  #1  
Old 10/1/07, 11:12 AM
Ron E. Perkerewicz Ron E. Perkerewicz is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Bremerton, WA
Posts: 89
Default double GFCI protection

Is there a problem with there being two GFCI protected outlets on the same circuit ? the lower bathroom has a GFCI but it trips the one in the upper bathroom when tested. I have gotten mixed messages on this being a hazard or just a hassel for the owner.
Reply With Quote
  #2  
Old 10/1/07, 11:24 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: double GFCI protection

Sounds like a belt and suspenders solutions.

tom
Reply With Quote
  #3  
Old 10/1/07, 11:34 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

Quote:
Originally Posted by tdietrich1
Sounds like a belt and suspenders solutions.

tom
You are qoing to have to quit this type of response I have laughed until my side hurts.
Reply With Quote
  #4  
Old 10/1/07, 11:59 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: double GFCI protection

There is no hazard or "violation" with this type of redundancy, however, it may become a nuisance.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/1/07, 9:19 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

This is also an indication of electrical work performed by a non qualified individual.
Reply With Quote
  #6  
Old 10/2/07, 5:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

Quote:
Originally Posted by brian winkle
This is also an indication of electrical work performed by a non qualified individual.
Maybe so. I know I've done it accidently. Sometimes months and months can pass between the time I rough-in a home and when I go back for finsh. I've already forgotten that I jumped off the main bath GFCI to serve the receptacle in a powder room, and accidently install a GFCI both places.
Reply With Quote
  #7  
Old 10/2/07, 10:30 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

Quote:
Originally Posted by Marc D. Shunk
Maybe so. I know I've done it accidently. Sometimes months and months can pass between the time I rough-in a home and when I go back for finsh. I've already forgotten that I jumped off the main bath GFCI to serve the receptacle in a powder room, and accidently install a GFCI both places.
Marc, just for that reason, at rough in I take a couple short pieces of Romex skin, mark one "line" and the other "load". and slip them over the respective conductors. Then, at trim out, which can be MONTHS later as you know, there is no question on the gfci placement.
Reply With Quote
  #8  
Old 10/2/07, 10:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

Quote:
Originally Posted by brian winkle
Marc, just for that reason, at rough in I take a couple short pieces of Romex skin, mark one "line" and the other "load". and slip them over the respective conductors. Then, at trim out, which can be MONTHS later as you know, there is no question on the gfci placement.
Oh, I do that too, but if it's a dead end, there's no need. If it's a location where a GFCI would normally be, and it's a dead end, every now and again one will get installed. It's really not that big of a deal, but I catch them when I'm doing the hot check.
Reply With Quote
  #9  
Old 10/2/07, 11:05 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double GFCI protection

ah, I see where that could happen. I guess you could label them GFCI or NO GFCI, but then you'd have to teach your guys to read!
Reply With Quote
  #10  
Old 10/3/07, 12:38 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: double GFCI protection

I always listen for the click from another location just in case.
Reply With Quote
  #11  
Old 10/3/07, 9:28 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: double GFCI protection

Sometimes when I had a GFCI downstream of another GFCI, I would only get the local one to trip. The speed, and construction, isolated the fault and kept the upstream one working. As HI's you just have to report that it's protected(the circuit/receptacle), as an electrician/home owner I would want to fix it.

tom
Reply With Quote
  #12  
Old 10/9/07, 6:06 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: double GFCI protection

I find this occaisionally. I inform the client of the potential for confusion, but I don't call it out as a defect for repair. I also verbally inform them that a licensed electrician likely would not have done this.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
Double tapped GFCI breaker sspradling Electrical Inspections 6 12/9/06 10:51 AM
Double GFCI protection. dmacy Electrical Inspections 8 7/26/06 7:31 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM