Default When do you say wiring should be protected?

I generally use a 7' rule (thinking that within 7' is more likely to be damaged by physical contact). If the wiring is within 7' of the floor, then I recommend concealing it in conduit or behind walls. The exception is attics. Comments welcome and appreciated.

do-you-say-wiring-should-protected-012109-056-800x600-.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 1/22/09, 12:08 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by jfunderburk View Post
I generally use a 7' rule (thinking that within 7' is more likely to be damaged by physical contact). If the wiring is within 7' of the floor, then I recommend concealing it in conduit or behind walls. The exception is attics. Comments welcome and appreciated.

Attachment 26380
Joe,

This appears to be a mechanical room, which is fine the way it is. As long as all wiring is secured to within 12 inches of panel. I only recommend conduit protection to exterior wiring that is susceptible to mechanical damage.
Reply With Quote
  #3  
Old 1/22/09, 12:09 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: When do you say wiring should be protected?

Correct me if I am wrong, but isn't that old cloth jacket Romex? If so it's been there for 40 years plus.

I may be odd man out, but I would recommend nothing in that case. (Other than identifying the Old wiring)



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 1/22/09, 12:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by bwiley View Post
Correct me if I am wrong, but isn't that old cloth jacket Romex? If so it's been there for 40 years plus.
. . . and a Federal Pacific panel to boot!!

This wiring does not qualify for "in-need-of-protection" in my book.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/22/09, 12:16 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: When do you say wiring should be protected?

Yeah Jeff, with breakers on in the down position too!!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #6  
Old 1/22/09, 12:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: When do you say wiring should be protected?

The room is a utility room. Also serves as a laundry room. Note the storage shelf in front of the wiring.

(Yes, a FPE panel. Good eye.)

Expand the question to unfinished garages, which I see quite often. Would you recommend protection there?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 1/22/09, 12:20 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by jfunderburk View Post
Expand the question to unfinished garages, which I see quite often. Would you recommend protection there?

Only if it is for fire protection on a firewall. Exposed wiring inside stud cavities in a garage are fine.
Reply With Quote
  #8  
Old 1/22/09, 12:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by dvalley View Post
Exposed wiring inside stud cavities in a garage are fine.
Agreed.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 1/22/09, 12:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by dvalley View Post
Only if it is for fire protection on a firewall. Exposed wiring inside stud cavities in a garage are fine.
Then why to builders put sheetrock above and below and beside the main panel but often neglect to protect the wiring elsewhere in the garage?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 1/22/09, 12:32 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: When do you say wiring should be protected?

I believe that this is an interpretation of Romex and other wiring requiring protection that is installed on the exterior of a finished wall.
In this case
, if the wall was finished, the wiring would be protected properly. I think we need to fall back to, should these utility room walls be protected for fire code etc.
I feel this rule is more towards installing electrical conductors outside of the finished wall in a habitable space (crawlspace, basement and attic would be excluded in some instances). Protection of electrical conductors within the proximity of the crawlspace and attic access areas is defined.
If there is something you see on site that could potentially damage this fragile electrical conductor, you are obliged to note that as a safety concern.
For example, Romex wiring to the garbage disposal under the kitchen sink which is an extremely high traffic area (because of the detergents and cleaning components generally stored there) which is highly susceptible to damage. Armor shielded cable is generally used here and also becomes damaged due to this high traffic and their sharp edges potentially damage Romex wiring inside
.
I think that this is a case-by-case interpretation of how the property is currently being used and will potentially be used by the buyer. If there is a "potential" issue, I would make note of that.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 1/22/09, 12:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by jfunderburk View Post
Then why to builders put sheetrock above and below and beside the main panel but often neglect to protect the wiring elsewhere in the garage?
Local code interpretation.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 1/22/09, 1:27 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: When do you say wiring should be protected?

Quote:
Originally Posted by jfunderburk View Post
I generally use a 7' rule (thinking that within 7' is more likely to be damaged by physical contact). If the wiring is within 7' of the floor, then I recommend concealing it in conduit or behind walls. The exception is attics. Comments welcome and appreciated.

Attachment 26380

Needs to be protected as shown. I report like you do on this one Joe
Reply With Quote
  #13  
Old 1/22/09, 9:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: When do you say wiring should be protected?

It survived this long in that same location without a blemish so there's no real reason to believe that it will need mechanical protection for the next 40 years unless the way that room is used changes substantially.
Reply With Quote
  #14  
Old 1/22/09, 10:11 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: When do you say wiring should be protected?

I am sure it is not all 40 years old. I am not sure how it performed in the past.
Reply With Quote
  #15  
Old 1/23/09, 12:27 AM
ebretheim ebretheim is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Minot, ND
Posts: 2
Send a message via MSN to ebretheim
Default Re: When do you say wiring should be protected?

Hey everybody, im breaking my post cherry here, so take it easy on me.

It looks like there is no connector in that black receptacle. a lot of the wires are not secured within 12".
Code summary in short is.... all romex should be strapped within 8" of the enclosure unless there is a mechanical clamp, then it has to be secured within 12".

The space in front of the panel has to be clear of obstructions for 36" in this case. (there are 4 exceptions)

If the wires that were bored through those holes were installed after Jan. of 2008 then there could only be 2 romex conductors ran through them.
(4 current carrying conductors have to be de-rated for ampacity if they are ran through a raceway, bored holes, etc. size of the hole or raceway plays a factor in that also)

Like blaine stated, any breakers, switches, etc. should not be energized in the down position. This helps prevent against a breaker falling down on its own (it happens). Some switches and breakers lose their "switching" strength over time and can fall in the on position.


The bored holes should not be within 1 1/4" of the edge of the stud. Which is clearly depicted on the third stud to the right of the panel.

Last but not least, make sure the breakers are labeled.

Ya, im not smart, I'm just a full time electrician. haha

All in all it looks like a real ****ty installation, I suspect the homeowner wired mostly all of this. I would hope most electricians would not cross wires, and strap them accordingly, just for aesthetics sake.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM