Old 9/15/09, 9:37 PM
nbhi's Avatar
nbhi nbhi is offline
Default Double main
The main is double tapped. The white hot is not properly marked. No bonding screw or strap. Is there other issues I might be missing.
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison
www.newbeginningshomeinspection.com
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
Old 9/15/09, 10:10 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
Default Re: Double main
Double taps of the neutrals. Only allowed one neutral under each lug.
David
InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Old 9/15/09, 10:11 PM
wsiegel wsiegel is offline
ground and neutrals under the same screw
Old 9/15/09, 10:13 PM
Dont know where the location of that box is, but the wires leaving the box should be protected.
Old 9/15/09, 10:37 PM
Bob Elliott's Avatar
Do not see much Romex but are there 3 bushings missing at bottom left of the panel?
Those blank looking breakers disturb me, so what size conductor and what is the amp on that top right double.?
Pretty obvious they had no room for a breaker to that sub-panel on the left as the reason why they doubletapped.
Old 9/16/09, 8:42 AM
Jim Port Jim Port is offline
Unmoderated Guest
Bob E,
The top right breakers are 2 single pole breakers.
At the bottom left of the panel the connectors look like Tomics, at least on the laptop screen.
Old 9/18/09, 12:05 AM
Jeff Rema's Avatar
Jeff Rema Jeff Rema is offline
Please Note: Jeff Rema is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is a split-bus main panel. I assume the meter is directly above and that is not a disconnect. If it is a disconnect then this should be set up as a sub-feed.
This panel requires 5 throws to shut off power.
The double tapped mains for the 2 phases are problems.
Neutrals and ground under the same terminal screw are problems.
Is there a panel bond for the neutral/ground bars?
Double Tapping Main Lugs tdomingues Electrical Inspections 1 8/19/09 11:33 PM
Double tap at main lugs gmathias Electrical Inspections 4 8/8/07 7:20 PM
Main panel double tap dmccauley Electrical Inspections 20 1/25/07 5:31 PM