#1
|
||||
|
||||
|
I called out a double tap on a square "D" 100 amp box last week. Today the electrician who was called in to correct it said that there was no problem with this because Square D was the only box allowed to have a double tap on a 40 amp cb for a range and a B/I Dutch oven. I can not find in any of my books where it says this, so before I open my mouth and insert my foot I thought I would ask here first?
Many Happy Inspections, Mark H Roe BeSure Home Inspection Service NACHI05080887 Lancaster, Ohio 43130 InterNachiOhio Chapter President www.besurehomeinspectionservice.com http://www.besurehomeinspectionservice.blogspot.com/ http://www.zoominfo.com/Search/PersonDetail.aspx?PersonID=901109341 besurehomeinspectionservice@gmail.com http://oh.nachi.org/nachiohio/ http://www.columbusohiohomeinspection.com/ Visit this GREAT Real Estate Community http://activerain.com/besurehomeinspectionservice |
|
#2
|
||||
|
||||
|
He is correct. Did the breaker wire connection look like this (see image)?
************************************** Shawn Rowe, CMI HomeFirst Inspection Services, LLC - InfraRed Specialist (Level 1 & Building Science certified) - Code Certified Residential Building Inspector - Certified Master Inspector -- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties -- |
|
#3
|
||||
|
||||
|
I like to go to Home Depot and Lowes on occasion just to walk through the various sections of the store just to see what is out there. There are constantly new items coming out that we as Home Inspectors need to know about. I get to pick them up and handle them without getting my yoyo knocked into my watchpocket unlike inside a live panel or system. Square D has had these brkrs around for years and you will run across them. You can get a real education just by hitting the Home Centers and pilfering thru their shelves. Plus it gets me out of the house and yard work.
"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself." - John Stuart Mill |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have never seen a 40a breaker with the square plate termination, only the hole with the set screw and that type is only rated for one conductor.
|
|
#5
|
||||
|
||||
|
To answer your question, No... But I was able to contact a supplier of Square D and they did say they could do it if the right breaker was used. But when I describe the setup they said it didn't sound right. They recommended that another breaker be added for the other wire. They did state that even if the correct breaker was used. The the for the range and the dutch oven setup, it would really be a strain on the breaker. Thanks for the help and the tips on this question...
Many Happy Inspections, Mark H Roe BeSure Home Inspection Service NACHI05080887 Lancaster, Ohio 43130 InterNachiOhio Chapter President www.besurehomeinspectionservice.com http://www.besurehomeinspectionservice.blogspot.com/ http://www.zoominfo.com/Search/PersonDetail.aspx?PersonID=901109341 besurehomeinspectionservice@gmail.com http://oh.nachi.org/nachiohio/ http://www.columbusohiohomeinspection.com/ Visit this GREAT Real Estate Community http://activerain.com/besurehomeinspectionservice |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
"A strain on the breaker?"
That doesn't even pass the laugh test. |
|
#7
|
||||
|
||||
|
Square D breakers are not the only breakers rated for two conductors, but as Greg implied, I don't think there is a 40 amp breaker with that listing. Generally, it's only the 15 and 20 amp breakers that allow more than one conductor - when listed accordingly.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
SqD 30s can also have the square washer that takes 2 wires. They make both styles in a 30 so have an option when larger wire sizes are used.
|
|
#9
|
|||
|
|||
|
Quite possibly the fellow electrician is confused with 210.19(A)(3) Ex. 1 when he is talking taps...tehhehehe
No, a 40A Sq D breaker is not rated for (2) conductors and no he can't use 210.19(A)(3) for this either....I was just throwing that one in for FUN Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Jeff writes:
Quote:
Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 |
|
#11
|
|||
|
|||
|
Yes ..Mr. G....you are correct as CH and QO are both listed for (2) conductors of the same size....
Paul W. Abernathy |
|
#12
|
|||
|
|||
|
That's why I like this board so well - great questions, and great answers. I haven't seen this yet, so now if I see it in the next 24 hours, I won't have to ask! (More than 24 hours, I'll forget I ever read it...
|
|
#13
|
|||
|
|||
|
andrew thats why we answer the SAME questions...over...and over....and over...and over....and over.....and over....and over............
Paul W. Abernathy |
|
#14
|
|||
|
|||
|
What question?
Kenneth Miller Jordan Hill Home Services,LLC Vice-President Great Lakes - East Chapter 248-398-2438 |
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You boys need a FAQ page
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Interesting Question? | jmckenna1 | Miscellaneous Discussion for Inspectors | 9 | 11/25/07 1:13 PM |
| Double Tap Question | ekartal6 | Electrical Inspections | 6 | 10/22/07 7:30 AM |
| Double Tap Questions | jkogel | Electrical Inspections | 6 | 6/28/07 9:46 PM |
| Double Tapping a Circuit Breaker | Skip Erwin | Electrical Inspections | 4 | 2/17/07 7:15 PM |
| Double Taps... Here we go again | rwand1 | Canadian Inspectors | 12 | 10/28/06 3:55 PM |