I found a 20 amp breaker with a single 12ga. wire about 4 inches long connected to two 14ga. wires with wire nuts branching out to their individual circuits. Any feedback? Thanks
Will R. Stafford Promised Land Construction & Home Inspection Home Inspector from Wilmington to Jacksonville NC and surrounding areas. www.plchomeinspection.com Jacksonville Home Inspector Wilmington Home Inspector |
| Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Quote:
that should be a 15 amp breaker Will....imo |
|
#3
|
||||
|
||||
|
That would not be considered a "double tap," in fact, if the breaker was sized appropriately (which it is not), it's perfectly acceptable.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Quote:
And like Jeff sadi, it's fine (provided the breaker is right szie) Owl Home Inspections Rick Maday Itasca, IL Home Inspector Serving all Chicago Suburbs Schaumburg Home Inspector Naperville Home Inspector Lake County Home Inspector
|
|
#5
|
||||
|
||||
|
Correct-a-mundo
|
|
#6
|
||||
|
||||
|
Thanks guys
Will R. Stafford Promised Land Construction & Home Inspection Home Inspector from Wilmington to Jacksonville NC and surrounding areas. www.plchomeinspection.com Jacksonville Home Inspector Wilmington Home Inspector |
|
#7
|
||||
|
||||
|
Quote:
So the real issue here is not the pigtail....it is what the pigtail connects to Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
|||
|
|||
|
This is a method some people use to get around the fact that the breaker allows only one conductor. The concept i sperfectly legal. However, the comments about the breaker size are, of course, correct.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double tapped breaker | shand | General Inspection Discussion | 9 | 6/7/09 2:50 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| What's this video worth? | jtedesco1 | Education | 5 | 4/18/08 10:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical | 0 | 7/2/07 1:35 PM |
| Double Tapped Breaker | tjohnson3 | Electrical | 8 | 4/20/07 10:04 AM |