Two Prong ungrounded outlets. Second defect; Tester shows Hot and Neutral reversed. Thanks in advance!! George Russell George Russell Professional Inspections Austin,Texas TREC # 10215 512-296-9538 http://georgerussellprofessionalinspections.com/ http://www.facebook.com/austinhomeinspections |
| Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Two-prong ungrounded receptacles are not a defect.
Hot & neutral reversed should be stated as just that - or - simply state that the receptacle is improperly wired. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Ok not a defect. Do you mention them at all? Suggest upgrade?
George Russell George Russell Professional Inspections Austin,Texas TREC # 10215 512-296-9538 http://georgerussellprofessionalinspections.com/ http://www.facebook.com/austinhomeinspections |
|
#4
|
||||
|
||||
|
I will recommend upgrades only in areas where GFCI's are required today, or in locations where large appliances may be installed (i.e. refrigerators, washers, dryers, etc.).
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
I mention they are there. I do it more for the customer's general knowledge. They can leave them or have them replaced to make the outlets more convenient.
|
|
#6
|
||||
|
||||
|
Quote:
2) Receptacle showed reverse polarity. As far as recommending "upgrades", in most homes that I have inspected, and I am referring to the 2-prong receptacle issue, most times there are enough defects that it won't be an upgrade, it will be a repair done to the existing building code. |
|
#7
|
||||
|
||||
|
Maybe an FYI comment something like; The home is wired mostly with 2-prong ungrounded receptacles. While common years ago and still acceptable today, the lack of a grounding conductor will limit the use of certain appliances, computers, etc. that require a ground. Dedicated circuits may have to be run to properly and safely use such appliances. You may consider having a qualified licensed electrician evaluate the wiring if this is a concern to you. Robert Newland Tyrone, GA 30290 NACHI05101290 http://www.CertifiedHI.com http://www.HomeInspectorTyroneGa.com Home Inspection Reports Powered by: HomeGauge eServices |
|
#8
|
||||
|
||||
|
Quote:
Non-grounding type receptacles can be installed on an existing system as replacements to non-grounding type receptacles. There are no requirements to install grounding-type. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Quote:
Quote:
|
|
#10
|
||||
|
||||
|
Quote:
If you fail to mention the presence of 2-prong outlets, a client may be pretty upset with you once they move in. Better to give them an FYI upfront. Jeff is correct about their "legal" acceptability, but clients might not find them acceptable. Generally, whenever you do see 2-prong receptacles, you won't find as many outlets as is required by today's standards. I tell them that also as an FYI. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
That was my point. Current NEC allows two-prong receptacles to be replaced with two-prong receptacles.
There is no requirement that they be replaced with three-prong receptacles. In fact, to do so would be in violation of current requirements unless installed in accordance with NEC 406.3(D)(3)(a), (b) or (c) IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Quote:
It is why I re-quoted my entire quote, the whole paragraph, not one sentence from it. I'll say it again: Quote:
|
|
#13
|
||||
|
||||
|
So you're saying that most homes with two-prong receptacles will require re-wiring of the residence? I will have to disagree.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
| Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
Since you asked, out of the homes I have inspected that were built in the 50s and 40s, 3/4 of them did have to be re-wired. For numerous reasons. On one home, the homeowners decided to rewire everything themselves. When I checked a three-prong receptacle, it showed as an open ground. So did several others. I then pulled the dead front cover, which I usually do first, but no one could get into the garage until the end of the inspection, and there was all new Romex.......with every ground wire snipped off! Needless to say, no permit was pulled and when the city was called, they wanted everything opened up to see what was done. The house got rewired. On a majority of the other homes, the wiring in the attic had been damaged by rodents or something else, the homes had 100amp or less service, fuses, etc. and it was more feasible to re-wire the home. I am not saying, by any stretch of the imagination, that just because a home has two-prong receptacles, everything must be changed. However, I do mention to my Clients that there is the possibility that it may have to be rewired, someday. |
|
#15
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Unless it was a polarized receptacle, how did you determine reversed polarity on a 2 prong receptacle?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| No AFCIs for living areas...time to write it up? | jfunderburk | Electrical Inspections | 18 | 2/2/10 2:35 PM |
| Episode 53 - Home Inspector's Electrical Wall of Defects | inxil | NACHI.TV Inspection Videos | 62 | 11/21/08 8:30 PM |
| Defects as described by Lawyers | mcyr | Miscellaneous Discussion for Inspectors | 3 | 10/28/07 7:58 AM |