Default Double Lug on Ground bus and no crimp sleeves

Can someone confirm that the double conductors under the lugs on the ground bus are incorrect and that the twisted conductors should have a crimp sleeve and then one conductor only under the lug. With the number of available lugs I am not sure why the conductors were doubled. Photos are attached. Thanks

double-lug-ground-bus-and-no-crimp-sleeves-dsc03107.jpg

double-lug-ground-bus-and-no-crimp-sleeves-dsc03108.jpg

double-lug-ground-bus-and-no-crimp-sleeves-dsc03109.jpg
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/29/10, 9:33 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Lug on Ground bus and no crimp sleeves

Most ground busses are listed for use with multiple grounding conductors. Check the label inside the panel for sizes, materials. Stranded conductors do not need anything added before they are terminated in the buss.

Last edited by Jim Port; 4/29/10 at 11:35 PM..
Reply With Quote
  #3  
Old 4/29/10, 10:03 PM
Dale G. Ganfield Dale G. Ganfield is offline
InterNACHI Member
 
Join Date: Feb 2010
Posts: 2
Default Re: Double Lug on Ground bus and no crimp sleeves

Thanks. I looked at the label. (2) #14 on grounding bus allowed.
Reply With Quote
  #4  
Old 4/30/10, 8:40 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Double Lug on Ground bus and no crimp sleeves

Multiple ground conductors may be allowed, but is that the best practice? I think if there are open lugs, they should be used... there's no reason to double or triple up on conductors if there are open lugs.
I realize that is not for me to decide, and is not necessarily an issue to call out, but it does make me look harder for other shortcuts in the panel...



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #5  
Old 5/1/10, 10:57 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Lug on Ground bus and no crimp sleeves

I would not consider using a panel part as it was designed to be a shortcut. Leaving other buss holes open also allows for future circuits to be added without affecting any other part of the panel wiring. Heck, if this is a service panel the use of the auxullary ground bar would show extra effort and cost vs using the neutral buss for both grounded and grounding conductors.
Reply With Quote
  #6  
Old 5/2/10, 6:55 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Double Lug on Ground bus and no crimp sleeves

I found these today.
Attached Thumbnails
double-lug-ground-bus-and-no-crimp-sleeves-048.jpg   double-lug-ground-bus-and-no-crimp-sleeves-046.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #7  
Old 5/2/10, 7:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double Lug on Ground bus and no crimp sleeves

Quote:
Originally Posted by acox View Post
Multiple ground conductors may be allowed, but is that the best practice? I think if there are open lugs, they should be used... there's no reason to double or triple up on conductors if there are open lugs.
I realize that is not for me to decide, and is not necessarily an issue to call out, but it does make me look harder for other shortcuts in the panel...
Now why would you call it a short cut if the manufacturer allows the installation to be done. If Eaton Cutler Hammer has a panel tested that allowed multiple equipment grounding conductors to be terminated under a single screw of a UL approved terminal buss then why is it a short cut or a problem?

Again what one person may fine as a shortcut another finds as thrifty, all under the eye of perfectly compliant. As an inspector I try to leave personal preferences out of my inspection process and inspect to compliance.



Paul W. Abernathy
Reply With Quote
  #8  
Old 5/2/10, 7:02 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double Lug on Ground bus and no crimp sleeves

Quote:
Originally Posted by bhartley View Post
I found these today.
Now see....these are some GREAT examples of non-compliant installations and yet another reason why even meeting the minimum standards of the National Electrical Code are critical starting points.

Great Pics !



Paul W. Abernathy
Reply With Quote
  #9  
Old 5/3/10, 8:20 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double Lug on Ground bus and no crimp sleeves

Quote:
Originally Posted by pabernathy View Post
As an inspector I try to leave personal preferences out of my inspection process...
Good advice...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts