  #16  
Old 1/19/06, 10:52 AM
dgriffith dgriffith is offline
New User
 
Join Date: Jan 2005
Location: Akron, Oh
Posts: 72
Please Note: dgriffith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Doesn't look right part 2

Thank you to all for the input. I didnt think there was a problem with the loop but I did report all the other problems as well as a double tap that wasnt very clear in the pic. There was stranded aluminum in the other panel as well and the insulation was falling apart in that one. I thought it was a typical Joe home owner update but he said electrician did it.
Reply With Quote
  #17  
Old 1/19/06, 11:07 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Doesn't look right part 2

Stranded AL is generally okay. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #18  
Old 1/19/06, 11:24 AM
dgriffith dgriffith is offline
New User
 
Join Date: Jan 2005
Location: Akron, Oh
Posts: 72
Please Note: dgriffith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Doesn't look right part 2

Jeff, the only problem I cited with the AL is the worn insulation. I wish I had a better pic but the visibility and angle were bad. (There was maybe 1.5 feet of access between a shelf and the panels, which was reported as well).
Reply With Quote
  #19  
Old 1/19/06, 5:27 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Doesn't look right part 2

Will,

To sum this up......the picture is of a Bow-Tie style....while it is great for getting extra wire it is really a waste of space, and wire if you ask me. However, the loop itself will not cause any magnetic issues that should be worried about.

AS joe stated I believe....the only real concern in these cases is when the wire is bend to fit into the lugs at angles that exceed the requirement for cable itself in regards to bend radius.

I just happen to think bow-ties look nasty in a panel...but hey thats me.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspection Business Part Time (Seeking Advice) Shawn M. Nold General Inspection Discussion 32 9/16/07 11:58 AM
grounding on plumbing gmathias Electrical Inspections 7 8/17/07 2:22 PM
Environmental sensitivities part 2 - EMFs Caoimhín P. Connell Ancillary Inspection Services & Additional Topics 2 4/22/07 11:28 PM
hot neutral found on part of house inspection dmcauley Electrical Inspections 5 4/4/06 9:40 PM


All times are GMT -4. The time now is 8:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts