| Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera. |
I know that Cutler Hammer allows double taps on low amp breakers. I thought is was allowed if the wire is the same gauge and the breaker has a double clamp to allow the second wire. I am correct?
Thanks! |
| Find an InterNACHI certified Arizona Home Inspector (and anywhere else in North America) |
Those are not allowed...
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
This is what you want to look for:
Thanks! Larry. That type of connection is not present.
The Cutler Hammer breakers that allow two wires are the CH series. You can recognize them instantly by the tan colored handles. They also fasten to the bus differently than the BR series, (which are the ones in your picture) and will only fit a CH series panel. They are Cutler Hammers premium product.
This has got to be a horizontal pic of a vertical connection point.... Square-D has a similar connection.
Looking at Buck's original post, the branch circuits are of the same gage and same type. (both solid conductors and estimating 14 ga). Can't read the fine print. Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowlege will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.4squarehi.com Follow Us on Facebook Follow Us on Linked-In |
Hi,
I have two conductors going to a single lug on a Cutler Hammer BR115 breaker. Therefore, would this be considered a safety issue? Please advise, Steve |
Stephen,
Does it have the "W"- retainer? Insulation is nicked 2 wires above the one in question Wish I could have been more help |
Not sure if they had the W lugs or not. I'll have to take a closer look some of my other photos. I also noticed that the insulation on that one wire was damaged. Do you typically report that as a safety concern as well?
That wire does not look burned. Unless copper is showing through I would not report it.
Bill Siegel Florida Home Inspection Team Inc. |
Be careful when you are calling out a single double tap. This particular tap could be supplying a doorbell transformer (which is low voltage). I see this in 95% of the panels I inspect. If you call these out, you will be wasting your time. |
Lets explain double taps for a second. The HI has to use their own good judgement on this because while it may be a code violation it may not present such a hazard that it gets elevated on a report in a manner that can cause great concern. Yes, it is a violation of the National Electrical Code unless the device is designed to handle it and yes, even if it was allowed they should be of the same conductor sizing.
Now, Eaton ( Cutler Hammer ) indeed does make breakers that are designed to handle two conductors and it does not look like the Square D version being shown here. Typically their version is a "V" pattern that when torqued down will sandwich the conductors in a tight format and those will say on the side that they are rated for (2) two conductors. As you see in the images Schneider ( Square D ) also has devices that are rated for (2) two conductors and will be listed as such on the side. If in the entire electrical inspection you run into a single double tap on a breaker that is not designed for being double tapped, call it out on the report but I would not elevate it beyond the aware status unless it has different size conductors this is being done with, it has conductors rated less than the breaker being double tapped ( except in the allowances of 240.4(G) ) and so on. This is a simple fix for an electrical contractor. Remember, if the breaker is double tapped with (2) 14 AWG conductors onto a 15A breaker the loads is still limited to 15A and if it comes loose the only real issue is the circuit will not function. Yes, it is a violation of the National Electrical Code and the manufactures listings (110.3b) but if this is the only thing you find I would not elevate it to critical status...save yourself alot of grief and recommend it be corrected at some point but most certainly I am a fan of color coding your critical list...this would not be a RED classfication to me....... While I am a codeist.....I am not an alarmist and many HI's need to understand the different when reporting on issues. Now, if the list GROWS.....then you indeed have reported on it and it should be corrected when other issues are corrected. Paul W. Abernathy,CMI,CEI,CEPE NEC® Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
This may sound a bit naive, but do you actually flip the breaker in question and go test the door bell to verify? I've not seen any breaker panels yet (not looked at that many yet either) that call out the door bell as part of the marking in the box. I guess my concern with flipping the breaker would be if there was a receptacle on that same circuit that might have a home PC plugged into it that might be on at the time. Please advise, Steve |
| Electric Panel | dmozzillo | Electrical | 26 | 1/26/09 2:18 PM |
| Cutler Hammer panel with Square D breakers | bhartley | Electrical | 3 | 11/25/08 10:48 PM |
| Sq D 200 amp panel with Cutler Hammer Breaker | lfoster | Electrical | 7 | 6/28/07 11:06 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |