Default Does Anyone See A Panel Bond Here?

This is a Cutler Hammer split bus panel. I couldn't see a panel bond, and the sticker on the panel was not readable. I suspect it is one of the two screws at the bottom of the bus. Can anyone confirm?

This split bus panel has two lower sections each fed by a 60 amp breaker in the upper section. I have only seen this once before, and that was last week. I did see the double tapped neutrals.
Attached Thumbnails
does-anyone-see-panel-bond-here-p1030415.jpg   does-anyone-see-panel-bond-here-p1030416.jpg  
Reply With Quote
  #2  
Old 10/23/07, 10:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Does Anyone See A Panel Bond Here?

Quote:
Does Anyone See A Panel Bond Here?
Not at the terminal bar, but perhaps somewhere else. Many times there is a bonding lug attached to a conductor somewhere in the panel enclosure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/23/07, 10:40 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Does Anyone See A Panel Bond Here?

Jeff,

I am not sure I understand. The panel must be bonded to the Neutral bus, right? Are you saying that it is OK for the grounding electrode or one of the grounding conductors to pull "double duty" and act as the panel bond?
Reply With Quote
  #4  
Old 10/24/07, 12:14 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Does Anyone See A Panel Bond Here?

Yes, but I'm not sure your reference to "double duty" fits.

If a conductor passes through a bonding lug (which is attached to the panel enclosure), and continues to the grounding electrode, it accomplishes the required bond.

The bond can be made by several methods - screw, strap, conductor, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/24/07, 12:18 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Does Anyone See A Panel Bond Here?

The neutral seems insulated, has me curious, is there a bigger photo?

tom
Reply With Quote
  #6  
Old 10/24/07, 12:20 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

The grounded (neutral) must bond to the panel enclosure and the grounding electrode system at the main disconnect.

I think what he is asking is if the neutral is bonded to the enclosure and grounding electrode in this panel.

No from what I can see but I can't see the entire inside of the panel so I can't say for sure that they are not bonded.
Reply With Quote
  #7  
Old 10/24/07, 12:24 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Does Anyone See A Panel Bond Here?

Here are some more photos of the panel
Attached Thumbnails
does-anyone-see-panel-bond-here-p1030410.jpg   does-anyone-see-panel-bond-here-p1030411.jpg   does-anyone-see-panel-bond-here-p1030413.jpg   does-anyone-see-panel-bond-here-p1030412.jpg  
Reply With Quote
  #8  
Old 10/24/07, 12:27 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Does Anyone See A Panel Bond Here?

I don't see a bond in those pictures. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 10/24/07, 1:47 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

Then where is the hole for it in the buss bar.?
Reply With Quote
  #10  
Old 10/24/07, 2:08 AM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

One of those screws in the Neutral/Ground bar may be a bonding screw----you would have to look at the panel diagram to see where it tells you to install the screw when needed.
Reply With Quote
  #11  
Old 10/24/07, 10:12 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

This is a main lug panel which tells me there is a service disconnect elsewhere.

If there is a disconnect elsewhere then there should be an equipment grounding conductor installed and the equipment grounding conductors for the branch circuits and the grounded (neutral) conductors should be kept separate.
Reply With Quote
  #12  
Old 10/24/07, 10:36 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Does Anyone See A Panel Bond Here?

Quote:
Originally Posted by Mike Whitt
This is a main lug panel which tells me there is a service disconnect elsewhere.

If there is a disconnect elsewhere then there should be an equipment grounding conductor installed and the equipment grounding conductors for the branch circuits and the grounded (neutral) conductors should be kept separate.
Mike, that appears to be another split bus panel, with the lowest double breaker on the left side feeding the lower part of the buses (conection is visible) I also cannot see a panel bond there, but as Jeff said it may be somewhat hidden.

Must be the morning for split buses.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 10/24/07, 10:58 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Does Anyone See A Panel Bond Here?

I hope there is not a panel elsewhere because it appears the GEC's come into this panel, It is indeed a split buss panel and another give away is the USE coming into it ....either they ran USE into the interior of the dwelling and forgot it needs to have (4) conductors to the panel.....or someone just went plain LOCO on the install.......I would venture to say main panel, split buss design and SOMEWHERE in that picture bonding should take place....but my eyes wont allow me to see it......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 10/24/07, 11:22 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

I also white wires into the brakers and a groung and neutral wire under the same screw.
Reply With Quote
  #15  
Old 10/24/07, 12:40 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does Anyone See A Panel Bond Here?

Quote:
Originally Posted by gbeaumont
Mike, that appears to be another split bus panel,
Gerry
Yes you are right and a bond will be needed in this panel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Panel bond dmacy Electrical Inspections 12 10/19/06 11:19 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM