Can Square D breakers be double tapped. There is a small lug that appears to be able to handle 2 wires, one on each side of the lug.
|
| Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Some of the newer Square D Homeline breakers can be double tapped.
This is how I tell the difference: Single screw, and compression = Single wire Single screw with compression plate = Double tap (not sure the actual term) http://www.nachi.org/forum/f19/squar...re-size-26314/ In this thread, the wires are installed poorly, but you can see in the photo the crimped plate below the screw. |
|
#3
|
|||
|
|||
|
This is what to look for:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#4
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
The Square D QO and Homline are good for 2 conductors in the 15 and 20 amp sizes.
|
|
#5
|
||||
|
||||
|
Around here (Great Lakes/Upper Midwest), we call them saddle clamps. The terminology for electrical system components is not the same everywhere so they may known by other names elsewhere.
BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
|
#6
|
||||
|
||||
|
Jim what documentation do you have on this......I have been reading online from the square d site and have not found this info yet.....
Thanks "He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
|
#7
|
||||
|
||||
|
Quote:
The term "double-tap" is generally reserved to describe an "improper connection." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
In this photo, from Mark Shunk in that old thread, you can clearly see the wire sizes and connections for the square D breaker:
|
|
#9
|
|||
|
|||
|
and both wires have to be the same gauge. Had a electrician try to tell me the doorbell transformer(16 gauge strained) was ok on that 15 amp circuit with the #14 solid. Ask for his determination in writing, still don't have it.
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#10
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Bruce do you think that's true when you look at the installation graphic on the side of the Square D breaker in the photo? I see #14-#10 as permitted to be both landed on the breaker. Maybe I'm missing something but I don't see any prohibition for different size conductors. |
|
#11
|
||||
|
||||
|
Please Note:
pmassie is a non-member guest and is in no way affiliated with InterNACHI or its members.
Square D single-pole. This breaker is rated for two conductors only, but many are rated for a single conductor only, so this is something to be aware of when inspecting the breaker. Square D and Cutler-Hammer currently manufacture breakers which are UL-listed for this application.
|
|
#12
|
||||
|
||||
|
The label on the Square D breaker states that it is listed for one or two wires.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#13
|
|||
|
|||
|
What about 2 neutral wires under one screw on the ground bar or a neutral and a ground wire together under one screw
|
| Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
While commonly done in the past it was contrary to the UL listing. It has been spelled out now in the NEC so that the infomation is more readily available.
The rule is multiple grounding conductors are typically ok, but check the panel label. Neutrals must not share, nor be grouped with another conductor. |
|
#15
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double Taps in Cutler Hammer Panel | bhartley | Electrical Inspections | 38 | 7/1/09 5:42 AM |
| Neutral/Ground double taps | kmalone | Electrical Inspections | 6 | 4/24/08 5:26 PM |
| Double Taps | rwand1 | Canadian Inspectors | 39 | 3/29/06 7:16 PM |
| Double Taps | psmothers | Electrical Inspections | 3 | 3/9/06 10:04 PM |