Default Double-tapped Doorbell wiring

If this double-tap arrangement is wrong, and it can't be right to use stranded and solid wire under one screw, can it?
Could this be fixed with a pigtail and a wire nut? How is this done professionally?

(Yes, this is a Canadian Federal Pioneer panel, fairly new.)

John Kogel
www.allsafehome.ca

Last edited by jkogel; 1/22/09 at 12:20 AM..
Reply With Quote
  #2  
Old 5/19/08, 9:21 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Double-tapped Doorbell wiring

Professionally you would install a separate breaker.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 5/20/08, 12:50 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-tapped Doorbell wiring

As far as I know, Federal Pioneer breakers are still rated for only one conductor under the breaker's terminal. What you have pictured is non-compliant, in my professional opinion. I do disagree, however, that the corrective measure is to dedicate a circuit to the chime transformer. That would be absurd, or wasteful at least. The real corrective action normally involves pigtailing a single conductor to the breaker and making a wirenut splice in the panel. Oops! Sorry. Canada here.... a 'marette' splice.
Reply With Quote
  #4  
Old 5/20/08, 1:44 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-tapped Doorbell wiring

Quote:
Originally Posted by Marc D. Shunk
The real corrective action normally involves pigtailing a single conductor to the breaker and making a wirenut splice in the panel. Oops! Sorry. Canada here.... a 'marette' splice.
Tres bien, Marc. Les marette s'appelle "wire-nuts" aussi.

My step-dad gave me a whole box of old timer "marettes" that were threaded brass rings with setscrews and plastic caps that screwed down over them, boy what a pain to wire a house with those! The electrician had a good laugh when he came to install the service.

I can think of another way to install the tranformer - to attach it to a handy junction box in the garage or the attic. Easier to replace that way.
Reply With Quote
  #5  
Old 5/20/08, 10:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-tapped Doorbell wiring

Quote:
Originally Posted by jkogel
I can think of another way to install the tranformer - to attach it to a handy junction box in the garage or the attic. Easier to replace that way.
Actually, if you see a chime transformer in the attic, chances are pretty good you're looking at an improperly installed chime transformer. While it has not always been the case, for the last 10-15 years they've had a maximum ambient temperature limitation, with a notation in the instructions to not install them in the attic. I recently finished rewiring an apartment building, and there was no good place in the tenant space to put each chime transformer. I ended up mounting each one on the end of the 2 foot fluorescent strip light that was mounted inside each entry hall closet, above the door header. Pretty much hidden that way.
Reply With Quote
  #6  
Old 5/21/08, 1:22 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-tapped Doorbell wiring

Quote:
Originally Posted by Marc D. Shunk
Actually, if you see a chime transformer in the attic, chances are pretty good you're looking at an improperly installed chime transformer. While it has not always been the case, for the last 10-15 years they've had a maximum ambient temperature limitation, with a notation in the instructions to not install them in the attic. I recently finished rewiring an apartment building, and there was no good place in the tenant space to put each chime transformer. I ended up mounting each one on the end of the 2 foot fluorescent strip light that was mounted inside each entry hall closet, above the door header. Pretty much hidden that way.

Splices and Taps.
No unnecessary splices or taps shall be made within or on a luminaire.


FPN: For approved means of making connections, see 110.14.
Reply With Quote
  #7  
Old 5/21/08, 8:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double-tapped Doorbell wiring

Quote:
Originally Posted by jtedesco1

Splices and Taps.
No unnecessary splices or taps shall be made within or on a luminaire.


FPN: For approved means of making connections, see 110.14.
This one was necessary. It was determined by me that it was necessary in order to make the chime transformer mounted on the end of the strip light function. In much the same manner that some luminaires contain the option to remove a 1" square knockout to install a receptacle or a small round knockout to install a canopy switch. Those connections are necessary too. That code section is so vague that it has no teeth to use for enforcement.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM
Double tapped GFCI breaker sspradling Electrical Inspections 6 12/9/06 10:51 AM
Doorbell transformer double tap bsmith Electrical Inspections 11 4/17/06 12:48 PM


All times are GMT -4. The time now is 8:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts