Default double tapped with wire nuts

I found a 20 amp breaker with a single 12ga. wire about 4 inches long connected to two 14ga. wires with wire nuts branching out to their individual circuits. Any feedback? Thanks



Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America)
  #2  
Old 6/23/09, 1:10 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: double tapped with wire nuts

Quote:
Originally Posted by wstafford View Post
I found a 20 amp breaker with a single 12ga. wire about 4 inches long connected to two 14ga. wires with wire nuts branching out to their individual circuits. Any feedback? Thanks

that should be a 15 amp breaker Will....imo



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 6/23/09, 1:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: double tapped with wire nuts

That would not be considered a "double tap," in fact, if the breaker was sized appropriately (which it is not), it's perfectly acceptable.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 6/23/09, 2:00 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: double tapped with wire nuts

Quote:
Originally Posted by jpope View Post
That would not be considered a "double tap," in fact, if the breaker was sized appropriately (which it is not), it's perfectly acceptable.
It would be considered a "pig-tail".
And like Jeff sadi, it's fine (provided the breaker is right szie)



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #5  
Old 6/23/09, 2:43 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: double tapped with wire nuts

Correct-a-mundo
Reply With Quote
  #6  
Old 6/23/09, 3:51 PM
Will R. Stafford's Avatar
Will R. Stafford Will R. Stafford is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Holly Ridge, NC
Posts: 8
Default Re: double tapped with wire nuts

Thanks guys



Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
  #7  
Old 6/23/09, 11:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: double tapped with wire nuts

Quote:
Originally Posted by wstafford View Post
I found a 20 amp breaker with a single 12ga. wire about 4 inches long connected to two 14ga. wires with wire nuts branching out to their individual circuits. Any feedback? Thanks
Agreed it is not a double tap....However, lets not over look the fact it is (2) 14 awgs technically on a 20A breaker with no additional details. so if you are asking if it is a double tap...no...if you are asking if the method of installation is correct in your example....NO.......as others have said recommend to them to change the 20A breaker to a 15A breaker.

So the real issue here is not the pigtail....it is what the pigtail connects to



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 6/24/09, 10:02 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: double tapped with wire nuts

This is a method some people use to get around the fact that the breaker allows only one conductor. The concept i sperfectly legal. However, the comments about the breaker size are, of course, correct.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double tapped breaker shand General Inspection Discussion 9 6/7/09 2:50 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM


All times are GMT -4. The time now is 2:54 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts