Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Do you trust your receptacle tester?

There was an interesting article in IAEI news this month about new ideas and marketing them but the thing that grabbed my attention was a couple ways a receptacle could have a fatal wiring flaw and still test OK or marginally OK with the typical tester.
One is a 2 wire system with a bootleg ground and reverese polarity . The box and any attached 3 wire equipment would be 120v above ground but the 3 light tester would be happy.
Number 2 is a 2 wire system with the ground pin pigtailed to an ungrounded box (or simply connected via the yoke) and a ground fault. The tester would simply show reverse polarity.

You can see how this could actually happen in one house.
The guy gets the reverse polarity in #2, he switches wires in #2 (that feeds #1 and now both test normal. He traded #2 fatal condition for #1.
Reply With Quote
  #2  
Old 2/2/06, 12:49 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Do you trust your receptacle tester?

Hi Greg,

which one

Regards

Gerry
Attached Thumbnails
do-you-trust-your-receptacle-tester-img_0302-small-.jpg.jpg
Views:	121
Size:	39.2 KB
ID:	971  



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 2/2/06, 1:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Do you trust your receptacle tester?

All of them will be tricked by these problems unless you use the adapter and a known good ground. That is the "idea" this guy is trying to develop, a tester that finds this problem.
Reply With Quote
  #4  
Old 2/2/06, 6:14 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Do you trust your receptacle tester?

Greg,

Is this part of the article you are speaking of...

In this case, however, the white wire was now energized at 120 V and thus the jumper wire energized all of the following at 120 V: the grounding terminals, the device mounting yoke, the wallplate screws, and all metal in contact. The black wire and terminal became the grounded circuit conductor and were connected to ground at the service.

The electrician tested the installation with a listed outlet circuit tester of the three-lamp type, and it indicated a correct installation. A plumber plugged a three-wire trouble light with metal lamp guard into the GFCI receptacle, crawled under the house to do plumbing, and was electrocuted by contact with the metal lamp guard.
It should be noted that the GFCI was doing its job. The GFCI function was being bypassed by the jumper.

As I investigated the accident, I was initially surprised that the outlet circuit tester showed that all was okay. As we look at the conditions and the construction of all of these three-wire circuit testers, we see that all listed, three-lamp outlet circuit testers would have shown that all was okay.

All of these testers have an indicating light between the hot and the grounded circuit conductor blades, that we will call light 1, a light between hot and the equipment grounding blades, that we will call light 2, and a light between the grounded circuit conductor and the equipment grounding blades, that we will call light 3 (see figures 1 and 2).

It doesn’t take a combination of a two-wire circuit, reversed polarity, and a jumper, intentional or unintentional, to cause serious unsafe signals from these testers. Let’s assume that a house has only two-wire circuits, correctly wired, black-to-black, and white-to-white. Section 406.3(D)(3) of NEC-2005 permits all the two-wire receptacles in the house to be replaced by three-wire receptacles, when protected by GFCIs and properly marked.

There are lots of scenarios, and I’m sure our inspectors can give us some others. At the Eastern Section meeting this year, I learned of a beaut. It seems that a small New England town with many nice decades-old Victorian homes built before equipment grounding conductors were required has most of its homes with two-wire branch circuits having reversed polarity.

The white wire is energized at 120 V and the black wire is the grounded circuit conductor! It turns out that the authority having jurisdiction (AHJ) way back then believed that the color white was more appropriate as the hot conductor and black was better as the grounded circuit conductor!



Paul W. Abernathy

Last edited by pabernathy; 2/2/06 at 6:22 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Would you use a floor system tester? dthomas2 Structural Inspections 24 12/23/06 12:20 PM
What kind of Outlet tester do you use? jwatts1 Electrical Inspections 23 11/13/06 11:45 PM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 3:39 PM