Default Double GFCI protection.

The exetrior & bathroom GFCI are double protected at the main panel. The only problem I see is that the GFCI at the receptacle wont reset unless the one in the main panel is reset. Would you advise removing the double protection or would you explain to the client how to reset if they trip.

Also the dishwasher is on the kitchen GFCI circuit. Is this OK or will the dishwasher cause the GFCI to trip.

Would yoo advise a recently refurbished home to have all kitchen countertop receptacles be GFCI protected?

Thanks

Dave
Reply With Quote
  #2  
Old 7/24/06, 8:08 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Double GFCI protection.

I would recommend that the downstream GFCI be removed from the circuit.

As for the dishwasher, it depends on how the house was originally wired up. It would be very difficult to separate the dishwasher outlet from the countertop ones at this stage. At least, make sure that the GFCI is rated for the amperage of the dishwasher.

BTW, since most kitchen outlets are suppose to be 20 amp circuits, why does everyone wire them up with 15 amp receptacles? I've only seen two houses with 20 amp receptacles in the kitchen.

As for the refurbished kitchen, once again it depends on how the circuit was physically wired together.
Reply With Quote
  #3  
Old 7/24/06, 9:32 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double GFCI protection.

Quote:
BTW, since most kitchen outlets are suppose to be 20 amp circuits, why does everyone wire them up with 15 amp receptacles? I've only seen two houses with 20 amp receptacles in the kitchen.
15 Amp are cheaper, why does everyone do everything that makes you shake your head?
Reply With Quote
  #4  
Old 7/25/06, 1:49 AM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Double GFCI protection.

It the little dirty secrets of building a home that people don't know about that make me smile. Everyone thinks that a newly constructed house or remodel is done per code, etc. What a big joke.

As far as kitchen outlets, the weakest link in the circuit is suppose to be the circuit breaker, not the wiring or the receptacle.
Reply With Quote
  #5  
Old 7/25/06, 11:02 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double GFCI protection.

Since there are no kitchen appliances with NEMA 5-20 plugs, why put in 20a receptacles? The 5-15s are listed for 20 pass through.
Reply With Quote
  #6  
Old 7/25/06, 11:15 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Double GFCI protection.

Quote:
Originally Posted by Greg Fretwell
Since there are no kitchen appliances with NEMA 5-20 plugs, why put in 20a receptacles? The 5-15s are listed for 20 pass through.
Yes but from the other side of the discusion the manufacture can say why should we make appliances that require a 20 amp plug .
They do not have the receptacles in the home for these.
Some one has to start some where
.
Roy Cooke sr.
Reply With Quote
  #7  
Old 7/25/06, 12:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Double GFCI protection.

Quote:
Originally Posted by rcooke
Yes but from the other side of the discusion the manufacture can say why should we make appliances that require a 20 amp plug .
They do not have the receptacles in the home for these.
Some one has to start some where Roy Cooke sr.
This is permitted in the NEC.
IMHO, the need for 20 A circuits in the kitchen has more to do with multiple appliances being used at the same time.

Mfgs. don't like to use 20A plugs because they will sell fewer units and the simple fact that people will cut the 20 A plug off and replace it with a 15A one and then use it on a 15A circuit with the resulting overload. Guess who gets sued.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #8  
Old 7/26/06, 6:20 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double GFCI protection.

If you have an appliance with a 20 plug, then it most likely needs a 20 ampere dedicated circuit. 15 ampere plugs are acceptable since the appliance is limited to 1500w by other codes. And since the load is limited the receptacle will never see more than the 1500w per yoke.
The dishwasher should have been on it's own circuit and not part of the small appliance circuit.

Last edited by smcarthur; 7/26/06 at 6:24 AM..
Reply With Quote
  #9  
Old 7/26/06, 7:31 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Double GFCI protection.

The breaker and wire must be rated 20 amp.
No special plug is required.

No other device, appliance or lighting should be on the kitchen counter circuits.

Now, no one posted the age of house that I saw.
These things do not need upgrade if not required at initial construction.

I would advise the client how to reset or find the tripped device. Advise that two on one circuit is just a wast of money. One can be removed if desired.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
double GFCI protection rperkerewicz Electrical Inspections 11 10/9/07 6:06 PM
Double tapped GFCI breaker sspradling Electrical Inspections 6 12/9/06 10:51 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 2:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts