  #1  
Old 4/18/07, 5:28 PM
tjohnson3 tjohnson3 is offline
InterNACHI Member
 
Join Date: May 2005
Location: Simpsonville, SC
Posts: 5
Default Double Tapped Breaker

I wrote up a double tapped breaker the seller call an electrician to correct the breaker. What he did was to take the extra wire off the breaker and splice it back to the wire that was left on the breaker. I still called this a double tapped breaker. Where can I find a code to back me up or am I wrong?


Thanks


Toby Johnson
South Carolina
Reply With Quote
  #2  
Old 4/18/07, 5:38 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Double Tapped Breaker

You can find the code in the NEC.
The Elecrician is correct
Reply With Quote
  #3  
Old 4/18/07, 6:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker

Quote:
Originally Posted by tjohnson3
What he did was to take the extra wire off the breaker and splice it back to the wire that was left on the breaker.
That is a textbook repair of a double-tapped breaker. It's also known as "pigtailing". It is absolutely proper.
Reply With Quote
  #4  
Old 4/18/07, 6:35 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double Tapped Breaker

Toby,

What the electrician did was create a pigtail from the (2) circuits that were sharing that breaker...and now simply have a single conductor going to the breaker now to remove the double tap issue.

Now....sure it does not remove the fact this breaker is controling (2) different circuits ( as it did before )...or (1) larger one now........but regardless of that nothing against that in the NEC.....the NEC does not tell you DIRECTLY how many things can be on a given circuit......while it gives us guidelines and so on and we can do the MATH to come to a conclussion.....

What the Electrician did was compliant.....

Oh...I wanted to add this.....in case you all see this be sure that the pigtail itself is equal or exceeds the rating of the conductors it is pigtailed too.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 4/18/07 at 6:38 PM..
Reply With Quote
  #5  
Old 4/18/07, 6:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double Tapped Breaker

Sorry marc......I was typing while you were answering....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 4/18/07, 6:38 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker

Quote:
Originally Posted by pabernathy
Sorry marc......I was typing while you were answering....
No worries. I certainly don't mind explaining things to people 12 different ways, as long as one gets through. The more, the merrier.
Reply With Quote
  #7  
Old 4/18/07, 6:46 PM
tjohnson3 tjohnson3 is offline
InterNACHI Member
 
Join Date: May 2005
Location: Simpsonville, SC
Posts: 5
Default Re: Double Tapped Breaker

Thanks Paul and Marc,

I knew you could do this if the wires were cut short but not with two different circuits. I'm glad you got back to me before I put my foot in my mouth.

Thanks,


Toby
Reply With Quote
  #8  
Old 4/18/07, 7:45 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Double Tapped Breaker

Quote:
Originally Posted by bkelly2
You can find the code in the NEC.
The Elecrician is correct
I guess he wanted a wordier response.
Reply With Quote
  #9  
Old 4/20/07, 10:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Double Tapped Breaker

Quote:
Originally Posted by bkelly2
I guess he wanted a wordier response.

and YOU know I am
Quote:
WORDIER
in nature.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double pole breaker, metal showing between sections lfoster Electrical Inspections 2 9/6/07 1:25 PM
Double pole breaker with one wire. abolt Electrical Inspections 5 5/1/07 2:47 PM
Double Tapping a Circuit Breaker Skip Erwin Electrical Inspections 4 2/17/07 8:15 PM
Double tapped GFCI breaker sspradling Electrical Inspections 6 12/9/06 11:51 AM


All times are GMT -4. The time now is 11:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts