I recently found an 110V outlet wired directly into one leg for the AC disconnect. Correct me if I'm wrong but isn't the whole purpose of this outlet is to provide a service tech a power source when the AC is shut down. Also the circuit wire for the outlet is undersized and not GFI protected. Would removal of the 110V outlet be the correct recommendation?
Attached Thumbnails
double-ac-disconnect-dscn9623.jpg  
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/8/10, 12:06 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Double on AC disconnect

I would certainly recommend removal, especially given the improper breaker rating for the wiring. Also, the narrower wire double-tapped with a thicker wire can come loose.
Reply With Quote
  #3  
Old 7/8/10, 12:25 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double on AC disconnect

Quote:
Originally Posted by jmccormick View Post
Would removal of the 110V outlet be the correct recommendation?
yes.

www.MauiHomeInspections.com
Reply With Quote
  #4  
Old 7/8/10, 1:30 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Double on AC disconnect

also, there is no neutral (grounded conductor) from this panel to the sub/main.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 7/8/10, 3:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Double on AC disconnect

That is a dedicated circuit. There should be no additional outlets other than the condenser unit itself. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 7/8/10, 6:09 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double on AC disconnect

Jeff - well put.
Reply With Quote
  #7  
Old 7/8/10, 8:02 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double on AC disconnect

In that one photo there are several code violations.

No connector on the cable in the back.
A receptacle box that is not rated for a wet location.
More than one conductor under a lug.
The incorrect tap to the receptacle.
No GFCI protection.
No wet location cover.
Grounded and grounding conductors not separated.
The feeder cable does contain a neutral otherwise it wouldn't have a red conductor.

Reply With Quote
  #8  
Old 7/8/10, 9:36 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Double on AC disconnect

Quote:
Originally Posted by jmccormick View Post
I recently found an 110V outlet wired directly into one leg for the AC disconnect. Correct me if I'm wrong but isn't the whole purpose of this outlet is to provide a service tech a power source when the AC is shut down. Also the circuit wire for the outlet is undersized and not GFI protected. Would removal of the 110V outlet be the correct recommendation?
Great photo Jason!
I just nominated this defect here: http://www.nachi.org/forum/f19/best-...tml#post669723




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #9  
Old 7/9/10, 6:56 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Double on AC disconnect

Jason,
So how is Harry doing?



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
Double Tapping Main Lugs tdomingues Electrical Inspections 1 8/19/09 11:33 PM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Double lugged breakers? dbook Electrical Inspections 7 4/30/08 12:35 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 12:32 PM


All times are GMT -4. The time now is 8:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts