Had an interesting thing at this mornings inspection.
Tested an outlet that a working appliance was plugged into. However all three lights in my little tester were blank. Typically this means that there is no power at the outlet. But the appliance worked. I looked at the label on the tester and it indicated "open hot". Can anyone help me overcome my ignorance on this, and tell me what is going on? Thanks in advance. Mark Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
| Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Mark did you check which opening the hot conductor was on with your sniffer?
|
|
#3
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
try http://www.thecircuitdetective.com/insp.htm
and further http://www.thecircuitdetective.com/test.htm Were there other outlets like that or this the only one? |
|
#4
|
||||
|
||||
|
No I did not. Didn't think to try that. I wish I had.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#5
|
||||
|
||||
|
Quote:
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#6
|
||||
|
||||
|
My guess (guess)
would be that the voltage is reversed and the ground is neutral. (just a guess) |
|
#7
|
||||
|
||||
|
Quote:
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#8
|
||||
|
||||
|
Just reversed as in hot at the large slot rather than the small slot on the outlet.
But that would show on your tester and I was just thinking that maybe a complication would be if their was no real neutral. I may be way off as I am just trying to imagine what might throw off your three light tester. Only way to know for sure would be to go back and retest with a multimeter. |
|
#9
|
||||
|
||||
|
Quote:
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#10
|
||||
|
||||
|
Mark...you have something else going on there. If you look at the schematic for a 3-lite tester then you will see that all combinations are covered. In other words, no mater how you miswire an outlet at least one of the tester indicators will illuminate. Now, seeing as though none did yet the appliance (what was it?) worked then I would more suspect an intermittent or loose connection somewhere resulting in a high resistance condition on one or more of the legs. The neon bulbs in the tester need 60-80 volts to light up so if the loose connection/high resistance condition resulted in less voltage then the tester lights may not light up yet the appliance would 'somewhat' work. My guess...the Hot leg is loose but making contact.
Excellence in Inspections Mike Boyett, TREC #7290 mikeb@capcityinspections.com Capital City Inspections Austin, Texas (512) 577-2579 Company blog is: www.capcityinspections.com/blog |
|
#11
|
||||
|
||||
|
That's where I've been leaning. Might be a stab lock connection on the back of the receptacle.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#12
|
||||
|
||||
|
Quote:
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#13
|
||||
|
||||
|
Was it a switch controlled outlet?
Ian Niquette Square One Home Inspection Markesan WI 53946 www.squareonehomeinspection.com Active Rain Network INACHI Awards Portal Want To Exchange Links? What we've got here is......failure......to communicate.....
|
| Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
You say that the disposal worked fine...was this after you flipped the switch?? Hint, Hint, Hint. Were you testing the receptacle while the disposal was not running? Maybe you see where I'm going here.
Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#15
|
||||
|
||||
|
Yea I guess it was. Hadn't thought of that. Kind of stupid...