Hello gurus and mini-gurus. I would like specifics on "allowable" double-tapping. If the breaker is Square D, CH, or other approved by the manufacturer for double tap, I think the gauge must still be the same for each conductor AND each conductor must be in its own slot, that is, one on each side of the screw, is this right?
In a case of double tapping not permitted, is it a permissable repair to join the two conductors to a short pigtail with a wire nut in the service panel, so that the pigtail goes to the breaker? If that is OK, provided the total load is still acceptable for the breaker size, double taps are not that serious of a defect in terms of repair, right? |
Yes, they should be the same size conductor. CH doesn't have individual "slots" but Square D does.
Yes, you can splice two circuits to one conductor to eliminate the "double tap." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
Matthew Hopkins is a non-member guest and is in no way affiliated with InterNACHI or its members.
On the double tap question, can you double tap a fuse as in this picture?
This also seems to be a fused neutral, is this what they would typically look like were I to find more? |
I don't see a fused neutral. The two conductors coming in from the top are fused. There's no way to determine if one of those is a neutral, but I'm assuming they're both hot.
The white and black conductors (that come up from the bottom and attach to the terminals above the fuses) are what I call a "direct tap" - meaning, they have no overcurrent protection. You could open the switch and remove the fuses, and those conductors would remain hot. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
Does anyone ever call out the fact that some of these boxes are old and should just plain be replaced? These things were not made to last forever. After all, our country survives on built in obselence. At what point do we call for replacement.
| Double Tap Question | ekartal6 | Electrical Inspections | 6 | 10/22/07 8:30 AM |
| Some good questions that always need answers | jtedesco1 | Electrical Inspections | 5 | 6/16/06 10:10 PM |
| 2 Questions for The Price of One | psmothers | Electrical Inspections | 16 | 5/6/06 11:22 PM |
| Double Taps | rwand1 | Canadian Inspectors | 30 | 3/29/06 8:16 PM |