#1
|
|||
|
|||
|
Hey everybody.
I did an inspection last week and found a 20a breaker that goes to god knows what since it wasn't labeled. It also was double tapped to feed a 2 amp motor for an awning. I called it out and now the agent called me back and said that he talked to the company and that they said they do it that way all the time. I told him that it was wrong and that they need to have a licensed electrician fix it or give it the OK. I am just looking for info in this and how best to handle it. If anybody has a code it would be great. By the way he said that he would have the awning company call me they haven't yet (shocking). Thanks Mark Last edited by mpeterson; 4/4/07 at 9:06 PM.. |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I sorta thought the word was out now that there are several brands of breakers, particularly in the 15 and 20 amp sizes, that can be compliantly double-tapped. What brand and model are we dealing with here?
|
|
#3
|
|||
|
|||
|
Here is a pic it was a 20a breaker the one in the middle tell me what you think
Thanks |
|
#4
|
|||
|
|||
|
This is a type that accepts 2 wires:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Am I seeing two wires on that breaker or not?
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Its hard to tell in the pic but there is another wire directly under the top one
|
|
#8
|
||||
|
||||
|
Quote:
![]() Then you've got a double tap that needs to be separated. I stopped calling out the low voltage wiring such as doorbell transformers because every panel I run into have these double tapped. |
|
#9
|
||||
|
||||
|
Please Note:
cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Larry's right on with his pic.
If the breaker in question is rated for 2 wires, it's tapped incorrectly anyway. Wires should be side by side under the terminal, not on top of each other. The flared ends of the terminal are designed to hold the wires individually. I believe some Square D and Cutler Hammer breakers are rated for this??? Can't tell what this one is. Funny that the agent thinks it's ok cause the "awning guy" says so. You were right for calling it out, even if it was rated for the double tap. |
|
#10
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Those Siemens Q series breakers have a captured square washer, with a wire niche on each side of the screw. I've never been able to find anything official from Siemens, or on the breaker, that actually confirms you can double tap a QP breaker. I know the ITE's that proceeded them, you couldn't, but they had a slightly different terminal design. I almost never run across Siemens resi equipment in my area, so I never puzzled on it before. Siemens is mostly heavy industrial stuff.
|
|
#11
|
|||
|
|||
|
I just talked to the buyers in this case and told them to have the owner get it inspected and certified by an electrician then I further told him that because the awning company says its OK to have them pay for the electrician. The awning company says it is their standard operation procedure. Can you believe that every house they put an awning on they do this
|
|
#12
|
||||
|
||||
|
I am only aware of (2) models that activly allow multiple conductors at this time....Square D QO and Cutler Hammer CH models......
It will say it right on the side of the breaker if it allows this application. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#13
|
||||
|
||||
|
Quote:
|
|
#14
|
|||
|
|||
|
no the conductors are the same size
|
|
#15
|
|||
|
|||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double pole breaker, metal showing between sections | lfoster | Electrical Inspections | 2 | 9/6/07 1:25 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 10:04 AM |
| Double Tapping a Circuit Breaker | Skip Erwin | Electrical Inspections | 4 | 2/17/07 8:15 PM |
| Double tapped GFCI breaker | sspradling | Electrical Inspections | 6 | 12/9/06 11:51 AM |