Here is how I document undersized breakers and or circuits. Top right breaker is a 60 amp double pole at the meter base feeding a sub-panel in a basement IR image was taken right before the breaker tripped under load test. The breaker was varying its amp load 56 to 62 amps when it tripped I terminated the test and begin writing. I luv it when the Realtor is sitting in the house and the lights go out
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
| Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
What's undersized?
|
|
#3
|
||||
|
||||
|
The 60 amp breaker and more than likely the wire size feeding the sub-panel in the basement That had a 4 ton A/C unit electrical cook stove, dryer and all of the light circuits and some wall outlets all on one 60 amp breaker
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#4
|
||||
|
||||
|
Quote:
What do you mean "more than likely" the wire size? Its pretty cut and dry as to what size wire can be used where. Comprehensive Building Consultants Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection. Donate here: or send checks to the Fl Home and Insurance Inspector Chapter 1103 W Hibiscus Blvd Ste 311 Melbourne, Fl 32901
|
|
#5
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#6
|
|||
|
|||
|
Quote:
David Hays All Points Home Inspections LLC Denver, CO 720-670-0366 allpointshomeinspect@yahoo.com www.allpointshomeinspections.org |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Ahh, so you're saying that based on the large load the 60 amp feeder is too small? |
|
#8
|
||||
|
||||
|
So how did you report this? Did you report that the wire was undersized? What was your evaluation as a Level III thermographer?
BPI Certified Professional Building Analyst BPI Certified Envelope Professional Infraspection Institute Certified Level II Thermographer # 8510 www.dapkusinspections.com www.chicagoinfraredthermalimaging.com www.mychicagohomeinspector.com www.commercialbuildinginspectionchicago.com Professional Infrared Network Chicago Energy Audit Aerial Infrared Inspection Certified Infrared Thermal Imaging |
|
#9
|
||||
|
||||
|
Yes sir that would be what I was implying being I had a 72 degrees above ambient on the wires, the amount of amp draw, the size of the breaker and the size of the wire. Call in the sparky and let them sort it out. BTW that 60 amp breaker was feeding the sub below
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#10
|
||||
|
||||
|
I use all in house built in appliances all the light ceiling fans bathroom /kitchen exhausts and anything else available to create a load on the panels
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#11
|
||||
|
||||
|
Linas I had temps on both feeder conductors that was close to the same indicating no loose wires that the temp was created by excessive amp. I will just report What I observed and nothing more. I saw an excessive temp and I saw the breaker trip and that is what will be in the report let the sparky determine why.
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
||||
|
||||
|
That is why the sparky is coming I had the feeling that Harry did his own wiring
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
| Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
(1) Was the wire rated for 90*C? That is 194*F....so the wire may be 44*F below its maximum operational temp. Being electrical, there probably is a good saftey factor in that temp. (2) In electrical as in HVAC, the concept of diversity is used in designing codes, loads and demands. Is there even a slight chance that all the appliances, AC, bath fans, all the lights, vacuum will be on at the same time? For example, in our codes with a house with individual baseboard heaters, a circuit fed with #12 AWG can have 4,800 watts of heaters potentially drawing 20 amps at odd times but........ the code talks a lot about designing for 80% loading in many instances. (3) In this case where you have no temperature difference on the 2 conductors probably indicating a balanced circuit/load distribution on both legs of the service, I may have done a demand/load calculation.....it may have met code requirements for sizing. |
|
#15
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
It's possible that Charley's feeling about the feeder being too small are accurate but as Brain stated the only real way of knowing is to perform a load calculation. I do find it surprising that in Canada you can run a 4800 watt heating load on a 20 amp, 240 volt circuit. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| over sized wire | rjude | General Inspection Discussion | 3 | 9/23/10 10:02 AM |
| Ever wonder if the conductor is sized properly? | gheller | Electrical Inspections | 8 | 6/25/09 10:43 PM |
| I thought it was "thou shalt not steal" | kpierce | Miscellaneous Discussion for Inspectors | 284 | 12/9/08 6:31 PM |
| New medium sized InterNACHI decals coming soon! | lendza | Miscellaneous Discussion for Inspectors | 4 | 12/17/07 6:53 PM |
| 4 Custom sized NACHI shirts available... | lendza | Miscellaneous Discussion for Inspectors | 16 | 4/26/06 6:46 PM |