I recently found an 110V outlet wired directly into one leg for the AC disconnect. Correct me if I'm wrong but isn't the whole purpose of this outlet is to provide a service tech a power source when the AC is shut down. Also the circuit wire for the outlet is undersized and not GFI protected. Would removal of the 110V outlet be the correct recommendation?
|
| Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
I would certainly recommend removal, especially given the improper breaker rating for the wiring. Also, the narrower wire double-tapped with a thicker wire can come loose.
|
|
#3
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
www.MauiHomeInspections.com |
|
#4
|
||||
|
||||
|
also, there is no neutral (grounded conductor) from this panel to the sub/main.
"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#5
|
||||
|
||||
|
That is a dedicated circuit. There should be no additional outlets other than the condenser unit itself. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff - well put.
|
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
In that one photo there are several code violations.
No connector on the cable in the back. A receptacle box that is not rated for a wet location. More than one conductor under a lug. The incorrect tap to the receptacle. No GFCI protection. No wet location cover. Grounded and grounding conductors not separated. The feeder cable does contain a neutral otherwise it wouldn't have a red conductor.
|
|
#8
|
||||
|
||||
|
Quote:
I just nominated this defect here: http://www.nachi.org/forum/f19/best-...tml#post669723 Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#9
|
|||
|
|||
|
Jason,
So how is Harry doing? 1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main Panel vs Sub-Panel and main disconnect? | rbassett | Electrical Inspections | 11 | 10/24/09 6:16 PM |
| Double Tapping Main Lugs | tdomingues | Electrical Inspections | 1 | 8/19/09 11:33 PM |
| Electric Panel | dmozzillo | Electrical Inspections | 26 | 1/26/09 1:18 PM |
| Double lugged breakers? | dbook | Electrical Inspections | 7 | 4/30/08 12:35 AM |
| 100 Amp Meter, 200 Amp Disconnect | jweinberg | Electrical Inspections | 8 | 8/15/06 12:32 PM |