Default Double tapping main

Is it ever ok to double tap the main lug in a panel. I alway believed this was never allowed. I have a sellers electrician telling me it is ok. something about a 35 foot rule and something about crimping? The tap goes to the AC disconnect.

Any help would be appreciated.

Thanks



Steve Rinner
GLH Home Inspections
Norwalk, Ohio
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/13/10, 2:45 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Double tapping main

Have the seller's electrician refer you to the local code that allows it.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 8/13/10, 3:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Double tapping main

Quote:
Originally Posted by srinner View Post
The tap goes to the AC disconnect.
Very unlikely that this is a proper connection. Do you have any puctures?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 8/13/10, 7:13 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Double tapping main

I know someone who had a meter panel burn up due to loose double taps. The power company came out and said "not our problem, not our box, call an electrican".

She had it fixed by an electrician, the bill was quite high, they had to make a few trips, a cable was too short, it was below 15 degrees etc etc.

The owner ended up filing a complaint with the power company and getting reimbursed.
Here is why they had to pay:
1. Your name is on the box.
2. You put the anti-tamper tag on it so you must have approved the wiring.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 8/13/10, 11:43 PM
Steve A. Rinner Steve A. Rinner is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Norwalk, OH
Posts: 60
Default Re: Double tapping main

photo. hope this helps
Attached Thumbnails
double-tapping-main-elecpandbl26.jpg  



Steve Rinner
GLH Home Inspections
Norwalk, Ohio
Reply With Quote
  #6  
Old 8/14/10, 6:09 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tapping main

Quote:
Originally Posted by srinner View Post
photo. hope this helps

100% violation for using a lug listed for one conductor with two conductors. Also the use of a white conductor as an ungrounded conductor is a violation as well.

Quote:
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
FPN: Many terminations and equipment are marked with a tightening torque.
(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Reply With Quote
  #7  
Old 8/14/10, 9:18 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tapping main

RM has posted the correct cite for this violation.

It is possible to employ the tap rules to do what was asked about. however, this is not the correct way to do it.
Reply With Quote
  #8  
Old 8/14/10, 9:51 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double tapping main

Quote:
Originally Posted by Jim Port View Post
It is possible to employ the tap rules to do what was asked about. however, this is not the correct way to do it.

It would be nice to post a picture employing the tap rule. Do you have one?

If yes, email it to me (whis11 @ charter.net) if your member status doesn't allow picture posting.

Thanks.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 8/14/10, 9:58 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: Double tapping main

I would really like to see that picture as well....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #10  
Old 8/14/10, 1:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tapping main

First it would help to understand that a tap has specific rules and conditions in which they can be used. A tap by definition has its OCP at the end, not where it originates. NEC Article 240.21 will spell these out.

No personal pics but here is one from another HI forum,
Reply With Quote
  #11  
Old 8/14/10, 3:08 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double tapping main

Quote:
Originally Posted by Jim Port View Post
First it would help to understand that a tap has specific rules and conditions in which they can be used. A tap by definition has its OCP at the end, not where it originates. NEC Article 240.21 will spell these out.

No personal pics but here is one from another HI forum,


There is no image, Jim, simply the red "X" box...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #12  
Old 8/14/10, 5:52 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tapping main

Here's a 10' tap rule compliant installation. 400 amp feeder, #6 tap conductors (minimum 10% of feeder ampacity) to 15 amp circuit breaker. The lugs on the bottom accept two conductors (double lugs) in the #6 AWG to 500 kcmil range:

Reply With Quote
  #13  
Old 8/14/10, 7:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double tapping main

Thanks.

Do the lugs at the top, that are hidden, have a similar design accepting two conductors?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/14/10, 7:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double tapping main

Quote:
Originally Posted by lkage View Post
Thanks.

Do the lugs at the top, that are hidden, have a similar design accepting two conductors?
Yes, the load portion of the switch (top lugs) is factory wiring for a dimming system. The bottom portion is the feeder connection.
Reply With Quote
  #15  
Old 8/15/10, 12:17 AM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is online now
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: Double tapping main

Nice pictures. Thanks for posting these.





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEED® Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double Tapping Main Lugs tdomingues Electrical Inspections 1 8/19/09 11:33 PM
Double tap at main lugs gmathias Electrical Inspections 4 8/8/07 7:20 PM
Main panel double tap dmccauley Electrical Inspections 20 1/25/07 5:31 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts