education & Training | 1 | 10/26/07 3:00 PM |
| NACHI and another national association make peace today with new agreement. | gromicko | Miscellaneous Discussion for Inspectors | 115 | 7/16/07 9:34 PM |