Default double panels

The box on the left is grounded at the plumbing. The box on the right, there is no grounding what so ever. Is the grounding coming from the conduit that connects the panels?

Attachment 12492

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 9:42 AM..
Reply With Quote
  #2  
Old 6/21/07, 1:07 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double panels

Your website has something wrong with it ,and there may be some spy ware site in its place.
Reply With Quote
  #3  
Old 6/21/07, 5:51 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: double panels

Robert
Don't know what happened, but I change my signature and now its fixed.

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 6/21/07, 10:14 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: double panels

The panels are bonded at the meter bases. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 6/21/07, 2:23 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: double panels

Jeff
This is find then correct?

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 6/21/07, 3:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: double panels

Looks good from my house



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 6/22/07, 6:35 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double panels

The grounding of each service disconnect has to be brought into each service disconnecting means. One should not bring the GEC to one service disconnect and then leave the other without a GEC.
250.24(A)
Reply With Quote
  #8  
Old 6/22/07, 1:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double panels

Pierre, with all due respect you only need one ground at each "service".

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

In fact it does not need to enter the service disconnect enclosures at all. It could be up on the mast at the service point. A silly choice but legal. In the meter base is more common.

Last edited by Greg Fretwell; 6/22/07 at 1:08 PM..
Reply With Quote
  #9  
Old 6/23/07, 7:58 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: double panels

So Greg what you are saying is that, each panel needs to have its own ground? Meaning, ground rod and at the plumbing, correct?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 6/23/07, 12:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: double panels

Each "service" needs a grounding electrode system but you only have one service in your example. You can have up to six disconnects on a service but you only need one grounding electrode conductor. "made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means".

I suppose there are other intrepretations but you will need to explain them to me and rationalize the things in red above (on post .
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double Tap Questions jkogel Electrical Inspections 6 6/28/07 10:46 PM
Distribution panels bking Electrical Inspections 2 3/11/07 11:29 AM
Double Tap! wward Electrical Inspections 12 2/22/07 6:39 PM
Double Taps rwand1 Canadian Inspectors 30 3/29/06 8:16 PM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 7:31 PM


All times are GMT -4. The time now is 7:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts