Exclamation Double pole breaker, metal showing between sections

On inspection today, the exterior panel was an ITE, EQ Loadcenter. House is 27 years old.

The upper left double pole breaker shows metal between the two sections.

Is the breaker coming apart, or, is this part of a lockable breaker?

Thanks for all your help !!
Attached Thumbnails
double-pole-breaker-metal-showing-between-sections-100_8289a-small-2-.jpg (2).jpg
Views:	111
Size:	34.1 KB
ID:	14313  
Reply With Quote
  #2  
Old 9/6/07, 1:32 AM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Posts: 32
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double pole breaker, metal showing between sections

That is not a ITE breaker, its a Crouse-Hinds and that is handle locking device, and the only I-T-E breaker I see is the one on the upper right row, the rest are GE or Crouse-Hinds, I doubt you could find any paperwork that they are UL "Classified" in a I-T-E loadcenter.

BTW I-T-E is now Siemens, and Crouse - Hinds is now back to their original name Murray, also owned by Siemens, they dropped the Murray/Crouse-Hinds breakers and rebranded I-T-E breakers as Murray,but have seen no paperwork stating I-T-E / Siemens and Murray is interchangable, if anyone has something that says it's OK, I would like to know.
Reply With Quote
  #3  
Old 9/6/07, 1:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Double pole breaker, metal showing between sections

Well going beyond that...notice the breakers on the right ( GE to be more specific ) does not fit properly into the KO area for the breaker....causing the breakers to sit back into the enclosure.

When Cutler Hammer ( Eaton®) got the " Classified " breakers approved for use in ITE and other enclosures this was critical...to work in the panel it has to SEAT in the panel properly....

Just as a tip...if you see a breaker in an enclosure that is not fitting properly chances are it is not listed for installation in that enclosure...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Double pole breaker with one wire. abolt Electrical 5 5/1/07 2:47 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
Double Tapping a Circuit Breaker Skip Erwin Electrical 4 2/17/07 8:15 PM
Double tapped GFCI breaker sspradling Electrical 6 12/9/06 11:51 AM


All times are GMT -4. The time now is 5:37 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts