Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information
Default Double Main Panel Question

Crouse Hinds
120/240 3 Wire Single Phase
208Y/120 3 Wire Single Phase

Type G Panel Board

My concern is large threads of aluminum wire braded together tied into the panel. Should I be worried? This house has two mains and no sub panels.




Bill Boerner
St. Louis,MO - Professional Home Inspector

STLhomeinspector.com
All of metro St. Louis including all surrounding Areas Customer Testimonials



Home Inspector Pro Software - A Professionals choice in software.
Reply With Quote
  #2  
Old 11/5/08, 8:02 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Main Panel Question

Quote:
Originally Posted by bboerner View Post
My concern is large threads of aluminum wire braded together tied into the panel. Should I be worried?
This is extremely vague. Can you explain a bit better what you mean, or better yet posts a pic?

I have a feeling you are describing SEU cable which is perfectly fine.
Reply With Quote
  #3  
Old 11/5/08, 11:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Double Main Panel Question

Two mains? What exactly do you mean by that? Is this a parallel service?



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #4  
Old 11/5/08, 4:05 PM
Billy F. Boerner's Avatar
Billy F. Boerner Billy F. Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Belleville, IL
Posts: 1,836
Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information
Default Re: Double Main Panel Question

Yes both are side by side and both have 2 120 SEC's coming into them and both have large aluminum braded strand wire coming through the same knockout as the SEC's. Each panel rates at 200AMPS max. Thanks for the help I really apprecaite it. I'll post pics soon. The house is 3862 sq ft.




Bill Boerner
St. Louis,MO - Professional Home Inspector

STLhomeinspector.com
All of metro St. Louis including all surrounding Areas Customer Testimonials



Home Inspector Pro Software - A Professionals choice in software.

Last edited by bboerner; 11/6/08 at 1:35 AM.
Reply With Quote
  #5  
Old 11/5/08, 4:33 PM
Billy F. Boerner's Avatar
Billy F. Boerner Billy F. Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Belleville, IL
Posts: 1,836
Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information
Default Re: Double Main Panel Question

Here's the panels I was talking about. Please let me know how you would report this... Thanks again!!
Attached Images
File Type: jpg inspections 040.jpg (128.4 KB, 69 views)
File Type: jpg inspections 041.jpg (126.3 KB, 65 views)




Bill Boerner
St. Louis,MO - Professional Home Inspector

STLhomeinspector.com
All of metro St. Louis including all surrounding Areas Customer Testimonials



Home Inspector Pro Software - A Professionals choice in software.
Reply With Quote
  #6  
Old 11/5/08, 4:52 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,577
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: Double Main Panel Question

Both pictures are of the same panel.



B.A. King Home Inspections, LLC
York, South Carolina
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
Reply With Quote
  #7  
Old 11/5/08, 5:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Double Main Panel Question

No problem with the neutral in the SEC. There's nothing wrong with having a parallel service.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #8  
Old 11/5/08, 5:56 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Main Panel Question

Yup, that's SEU cable and is typical.
Reply With Quote
  #9  
Old 11/6/08, 12:10 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 42
Joseph M. Whitt is generally well trusted
Default Re: Double Main Panel Question

Quote:
Originally Posted by bboerner View Post
Here's the panels I was talking about. Please let me know how you would report this... Thanks again!!
Always when in doubt defer to a lisenced electrician



Mike Whitt
Contractor/Instructor
Reply With Quote
  #10  
Old 11/6/08, 1:27 AM
Billy F. Boerner's Avatar
Billy F. Boerner Billy F. Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Belleville, IL
Posts: 1,836
Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information Billy F. Boerner is very trusted source of information
Default Re: Double Main Panel Question

Thanks again guys for the help everyone. I sure appreciate each and everyone of you. I didn't want to refer this one. I knew I was probably missing the obvious. I guess standing there looking at two identical panels (indeed Bruce ) just threw me for a min and started the question game in my head. Thanks again!




Bill Boerner
St. Louis,MO - Professional Home Inspector

STLhomeinspector.com
All of metro St. Louis including all surrounding Areas Customer Testimonials



Home Inspector Pro Software - A Professionals choice in software.
Reply With Quote
  #11  
Old 11/6/08, 9:39 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,152
Barry Adair .
Default Re: Double Main Panel Question

Billy,
This is what I'm seeing installed for parallel service when the POCO leaves the seal off or the meter has been tampered with
Attached Images
File Type: jpg DSC00022 (Small).JPG (55.1 KB, 40 views)
File Type: jpg DSC00024 (Small).JPG (46.4 KB, 44 views)



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif

Last edited by badair; 11/6/08 at 9:42 AM.
Reply With Quote
  #12  
Old 11/6/08, 11:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,889
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Main Panel Question

Dog-gone, those panels are low. Another legal but dumb install.
Reply With Quote
  #13  
Old 11/6/08, 11:28 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 42
Joseph M. Whitt is generally well trusted
Default Re: Double Main Panel Question

Quote:
Originally Posted by badair View Post
Billy,
This is what I'm seeing installed for parallel service when the POCO leaves the seal off or the meter has been tampered with
Barry

This is not a paralleled service although it gets call this all the time.

Paralleled means that it is connected at both ends and this does not connect on both ends.

This is a service that has two disconnects instead of one. We are allowed to have up to six disconnects to serve as one main.



Mike Whitt
Contractor/Instructor
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Main and Sub Panel gheller Electrical 10 9/25/08 10:22 PM
Outlet off of Main Panel? jlevy Electrical 2 8/5/08 6:18 PM
Main panel question, pic included dnasser Electrical 2 7/16/08 7:26 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 6:51 PM.


Popular Sections

: