This is a Cutler Hammer split bus panel. I couldn't see a panel bond, and the sticker on the panel was not readable. I suspect it is one of the two screws at the bottom of the bus. Can anyone confirm?
This split bus panel has two lower sections each fed by a 60 amp breaker in the upper section. I have only seen this once before, and that was last week. I did see the double tapped neutrals. |
|
#2
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Jeff,
I am not sure I understand. The panel must be bonded to the Neutral bus, right? Are you saying that it is OK for the grounding electrode or one of the grounding conductors to pull "double duty" and act as the panel bond? |
|
#4
|
||||
|
||||
|
Yes, but I'm not sure your reference to "double duty" fits.
If a conductor passes through a bonding lug (which is attached to the panel enclosure), and continues to the grounding electrode, it accomplishes the required bond. The bond can be made by several methods - screw, strap, conductor, etc. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
The neutral seems insulated, has me curious, is there a bigger photo?
tom |
|
#6
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
The grounded (neutral) must bond to the panel enclosure and the grounding electrode system at the main disconnect.
I think what he is asking is if the neutral is bonded to the enclosure and grounding electrode in this panel. No from what I can see but I can't see the entire inside of the panel so I can't say for sure that they are not bonded. |
|
#7
|
|||
|
|||
|
Here are some more photos of the panel
|
|
#8
|
||||
|
||||
|
I don't see a bond in those pictures. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Then where is the hole for it in the buss bar.?
|
|
#10
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
One of those screws in the Neutral/Ground bar may be a bonding screw----you would have to look at the panel diagram to see where it tells you to install the screw when needed.
|
|
#11
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is a main lug panel which tells me there is a service disconnect elsewhere.
If there is a disconnect elsewhere then there should be an equipment grounding conductor installed and the equipment grounding conductors for the branch circuits and the grounded (neutral) conductors should be kept separate. |
|
#12
|
||||
|
||||
|
Quote:
Must be the morning for split buses. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#13
|
||||
|
||||
|
I hope there is not a panel elsewhere because it appears the GEC's come into this panel, It is indeed a split buss panel and another give away is the USE coming into it ....either they ran USE into the interior of the dwelling and forgot it needs to have (4) conductors to the panel.....or someone just went plain LOCO on the install.......I would venture to say main panel, split buss design and SOMEWHERE in that picture bonding should take place....but my eyes wont allow me to see it......
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#14
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
I also white wires into the brakers and a groung and neutral wire under the same screw.
|
|
#15
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Panel bond | dmacy | Electrical Inspections | 12 | 10/19/06 11:19 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |