Default Double tap

It seems like this is a problem I see often. There are no more breakers and when the air conditioer is installed it is double tapped improperly to the main breaker.

This panel was improper covered, pointed screw a broken breaker.

My question is on the air conditioner panel. I only see 2 wires and this is a 220 circuit. Besides the obvious double tap is this also improper wired for a 220?

I need to buy some panel screws. It seems like there are a lot of improper screws being inserted and instead of inserting these back in I should put in some proper ones. How much does a box or bag of deadfront blunt ended screws cost?
Attached Thumbnails
double-tap-94107-047-small-.jpg.jpg
Views:	85
Size:	51.0 KB
ID:	10225   double-tap-94107-046-small-.jpg.jpg
Views:	68
Size:	37.8 KB
ID:	10226   double-tap-94107-049-small-.jpg.jpg
Views:	100
Size:	66.2 KB
ID:	10227   double-tap-94107-050-small-.jpg.jpg
Views:	99
Size:	55.8 KB
ID:	10228  
Reply With Quote
  #2  
Old 3/23/07, 4:01 PM
wward wward is offline
New User
 
Join Date: Nov 2004
Location: Tampa, FL
Posts: 77
Please Note: wward is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tap

is the AC box relying on the 2" nipple as a means of ground?
how is the unit being grounded?

I would not change the panel cover screws!

While you may be doing someone a favor, your opening a can of worms.
Reply With Quote
  #3  
Old 3/23/07, 4:56 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Double tap

Several issues. The ceiling grid blocks proper access. If the conduit is used as a grounding means it has to extend all the way to the AC disconnect. If it uses knockouts in panels that are concentric (factory prepunched for different sizes) all raceway terminations need grounding bushings on them. If there is sealtite going from the disconnect to the unit depending on circuit size it needs a ground wire running through it. If I remember right it is only rated for a 20 amp circuit w/o a ground wire. The double tap is legal if the lugs are rated for 2 wires. The 6 disconnecting means cannot be exceeded. The AC breaker should be ID with service disconnect also. The best thing to do is call it out. Let an electrician sort it out. There is too many issues that should be corrected. I also agree with Whitley, changing screws may open a can of worms. Best use the $2 and buy a can of worms and go FISHING.
Reply With Quote
  #4  
Old 3/23/07, 5:22 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Double tap

It appears to me that the AC breaker is being fed from a double tap on the incoming side of the main panel main breaker, so there is no overcurrent protection whatever for the wires feeding the AC breaker. As a double tap, the different wire sizes would be a problem.

Jim King
Reply With Quote
  #5  
Old 3/24/07, 4:49 PM
alarsen1's Avatar
alarsen1 alarsen1 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 232
Default Re: Double tap

Speaking of double taps, check this out... As a rule I call these out as each lug is designed for one conductor only, but this "appears" to have been professionally installed. Any comments from the electricians here?

double-tap-paul-126-small-.jpg.jpg
Views:	66
Size:	71.0 KB
ID:	10250 double-tap-paul-128-small-.jpg.jpg
Views:	53
Size:	45.4 KB
ID:	10251
Reply With Quote
  #6  
Old 3/24/07, 5:22 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: Double tap

Quote:
Originally Posted by alarsen1
Speaking of double taps, check this out... As a rule I call these out as each lug is designed for one conductor only, but this "appears" to have been professionally installed. Any comments from the electricians here?

Attachment 10250 Attachment 10251

I'm not an electricain, but I do not believe the NEC says no double taps...except when performed by a professional electrican.

Double tapped is double tapped no matter who does it...and can be considered unsafe.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 3/24/07, 5:26 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: Double tap

This past weekend, I found one the other way--definitely installed by an amateur, but very neat and properly done. However, there was no inspection sticker and I suggested the client check it out and require a permit, an inspection, and an approval. The Electrical Inspecttion Bureau would know of the situation before the house changed hands and would require compliance by the present owner.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double tapping question mroe Electrical 17 8/30/07 9:32 AM
Double Tap Questions jkogel Electrical 6 6/28/07 10:46 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
Doorbell transformer double tap bsmith Electrical 11 4/17/06 1:48 PM
Double Taps rwand1 Canadian Inspectors 30 3/29/06 8:16 PM


All times are GMT -4. The time now is 6:41 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts