I found this in an old home yesterday, the panel appears to be a fairly new 200AMP. There are smaller wires installed with the main lugs. The house has 4 different sub-panels, I would guess these go to one of those panels, not that it would make it any more correct.
I believe it to be an incorrect installation, but wanted to see what you guys said. The main panel also has about 6 or 7 free spaces left. Sorry there's no picture, I am having trouble with the upload. I will try again. Thanks, Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
|||
|
|||
|
It's more of a danger to tap the main service lugs because there is no protection between the tap and sub-panel.
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#4
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#5
|
||||
|
||||
|
For some reason, I can't imagine how they got the smaller wires into the mains without getting zapped. Safety thing at any rate that deserves some mention.
|
|
#6
|
||||
|
||||
|
|
|
#7
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Especailly if you have copper and aluminum together
|
|
#8
|
||||
|
||||
|
|
|
#9
|
||||
|
||||
|
The NEC has stated this for MANY years...here is a snippet:
"Terminals for more than one conductor and terminals
used to connect aluminum shall be so identified." The main lug of a service panelboard is rated for a single conductor.....if rated for multiple conductors it MUST say so. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#10
|
|||
|
|||
|
Quote:
Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double tap at main lugs | gmathias | Electrical Inspections | 4 | 8/8/07 8:20 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 10:04 AM |
| Main panel double tap | dmccauley | Electrical Inspections | 20 | 1/25/07 6:31 PM |
| Double tapped GFCI breaker | sspradling | Electrical Inspections | 6 | 12/9/06 11:51 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |