Default Of double-tapping and subpanels

Hey guys I've got a question.

Regarding the first picture. Would this still be called double-tapping (using a lug instead of a breaker)? Or does it have another name?

Regarding the second picture. Is this what is meant when a subpanel has a white neutral bonded to enclosure and grounds?

Thanks in advance.
Bruce
Attached Thumbnails
double-tapping-and-subpanels-flore-insp-041.jpg   double-tapping-and-subpanels-flore-insp-055.jpg  
Reply With Quote
  #2  
Old 7/23/07, 5:43 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Of double-tapping and subpanels

1. Yes, 'double tapping' can be used as a term here.

2. Don't know if there is a specific term, but I describe it as "non-isolation of grounded conductors from ground (bonding) system"

Now that I quickly, and humbly, answered your questions here are mine.

Photo 1:
- Under the same lug, are they different conductor material? Al and Cu?

Photo 2:
- Did you call out improper cable connectors? (cables coming through knockouts)
- Did you actually see a bonding strap/screw on that neutral bar?
- Feeder appears coming through a conduit, is the locking ring properly sized?

tom
Reply With Quote
  #3  
Old 7/23/07, 5:57 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Of double-tapping and subpanels

Most inspectors agree that the term "double lugging" fits this condition better since it is a lug involved and not a breaker or terminal screw.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 7/23/07, 6:00 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Of double-tapping and subpanels

Quote:
Originally Posted by tdietrich1
Photo 1:
- Under the same lug, are they different conductor material? Al and Cu?

Photo 2:
- Did you call out improper cable connectors? (cables coming through knockouts)
- Did you actually see a bonding strap/screw on that neutral bar?
- Feeder appears coming through a conduit, is the locking ring properly sized?

tom
I'm glad you asked that b/c I was so wondering about the tap, I didn't look. Fortunately I have other photos that show the sec was copper. Thank you very much for asking!

photo 2:
Yes on the knockouts, but the bonding strap/screw is my question too. I am weak on this. So should the bonding strap be (or not) connecting the buss bar to the enclosure -- is that what is meant for this subpanel rule? Or is it the white neutral and circuit grounding conductors going into the same bar the problem. Obviously there is no where else for them to go, but this subpanel thing is blowing me away. I don't understand it. I've read the NEC stuff and whew... I need plane inglush.

I think that locking ring was just hanging there. It appears there is another smaller one behind it.

Thanks
Bruce
Reply With Quote
  #5  
Old 7/23/07, 6:11 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Of double-tapping and subpanels

I should mention the entire home is not grounded. Actually a few outlets did read that they had a ground but most did not.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #6  
Old 7/23/07, 6:26 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Of double-tapping and subpanels

Quote:
Originally Posted by bking
Most inspectors agree that the term "double lugging" fits this condition better
Understood.

When speaking to people, most people understand what 'tapping' off something means. So I use this. I don't want to have to explain what 'lugging' is. Too lazy.

tom
Reply With Quote
  #7  
Old 7/23/07, 10:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Of double-tapping and subpanels

Quote:
Originally Posted by bthompson1
Obviously there is no where else for them to go, but this subpanel thing is blowing me away. I don't understand it. I've read the NEC stuff and whew... I need plane inglush.
Thanks
Bruce
Only a phone call away my friend......only a phone call away to anyone in a JAM and needs something explained to them.....

BETTER YET......come over and post all those electrical questions anytime you need at www.theelectricalguru.com as well...We only deal in electrical questions over there...so if you end up with a REAL tough one....visit their also.



Paul W. Abernathy

Last edited by pabernathy; 7/23/07 at 10:35 PM..
Reply With Quote
  #8  
Old 7/25/07, 12:59 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Of double-tapping and subpanels

Quote:
Originally Posted by bthompson1
Obviously there is no where else for them to go, but this subpanel thing is blowing me away. I don't understand it. I've read the NEC stuff and whew... I need plane inglush.
Bruce,

Don't feel bad about not understanding grounding and bonding of panels. I've been teaching apprentices, journeymen, and electrical contractors for many years. You might be surprised to know that even many experienced master electricians and electrical contractors do not understand the rules for and bonding sub-panels. There are some instances where a sub panel can be grounded the same as it would be if it were the main panel on a separately derived system.

The NEC is not a design guide. It is a set of rules. I would not recommend trying to learn from the NEC. There are many good books available but my all time favorite is "Practical Electrical Wiring" by H.P. Richter. I'm not much involved with apprentices anymore so I don't know if it is still being published but, that was always the first book I'd have them read.

The important thing to know is that even though most subpanels are required to have the grounded and grounding conductors isolated from one another, that is not always the case. So, be careful how you report it to your client. Don't list it as being a deficiency unless you are sure. If you are not sure, recommend evaluation by a qualified electrician.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #9  
Old 7/25/07, 3:22 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Of double-tapping and subpanels

Quote:
Originally Posted by gwells
Bruce,

Don't feel bad about not understanding grounding and bonding of panels. I've been teaching apprentices, journeymen, and electrical contractors for many years. You might be surprised to know that even many experienced master electricians and electrical contractors do not understand the rules for and bonding sub-panels. There are some instances where a sub panel can be grounded the same as it would be if it were the main panel on a separately derived system.

The NEC is not a design guide. It is a set of rules. I would not recommend trying to learn from the NEC. There are many good books available but my all time favorite is "Practical Electrical Wiring" by H.P. Richter. I'm not much involved with apprentices anymore so I don't know if it is still being published but, that was always the first book I'd have them read.

The important thing to know is that even though most subpanels are required to have the grounded and grounding conductors isolated from one another, that is not always the case. So, be careful how you report it to your client. Don't list it as being a deficiency unless you are sure. If you are not sure, recommend evaluation by a qualified electrician.
Thank you for the advice. I'll try to find that book. Also Paul A. has offered some assistance.

Once again, thanks to all you NACHOs

Bruce
Reply With Quote
  #10  
Old 7/25/07, 6:44 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Of double-tapping and subpanels

Along with the missing connectors that someone has already pointed out, it looks like a flexible type cord is being used instead of a listed Class 3 wiring method.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On