Is it ever ok to double tap the main lug in a panel. I alway believed this was never allowed. I have a sellers electrician telling me it is ok. something about a 35 foot rule and something about crimping? The tap goes to the AC disconnect.
Any help would be appreciated. Thanks |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Have the seller's electrician refer you to the local code that allows it.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
Very unlikely that this is a proper connection. Do you have any puctures?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
I know someone who had a meter panel burn up due to loose double taps. The power company came out and said "not our problem, not our box, call an electrican".
She had it fixed by an electrician, the bill was quite high, they had to make a few trips, a cable was too short, it was below 15 degrees etc etc. The owner ended up filing a complaint with the power company and getting reimbursed. Here is why they had to pay: 1. Your name is on the box. 2. You put the anti-tamper tag on it so you must have approved the wiring. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#5
|
|||
|
|||
|
photo. hope this helps
|
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
100% violation for using a lug listed for one conductor with two conductors. Also the use of a white conductor as an ungrounded conductor is a violation as well. Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
RM has posted the correct cite for this violation.
It is possible to employ the tap rules to do what was asked about. however, this is not the correct way to do it. |
|
#8
|
|||
|
|||
|
Quote:
It would be nice to post a picture employing the tap rule. Do you have one? If yes, email it to me (whis11 @ charter.net) if your member status doesn't allow picture posting. Thanks. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#9
|
||||
|
||||
|
I would really like to see that picture as well....
|
|
#10
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
First it would help to understand that a tap has specific rules and conditions in which they can be used. A tap by definition has its OCP at the end, not where it originates. NEC Article 240.21 will spell these out.
No personal pics but here is one from another HI forum,
|
|
#11
|
|||
|
|||
|
Quote:
There is no image, Jim, simply the red "X" box... InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's a 10' tap rule compliant installation. 400 amp feeder, #6 tap conductors (minimum 10% of feeder ampacity) to 15 amp circuit breaker. The lugs on the bottom accept two conductors (double lugs) in the #6 AWG to 500 kcmil range:
|
|
#13
|
|||
|
|||
|
Thanks.
Do the lugs at the top, that are hidden, have a similar design accepting two conductors? InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, the load portion of the switch (top lugs) is factory wiring for a dimming system. The bottom portion is the feeder connection.
|
|
#15
|
||||
|
||||
|
Nice pictures. Thanks for posting these.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double Tapping Main Lugs | tdomingues | Electrical Inspections | 1 | 8/19/09 11:33 PM |
| Double tap at main lugs | gmathias | Electrical Inspections | 4 | 8/8/07 7:20 PM |
| Main panel double tap | dmccauley | Electrical Inspections | 20 | 1/25/07 5:31 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |