Default Double tap at meter?

I know I posted something similar to this a while back, but anyway, here goes again. Main house panel 100 amps and detached garage panel also with 100 amp panel which also had a main breaker and was not wired up like a distribution panel. The house panel did not have breaker and/or any wiring to feed garage panel. So this means they obviously double tapped meter socket, no? They're normally not double lugged, right? I'm assuming this is incorrect. 1959 house that was flipped. House panel was updated/newer and the garage panel was older (20+).
Attached Thumbnails
double-tap-meter-20721-buckskin-defiance-043.jpg  
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/12/11, 9:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tap at meter?

There's only one conduit coming out the bottom of the meter so where can this tap actually be?
Reply With Quote
  #3  
Old 5/12/11, 9:07 PM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Double tap at meter?

That's what I'm asking.
Reply With Quote
  #4  
Old 5/12/11, 10:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Double tap at meter?

Any pictures of the interior of the service panel?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 5/12/11, 11:52 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Double tap at meter?

Maybe the garage is feeding the house panel !



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #6  
Old 5/13/11, 12:42 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Double tap at meter?

If I really wanted to know badly enough I might accidentally trip the main breaker in the house.
Interesting panel behind that meter though.
Reply With Quote
  #7  
Old 5/13/11, 4:24 AM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Double tap at meter?

First pic house panel installed on adjacent wall from meter (50 amp breaker on left is stove). Second pic garage panel (didn't have a good interior pic).
Attached Thumbnails
double-tap-meter-20721-buckskin-defiance-068.jpg   double-tap-meter-20721-buckskin-defiance-035.jpg  
Reply With Quote
  #8  
Old 5/13/11, 7:10 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tap at meter?

The painter did a nice job of making everything off-white.
Reply With Quote
  #9  
Old 5/13/11, 8:40 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Double tap at meter?

Something is definitely wrong. If there are 2 main panels, the one in the detached garage being one of them, then the garage panel should have a main breaker or be no more than 6 throws to turn off the power there. Otherwise, if the garage is wired as a distribution panel and not a service entrance panel, there there should be a feeder at the house main panel with OCP.

Regardless, there should be a grounding electrode at the detached building. Was there?

It appears service comes into the meter from the mast head, goes through the wall to one panel, and underground to the detached building. That would be 2 main panels and if so, then there is a problem with the detached building panel's lack of a main breaker.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 5/13/11, 9:35 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tap at meter?

Quote:
Originally Posted by jfunderburk View Post
It appears service comes into the meter from the mast head, goes through the wall to one panel, and underground to the detached building. That would be 2 main panels and if so, then there is a problem with the detached building panel's lack of a main breaker.
If this is the case, another issue would be that the services are not grouped as required.
Reply With Quote
  #11  
Old 5/13/11, 9:37 AM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Double tap at meter?

Quote:
Originally Posted by jfrederick View Post
detached garage panel also with 100 amp panel which also had a main breaker and was not wired up like a distribution panel
It did have a main breaker. What do you mean "grouped"?
Reply With Quote
  #12  
Old 5/13/11, 9:47 AM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Double tap at meter?

Since the garage panel has a main breaker, is this set up acceptable? How would you report?
Reply With Quote
  #13  
Old 5/13/11, 10:29 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tap at meter?

Grouped as in co-located or next to each other. For this case there would be a means of disconnect either outside near the meter or the house panel with a main breaker and a disconnect next to that for the garage.
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/13/11, 10:40 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Double tap at meter?

Quote:
Originally Posted by jfrederick View Post
Since the garage panel has a main breaker, is this set up acceptable? How would you report?
Was there a GES at the garage? If not, it's wrong. You don't have to detail every single issue. Point out the concerns and refer it to a competent, licensed sparky.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 5/13/11, 11:01 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Double tap at meter?

How did you determine that the garage panel was not fed from the service panel?

The garage panel has its own disconnect - this is required and proper. The garage panel should also include a grounding electrode (as a detached building) as Joe mentioned. In addition, the garage panel should include a 4-wire feed (H+H+N+G). Grounds and neutrals should be separated, neutrals isolated. The exception would be a 3-wire feed with no other conductive connections between buildings. It's beyond the scope of the HI to determine that.

The service equipment looks fine (except for the paint) and there appears to be at least one 240V circuit, capable of feeding the garage panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
gas meter dyoung General Inspection Discussion 20 3/1/10 3:25 PM
Gas Meter dyoung AskNACHI.org Inspection Questions Forum 7 2/25/10 9:06 PM
CPSC -----> Recall on electric meter panels pbolliger Electrical Inspections 0 10/15/09 11:23 PM
Double tap on Meter ehyde Electrical Inspections 7 1/12/08 2:52 PM


All times are GMT -4. The time now is 8:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts