Default Documented under sized

Here is how I document undersized breakers and or circuits. Top right breaker is a 60 amp double pole at the meter base feeding a sub-panel in a basement IR image was taken right before the breaker tripped under load test. The breaker was varying its amp load 56 to 62 amps when it tripped I terminated the test and begin writing. I luv it when the Realtor is sitting in the house and the lights go out
Attached Thumbnails
documented-under-sized-1302-w-wabash-enid-7-11-11-025.jpg   documented-under-sized-1302-w-wabash-enid-7-11-11-102.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/11/11, 8:56 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Documented under sized

What's undersized?
Reply With Quote
  #3  
Old 7/11/11, 9:17 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by Robert Meier View Post
What's undersized?
The 60 amp breaker and more than likely the wire size feeding the sub-panel in the basement That had a 4 ton A/C unit electrical cook stove, dryer and all of the light circuits and some wall outlets all on one 60 amp breaker



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 7/11/11, 9:43 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Documented under sized

Quote:
Originally Posted by cbottger View Post
The 60 amp breaker and more than likely the wire size feeding the sub-panel in the basement That had a 4 ton A/C unit electrical cook stove, dryer and all of the light circuits and some wall outlets all on one 60 amp breaker

What do you mean "more than likely" the wire size? Its pretty cut and dry as to what size wire can be used where.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #5  
Old 7/11/11, 11:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by rhensel View Post
What do you mean "more than likely" the wire size? Its pretty cut and dry as to what size wire can be used where.
Just a ply of words I don't quote wire sizes I let the sparkys make that call. I like the words (appears to be)



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 7/12/11, 12:02 AM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Documented under sized

Quote:
Originally Posted by cbottger View Post
Here is how I document undersized breakers and or circuits. Top right breaker is a 60 amp double pole at the meter base feeding a sub-panel in a basement IR image was taken right before the breaker tripped under load test. The breaker was varying its amp load 56 to 62 amps when it tripped I terminated the test and begin writing. I luv it when the Realtor is sitting in the house and the lights go out
How did you load test this breaker?



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #7  
Old 7/12/11, 7:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Documented under sized

Quote:
Originally Posted by cbottger View Post
The 60 amp breaker and more than likely the wire size feeding the sub-panel in the basement That had a 4 ton A/C unit electrical cook stove, dryer and all of the light circuits and some wall outlets all on one 60 amp breaker

Ahh, so you're saying that based on the large load the 60 amp feeder is too small?
Reply With Quote
  #8  
Old 7/12/11, 8:01 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,185
Default Re: Documented under sized

So how did you report this? Did you report that the wire was undersized? What was your evaluation as a Level III thermographer?
Reply With Quote
  #9  
Old 7/12/11, 8:08 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by Robert Meier View Post
Ahh, so you're saying that based on the large load the 60 amp feeder is too small?
Yes sir that would be what I was implying being I had a 72 degrees above ambient on the wires, the amount of amp draw, the size of the breaker and the size of the wire. Call in the sparky and let them sort it out. BTW that 60 amp breaker was feeding the sub below
Attached Thumbnails
documented-under-sized-1302-w-wabash-enid-7-11-11-039.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 7/12/11, 8:14 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by dhays View Post
How did you load test this breaker?
I use all in house built in appliances all the light ceiling fans bathroom /kitchen exhausts and anything else available to create a load on the panels



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 7/12/11, 8:23 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by ldapkus1 View Post
So how did you report this? Did you report that the wire was undersized? What was your evaluation as a Level III thermographer?
Linas I had temps on both feeder conductors that was close to the same indicating no loose wires that the temp was created by excessive amp. I will just report What I observed and nothing more. I saw an excessive temp and I saw the breaker trip and that is what will be in the report let the sparky determine why.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 7/12/11, 8:25 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Documented under sized

Quote:
Originally Posted by cbottger View Post
Yes sir that would be what I was implying being I had a 72 degrees above ambient on the wires, the amount of amp draw, the size of the breaker and the size of the wire. Call in the sparky and let them sort it out. BTW that 60 amp breaker was feeding the sub below
That panel has some problems too, like the big green screw in the neutral bus.
Reply With Quote
  #13  
Old 7/12/11, 8:36 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Documented under sized

Quote:
Originally Posted by Robert Meier View Post
That panel has some problems too, like the big green screw in the neutral bus.
That is why the sparky is coming I had the feeling that Harry did his own wiring



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/12/11, 10:39 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Documented under sized

Quote:
Originally Posted by cbottger View Post
I use all in house built in appliances all the light ceiling fans bathroom /kitchen exhausts and anything else available to create a load on the panels
Comments:

(1) Was the wire rated for 90*C? That is 194*F....so the wire may be 44*F below its maximum operational temp. Being electrical, there probably is a good saftey factor in that temp.

(2) In electrical as in HVAC, the concept of diversity is used in designing codes, loads and demands. Is there even a slight chance that all the appliances, AC, bath fans, all the lights, vacuum will be on at the same time? For example, in our codes with a house with individual baseboard heaters, a circuit fed with #12 AWG can have 4,800 watts of heaters potentially drawing 20 amps at odd times but........ the code talks a lot about designing for 80% loading in many instances.

(3) In this case where you have no temperature difference on the 2 conductors probably indicating a balanced circuit/load distribution on both legs of the service, I may have done a demand/load calculation.....it may have met code requirements for sizing.
Reply With Quote
  #15  
Old 7/12/11, 12:49 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Documented under sized

Quote:
Originally Posted by Brian A. MacNeish View Post
Comments:

(1) Was the wire rated for 90*C? That is 194*F....so the wire may be 44*F below its maximum operational temp. Being electrical, there probably is a good saftey factor in that temp.

(2) In electrical as in HVAC, the concept of diversity is used in designing codes, loads and demands. Is there even a slight chance that all the appliances, AC, bath fans, all the lights, vacuum will be on at the same time? For example, in our codes with a house with individual baseboard heaters, a circuit fed with #12 AWG can have 4,800 watts of heaters potentially drawing 20 amps at odd times but........ the code talks a lot about designing for 80% loading in many instances.

(3) In this case where you have no temperature difference on the 2 conductors probably indicating a balanced circuit/load distribution on both legs of the service, I may have done a demand/load calculation.....it may have met code requirements for sizing.

It's possible that Charley's feeling about the feeder being too small are accurate but as Brain stated the only real way of knowing is to perform a load calculation.

I do find it surprising that in Canada you can run a 4800 watt heating load on a 20 amp, 240 volt circuit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
over sized wire rjude General Inspection Discussion 3 9/23/10 10:02 AM
Ever wonder if the conductor is sized properly? gheller Electrical Inspections 8 6/25/09 10:43 PM
I thought it was "thou shalt not steal" kpierce Miscellaneous Discussion for Inspectors 284 12/9/08 6:31 PM
New medium sized InterNACHI decals coming soon! lendza Miscellaneous Discussion for Inspectors 4 12/17/07 6:53 PM
4 Custom sized NACHI shirts available... lendza Miscellaneous Discussion for Inspectors 16 4/26/06 6:46 PM


All times are GMT -4. The time now is 8:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts