Saw a main breaker today on inspection. 200 amp breaker labeled for 1/0-4/0 copper SEC. Is 1/0 copper sufficient for a 200 amp breaker? I've seen it twice now and both times I've deferred it to an electrician to evaluate. Now, I see this breaker saying its ok to use 1/0 on this 200 amp but was always told (and taught) that 1/0 is for 100 amp and 2/0 is for 200 amp. What's the story??
Reply With Quote
  #2  
Old 4/18/07, 1:21 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

1/0 copper can be OK up to 175a using the residential main feeder rule 310.15(B)(6) but not 200, Good call.

I doubt you will ever see a 175a panel so 1/0 is effectively 150a
Reply With Quote
  #3  
Old 4/18/07, 1:28 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

and both times, the panel had the "approved" sticker by the electrical inspector when the house was built. I was starting to doubt myself which is why I am trying to find this out.
Reply With Quote
  #4  
Old 4/18/07, 1:36 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

Here is a pic of the breaker
Attached Thumbnails
do-you-make-irving-003.jpg  
Reply With Quote
  #5  
Old 4/18/07, 10:03 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

Quote:
Originally Posted by Scott Schultz
Saw a main breaker today on inspection. 200 amp breaker labeled for 1/0-4/0 copper SEC. Is 1/0 copper sufficient for a 200 amp breaker?
NO. 240.6 of the NEC list the size of overcurrent devices as outlined here
Quote:
(A) Fuses and Fixed-Trip Circuit Breakers. The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200,
Here we can see that a 175 is a standard size for a breaker. Using Table 310.16(B)(6) a 1/0 conductor can be used on a 175 amp service for a dwelling unit only. Being that 175 is a standard rating for an overcurrent device the rule outlined in 240.4(B) clearly states that a 175 must be used.

Quote:
Originally Posted by Scott Schultz
but was always told (and taught) that 1/0 is for 100 amp and 2/0 is for 200 amp. What's the story??
It would be better to look at 310.16(B)(6) as you can see that a 100 amp service can be supplied with a #4 copper or #2 aluminum conductor.
Reply With Quote
  #6  
Old 4/19/07, 11:19 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

How would the electrician go about fixing this problem? Do they replace the 1/0 SEC with 2/0 or replace part of it? Not sure how this would work. thanks
Reply With Quote
  #7  
Old 4/19/07, 2:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

Replace the SE or replace the breaker. The tradeoff is labor vs cost. The breaker may be over $100 depending on what panel it is.
Reply With Quote
  #8  
Old 4/19/07, 3:31 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: What do you make of this?

Scott, I read that breaker label as ONE 4/0 cable, I could be wrong I have been before.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #9  
Old 4/19/07, 5:32 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

Bruce,

I can see how you can see it like that but that's gotta be wrong cause there's no way they'd say that you gotta use only a 4/0 for a measly 200 amp breaker.
Reply With Quote
  #10  
Old 4/19/07, 7:36 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: What do you make of this?

so that would be a #1 up to a 4/0



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #11  
Old 4/19/07, 8:33 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

The information is for the terminal lugs, showing you what size conductors you can use in those terminals, along with the specified torque. It is not there as an indication of what wire size is acceptable for a 200 amp load, it is there to indicate what size wire is acceptable for those terminals. The correct wire size for the load is determined by referring to the applicable code.
Any electrician who would size conductors to this label is not really an electrician.

Last edited by brian winkle; 4/19/07 at 9:58 PM..
Reply With Quote
  #12  
Old 4/20/07, 9:14 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What do you make of this?

Quote:
Originally Posted by bgraham
Scott, I read that breaker label as ONE 4/0 cable, I could be wrong I have been before.
nope...it means....CU it will accept Size # 1 THRU 4/0 in AWG sizes of CU...not that it needs (1) 4/0......



Paul W. Abernathy
Reply With Quote
  #13  
Old 4/20/07, 2:00 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

I have a 30 horse power 240 volt three phase motor.

Looking at Table 430.250 this motor is rated at 80 Full Load Amps.

Looking at 430.22 a 125% factor must be applied to the Full Load Amps of this motor in order to size the branch circuit supplying this motor. 80 times 125% equals 100 amps for the conductor.

Looking at Table 310.16 for a TW copper conductor for this motor I find that it will require at least a #1 AWG conductor.

Table 430.52 gives 250% as the multiplier for an inverse time circuit breaker and this will look a little like this 80 X 250% = 200 amps.

Now I have a 200 amp breaker that will have a #1AWG conductor and all is legal.
Thus the listing for 1 through 4/0 on the terminals.
Reply With Quote
  #14  
Old 4/20/07, 2:43 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you make of this?

Hey Mike, how you been?
Reply With Quote
  #15  
Old 4/20/07, 5:55 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What do you make of this?

Quote:
Originally Posted by Mike Whitt
I have a 30 horse power 240 volt three phase motor.

Looking at Table 430.250 this motor is rated at 80 Full Load Amps.

Looking at 430.22 a 125% factor must be applied to the Full Load Amps of this motor in order to size the branch circuit supplying this motor. 80 times 125% equals 100 amps for the conductor.

Looking at Table 310.16 for a TW copper conductor for this motor I find that it will require at least a #1 AWG conductor.

Table 430.52 gives 250% as the multiplier for an inverse time circuit breaker and this will look a little like this 80 X 250% = 200 amps.

Now I have a 200 amp breaker that will have a #1AWG conductor and all is legal.
Thus the listing for 1 through 4/0 on the terminals.
lol.....very nice....but I hope these guys don't actually see a 30HP 3-phase motor in a normal dwelling anytime soon...tehehehe...



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to Make Money with Infrared seminar in Rye Brook, New York on December 5, 2007. gromicko Inspection Education & Training 1 10/26/07 3:00 PM
NACHI and another national association make peace today with new agreement. gromicko Miscellaneous Discussion for Inspectors 115 7/16/07 9:34 PM


All times are GMT -4. The time now is 8:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts