  #1  
Old 4/18/07, 5:28 PM
tjohnson3 tjohnson3 is offline
InterNACHI Member
 
Join Date: May 2005
Location: Simpsonville, SC
Posts: 5
Default Double Tapped Breaker

I wrote up a double tapped breaker the seller call an electrician to correct the breaker. What he did was to take the extra wire off the breaker and splice it back to the wire that was left on the breaker. I still called this a double tapped breaker. Where can I find a code to back me up or am I wrong?


Thanks


Toby Johnson
South Carolina
Reply With Quote
  #2  
Old 4/18/07, 5:38 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: Double Tapped Breaker

You can find the code in the NEC.
The Elecrician is correct



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 4/18/07, 6:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker

Quote:
Originally Posted by tjohnson3
What he did was to take the extra wire off the breaker and splice it back to the wire that was left on the breaker.
That is a textbook repair of a double-tapped breaker. It's also known as "pigtailing". It is absolutely proper.
Reply With Quote
  #4  
Old 4/18/07, 6:35 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Double Tapped Breaker

Toby,

What the electrician did was create a pigtail from the (2) circuits that were sharing that breaker...and now simply have a single conductor going to the breaker now to remove the double tap issue.

Now....sure it does not remove the fact this breaker is controling (2) different circuits ( as it did before )...or (1) larger one now........but regardless of that nothing against that in the NEC.....the NEC does not tell you DIRECTLY how many things can be on a given circuit......while it gives us guidelines and so on and we can do the MATH to come to a conclussion.....

What the Electrician did was compliant.....

Oh...I wanted to add this.....in case you all see this be sure that the pigtail itself is equal or exceeds the rating of the conductors it is pigtailed too.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 4/18/07 at 6:38 PM..
Reply With Quote
  #5  
Old 4/18/07, 6:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Double Tapped Breaker

Sorry marc......I was typing while you were answering....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 4/18/07, 6:38 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker

Quote:
Originally Posted by pabernathy
Sorry marc......I was typing while you were answering....
No worries. I certainly don't mind explaining things to people 12 different ways, as long as one gets through. The more, the merrier.
Reply With Quote
  #7  
Old 4/18/07, 6:46 PM
tjohnson3 tjohnson3 is offline
InterNACHI Member
 
Join Date: May 2005
Location: Simpsonville, SC
Posts: 5
Default Re: Double Tapped Breaker

Thanks Paul and Marc,

I knew you could do this if the wires were cut short but not with two different circuits. I'm glad you got back to me before I put my foot in my mouth.

Thanks,


Toby
Reply With Quote
  #8  
Old 4/18/07, 7:45 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: Double Tapped Breaker

Quote:
Originally Posted by bkelly2
You can find the code in the NEC.
The Elecrician is correct
I guess he wanted a wordier response.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #9  
Old 4/20/07, 10:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Double Tapped Breaker

Quote:
Originally Posted by bkelly2
I guess he wanted a wordier response.

and YOU know I am
Quote:
WORDIER
in nature.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double pole breaker, metal showing between sections lfoster Electrical 2 9/6/07 1:25 PM
Double pole breaker with one wire. abolt Electrical 5 5/1/07 2:47 PM
Double Tapping a Circuit Breaker Skip Erwin Electrical 4 2/17/07 8:15 PM
Double tapped GFCI breaker sspradling Electrical 6 12/9/06 11:51 AM


All times are GMT -4. The time now is 7:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts