Question Double-lugged Square D breakers

I understand that some double-lugged SquareD breakers are allowed and that others are not. Can anyone tell me from looking at this picture if they are allowed on these breakers or not?
Attached Files
File Type: pdf DSCN0357.pdf (238.1 KB, 442 views)

Last edited by mmorgan; 11/9/06 at 8:29 PM..
Reply With Quote
  #2  
Old 11/9/06, 8:26 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Double-lugged Square D breakers

Quote:
Originally Posted by mmorgan
I understand that some double-lugged SquareD breakers are allowed and that others are not. Can anyone tell me from looking at this picture if they are allowed on these breakers or not?
yes these are ok for double taps if the wire is the same size. Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 11/9/06 at 8:32 PM..
Reply With Quote
  #3  
Old 11/9/06, 8:28 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-lugged Square D breakers

If it is a "set screw" tpe of connection it is a single wire.
If it has a "screw and plate" connector it can accept two.
Reply With Quote
  #4  
Old 11/9/06, 8:30 PM
mmorgan mmorgan is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Brownwood, TX
Posts: 196
Default Re: Double-lugged Square D breakers

The picture is now attached to my original post. Sorry guys.
Reply With Quote
  #5  
Old 11/9/06, 8:35 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double-lugged Square D breakers

This is what to look for:
Attached Thumbnails
double-lugged-square-d-breakers-twowirebreaker.jpg  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 11/9/06, 8:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double-lugged Square D breakers

post images not downloads......much easier and safer!



Paul W. Abernathy
Reply With Quote
  #7  
Old 11/9/06, 8:42 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-lugged Square D breakers

That was just a PDF. If you don't have Adobe you won't open it.
This is a JPG
Attached Thumbnails
double-lugged-square-d-breakers-squared.jpg  
Reply With Quote
  #8  
Old 11/9/06, 8:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double-lugged Square D breakers

just better to have pictures posted....rather than downloadable files is all I am sayin.



Paul W. Abernathy
Reply With Quote
  #9  
Old 11/10/06, 8:13 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Double-lugged Square D breakers

I agree with Paul. Pictures not large PDFs.
I just look for the saddle clamp under the screw.
Same size wires (as Roy said) and saddle clamp = OK
No clamp, no double tap.

As in Larry's picture above.

Square D has a breaker with a clamp like that. So does one other manufacturer, is it Cutler Hammer????
Reply With Quote
  #10  
Old 11/10/06, 11:31 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Double-lugged Square D breakers

Whether it is "allowed" to double tap or not isn't always the point.
The other concern is that the added circuit may overload the breaker, and cause it to trip regularly during normal use.
It always catches my attention when I find double taps no matter who makes the breaker. It often represents a homeowners attempt at electrical.
(...I have never seen double tapped breakers in new construction, and/ or remodeling where it was both performed by a licensed electrician, and it was inspected by the AHJ)
I personally prefer to see a duplex breaker replace the double tapped breaker.
Reply With Quote
  #11  
Old 11/10/06, 2:45 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-lugged Square D breakers

How can a double tap overload a breaker any worse than a single circuit? If so, where is the harm? The conductors are doubled too so the load will be split across two instead of one. 240.4(D) provides more than adequate overload protection.
Reply With Quote
  #12  
Old 11/10/06, 2:57 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-lugged Square D breakers

Quote:
Originally Posted by Greg Fretwell
How can a double tap overload a breaker any worse than a single circuit? If so, where is the harm? The conductors are doubled too so the load will be split across two instead of one. 240.4(D) provides more than adequate overload protection.
i believe harold was saying that when a 2nd circuit is added, it could potentially double the load, potentially causing the breaker to trip more often.

if the loads have been taken into consideration prior to installing the 2nd circuit, then it should be no problem.
Reply With Quote
  #13  
Old 11/10/06, 4:24 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double-lugged Square D breakers

I think what greg is saying is.....if the breaker trips at lets say at a certain point....it will do it regardless of what it connected to it.....granted it will have more load on it when it is doubled up.....but the breaker itself knows not what it does....just what it is supposed to do...lol....

and thats trip in an overload........

The bad part is like cc stated.......if the homeowner has taken into consideration the loads prior...and we all KNOW they do not.....they see an open space and WHAMO....add another circuit....lol



Paul W. Abernathy
Reply With Quote
  #14  
Old 11/11/06, 9:12 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Double-lugged Square D breakers

Quote:
Originally Posted by Greg Fretwell
How can a double tap overload a breaker any worse than a single circuit? If so, where is the harm? The conductors are doubled too so the load will be split across two instead of one. 240.4(D) provides more than adequate overload protection.
How can a double tap overload a breaker? I see homeowners do this all the time. There is a reason that certain appliances have a dedicated circuit. Tap into one of these circuits with another high draw appliance, and run them at the same time. How about an outlet for a window unit air conditioner on the microwave circuit? Just an example of the many possible combinations I can think of. I am sure there are better examples.

I don't have a problem with an electrician performing legitimate double taps on approved breakers. But I never see that in my area....it is always the weekend warrior trying their hand at electrical with no regard for what they are doing.

Sometimes it is a double tap on a 20 amp circuit breaker with 14 guage copper wiring, or better yet the installer was aware that the load was being increased on a 15 amp circuit, and so they install a 30 amp 120 vac breaker to serve two 15 amp conductors....brilliance


I guess I am just saying if you see a double tap...don't stop looking...there is often more to the picture.
Reply With Quote
  #15  
Old 11/12/06, 11:50 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Talking Re: Double-lugged Square D breakers

I think PDF files are great! I like them because there are so many things one can do with them, the file posted as a PDF file here is not a problem, but then when it is as large as this one

http://www.ul.com/regulators/2006WhiteBook.pdf

it could take some time, about 6 MB's for sure but worth the time spent and it will have the specific answers to the original question here, again I think that PDF full version files are the best for those who have the software which is free anyway.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Counterfeit Square D Breakers - Fire Hazard jmckenna1 Electrical Inspections 4 11/21/07 6:13 AM
Surge Suppressor Double Lugged fpapp Electrical Inspections 3 6/1/07 9:41 AM
Square D double taps abishop Electrical Inspections 3 10/29/06 9:01 AM
Double lugged neutrals lschmid Electrical Inspections 14 8/11/06 9:11 AM
Square D Files Lawsuit to Prevent Counterfeiting jtedesco1 Electrical Inspections 2 5/26/06 6:36 PM


All times are GMT -4. The time now is 8:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts