I am just bored and tring to start a new thread here for fun. Let me know what you think about this.

This circuit is runnung 2 bedrooms (ceiling fans w/light, and all outlets approx 8 ea. rm.), One bathroom (all lights, exhaust fan, and outlets), and the hall lights (3).

The contractor said that he did all the work (complete rehab) including all electric, and that this 30 yr. old home is currently up to code. This is just one of four of the splices in the attic.

What are your thoughts. Be nice!!!
Attached Images
File Type: jpg PB080083.JPG (49.9 KB, 81 views)



Timothy J. Lower
Lowers Home Inspection
Dayton, Ohio 45439
937-654-0068
NACHI08021112
Reply With Quote
  #2  
Old 11/8/08, 3:55 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,795
Dale Duffy .
Default Re: What do you think???

What exactly do you mean Tim, whether or not the splice should be in a junction box?......of course..!!

But the Bathroom should been on a separate circuit.
Reply With Quote
  #3  
Old 11/8/08, 4:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,358
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: What do you think???

Quote:
Originally Posted by dduffy View Post
What exactly do you mean Tim, whether or not the splice should be in a junction box?......of course..!!

But the Bathroom should been on a separate circuit.
Yup...
Reply With Quote
  #4  
Old 11/8/08, 4:08 PM
Dylan J. Bucknavich Dylan J. Bucknavich is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 565
Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful
Default Re: What do you think???

Correct me if I'm wrong gentlemen, but don't just the GFCI recep's need to A) either be on a separate circuit including all bathroom GFCI's, or B) tied in with everything for just one bathroom, including fans, lights, etc?



Dylan Bucknavich
Arizona Professional Home Inspection L.L.C.
www.AzProHomeInspection.com
Chandler, AZ
Nachi ID# 06020796
Council-Certified Residential Mold Inspector
Reply With Quote
  #5  
Old 11/8/08, 4:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,321
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: What do you think???

Quote:
Originally Posted by dbucknavich View Post
Correct me if I'm wrong gentlemen, but don't just the GFCI recep's need to A) either be on a separate circuit including all bathroom GFCI's, or B) tied in with everything for just one bathroom, including fans, lights, etc?
Yes



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #6  
Old 11/8/08, 4:14 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,321
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: What do you think???

Long but helpful

Question 4.
We have had confusion regarding 210.11(C)(3), Exception, and 210.23(A), Exception. Can a bath light/fan and other light fixture(s) be on the 20-A, GFCI receptacle circuit if it feeds only a single bath room? Is there anything else to know about 210.11 and 210.23? — B.S.

Answer 4. The question is being answered with the 2002 NEC as a guide document. The exact words of Section 210.11(C)(3), Exception, are as follows: "Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)."The base rule of 210.11, Branch Circuits Required, (C) Dwelling Units, (3) Bathroom Branch Circuits states, "In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s).
Such circuit shall have no other outlets. "Thus if you have a dwelling unit with three bathrooms on the same floor level or one or two other floor levels, you can take one 20-ampere branch circuit and feed the GFCI [210.8(A)(1)] protected receptacles in each one on that single circuit. But it is not to have any other outlet(s), meaning other than receptacles on it.With that said and under our first scenario you could have a receptacle in each of the three bathrooms or more in all three provided that you do not have any light outlets, fan units or other loads on that circuit. But what the exception, as was restated above, allows you to do if you choose and have enough branch circuit spaces available in the panelboard is to take one 20-ampere branch circuit to a bathroom; or if you have more than one bathroom in the dwelling, you can take a separate 20-ampere branch circuit to each bathroom location and then since it only serves that one room, you can have other outlets or have other equipment on that same circuit.

Perhaps now is a good time to review the definition of outlet per Article 100 which states: "Outlet. A point on the wiring system at which current is taken to supply utilization equipment." This could be a light or fan unit or combination of both or a smoke detector if you chose to put one in the bathroom area. Possibly even a motor to a hydromassage tub unit depending on its size. Remember under the exception, it stated, "to be supplied in accordance with" and we were directed to 210.23(A).
With 210.23 being Permissible Loads and (A), being 15- and 20-ampere Branch Circuits, the requirement then indicates "a 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2)." Then(A)(1) states that "The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating." (A)(2) follow with,
"The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied."Under (A)(1) and with a 20-ampere circuit at 80 percent, you cannot have a cord-and-plug-connected piece of utilization equipment with a load greater than 16 amperes. As well under (A)(2) the total fastened in place utilization equipment cannot exceed 50 percent of the branch circuit ampere rating; or with a 20-ampere circuit have more than 10 amperes supplying that fixed piece of equipment and have lights or cord-and-plug equipment on that same circuit. Oftentimes what we see are baths with a hydro-massage bathtub and a connection made to that circuit, which puts the motor at a single-phase 120-volt, 1/2-hp motor or smaller. If the hydromassage tub has a ¾-hp motor or larger, then a separate circuit would be required; and oftentimes the listing by the manufacturer or nationally recognized testing laboratory and its labeling may require a separate circuit and not allow it to be fed by the single 20-ampere circuit going to the bathroom.

In conclusion, the question as asked indicates "can a bath light/fan unit (fixed piece of utilization equipment, non-cord-and-plug connected utilization equipment) and other light fixtures be on a single 20-ampere GFCI circuit if it feeds only a single bathroom." The answer is yes provided the "bath light/fan unit" does not exceed the 50 percent requirement at 10 amperes on a 20-ampere branch circuit. The important thing to remember is that 210.11 addresses branch circuits required and (3) covers bathroom branch circuits. Whereas 210.23 addresses permissible loads and the two sections are cross-referenced. I am a firm believer in the more circuits the better and lightly load them because we all know that future electrical loads will be added and oftentimes are not planned for. — Ray Weber, CMP-3



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #7  
Old 11/8/08, 4:19 PM
Timothy J. Lower's Avatar
Timothy J. Lower Timothy J. Lower is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Kettering, OH
Posts: 159
Timothy J. Lower is generally well trusted
Default Re: What do you think???

Dale..I was just curious as to what one would say about what they found here and what they would tell their contractor who did the work. This was meant just for fun.



Timothy J. Lower
Lowers Home Inspection
Dayton, Ohio 45439
937-654-0068
NACHI08021112
Reply With Quote
  #8  
Old 11/8/08, 4:30 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,795
Dale Duffy .
Default Re: What do you think???

Quote:
Originally Posted by tlower View Post
Dale..I was just curious as to what one would say about what they found here and what they would tell their contractor who did the work. This was meant just for fun.
I would simply say the electrician needs to make repairs..
Reply With Quote
  #9  
Old 11/8/08, 4:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you think???

The worst part of that is the fact that when the stuff you can see is that bad, the stuff you can't see will be downright scary.
Reply With Quote
  #10  
Old 11/8/08, 4:56 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you think???

Ask Marc. We get to fix stuff like this done by "the contractor" all the time.

Other than the fact that we can make money off their mistakes, I can't stand "do it all" contractors!
Reply With Quote
  #11  
Old 11/8/08, 5:07 PM
Timothy J. Lower's Avatar
Timothy J. Lower Timothy J. Lower is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Kettering, OH
Posts: 159
Timothy J. Lower is generally well trusted
Default Re: What do you think???

I completly agree with you Mark....If only we could use a hammer during our inspections and get away with it. Maybe we can put this in as part of our inspection agreement.... All damage done to the property in order to observe any hidden damage, or issues that may cause concern to the inspector during the inspection is the sole responsibility of *buyers name*. *buyers name* will cover all cost of repairs and all other fees associated to repairing the damage ......



Timothy J. Lower
Lowers Home Inspection
Dayton, Ohio 45439
937-654-0068
NACHI08021112
Reply With Quote
  #12  
Old 11/8/08, 6:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you think???

Quote:
Originally Posted by Speedy Petey View Post
Ask Marc. We get to fix stuff like this done by "the contractor" all the time.

Other than the fact that we can make money off their mistakes, I can't stand "do it all" contractors!
Yes, indeed. It's hard for me to get too excited about pictures like this anymore. There comes a point in time when you see BS like this so often, you take it in stride. It's a shame, really. I have to pretend to be excited and worked up when I point out these hazards to a homeowner in their home, otherwise they'd think my calmness was an indication that it's not a big problem.

Yes, I hate the "do it all" contractors too. There's very darned few who do it all well. Most of them do it all half shod. A man's got to get sorted out what he's good at, and what he sucks at. Sub out the stuff you suck at. The sad thing is, I'm afraid, that a lot of these guys actually think they do good work when we know they don't.
Reply With Quote
  #13  
Old 11/8/08, 7:41 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: nord-est [ northeast] wisconsin
Posts: 125
Marc Benz is generally well trusted
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What do you think???

If this contractor did the work on the electrical system did he pull the permit with this mess ???

I am not suprised about the flying splices I ran into more than I care recall it.

Really a good contractor should double check all the works in the building to make sure everthing is legit per code requirement.

That kind of mess I done that all the time to fix other mess to get the code legit in correct manner.

Merci,Marc
Reply With Quote
  #14  
Old 11/8/08, 7:52 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,647
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: What do you think???

although this is probably redundant at this time i would simply state numerous electrical defects need repaired by qualified Electrician....simple as that



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #15  
Old 11/8/08, 8:43 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information