Default Double Trouble

Main and Sub

Last edited by bkelly2; 6/12/09 at 6:48 PM..
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #2  
Old 4/9/09, 6:38 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: Double Trouble

was that one of Edison's earlier residences Brian ?



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 4/10/09, 11:30 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Trouble

Dang I thought it was a triple-tap but it was just a double-tapped double pigtail.
Picky, picky.
Reply With Quote
  #4  
Old 4/12/09, 9:40 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Trouble

Quote:
Originally Posted by jkogel View Post
Dang I thought it was a triple-tap but it was just a double-tapped double pigtail.
Picky, picky.
I wondered how to write it up myself John. I will use that the "next" time I come across it.
Reply With Quote
  #5  
Old 4/13/09, 11:26 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Double Trouble

Inspector Lingo "The Main and Sub panels are out of date, and contain recalled parts. The wiring is unprofessionally installed, and will Likely cause problems in the future. Recommend a licensed electrician evaluate" Translation "This panel is crap, Im not sure what they were drinking that day, but whoever did this was a hack. replace it immediately if not sooner."
Reply With Quote
  #6  
Old 4/13/09, 5:08 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: Double Trouble

Lots of 'classic' deficiencies in both the service and distribution panel depicted........all new inspectors should study these pics.

Thanks for sharing Brian.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #7  
Old 4/13/09, 5:58 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Double Trouble

Quote:
Originally Posted by scoslett View Post
Lots of 'classic' deficiencies in both the service and distribution panel depicted........all new inspectors should study these pics.

Thanks for sharing Brian.
And to be truely educational, Brian could use arrows, text and such to identify each and every defect so the new inspectors actually understand what they are seeing. And to be fair about it, I very rarely see a FP/Stab Lok panel. How 'bout it Brian?

And yes, thanks for sharing!!!
Reply With Quote
  #8  
Old 4/13/09, 10:41 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Trouble

Quote:
Originally Posted by jjonas View Post
And to be truely educational, Brian could use arrows, text and such to identify each and every defect so the new inspectors actually understand what they are seeing. And to be fair about it, I very rarely see a FP/Stab Lok panel. How 'bout it Brian?

And yes, thanks for sharing!!!
I do not see Stab-Lok panels that often either. So when I do, I write, you have Stab-Lok panels and need an electrician.
No Arrows and Text.
Reply With Quote
  #9  
Old 4/14/09, 9:50 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Double Trouble

I wrote up a StabLok panel on a condo 2 weeks ago. The seller found an electrician whose opinion was that it had been working for 30 years without a problem.
He actually wrote that the panel was acceptable and he saw no problems!



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #10  
Old 4/15/09, 12:18 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Double Trouble

I see alot of Federal Pacific Panels with stab lock breakers. They are pretty common here and alot of the electricians will state that they are ok. Just make sure your verbage states that:There are many known problems with the panels and the breakers and to have a electrician further evaluate. If the electrician calls it good it is on them. Not You.
There are so many writeups in both of these panels that a electrician should further evaluate the whole system. There is lots of info on line about them as well as Zinsco Panels.
Reply With Quote
  #11  
Old 4/18/09, 12:40 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Trouble


Last edited by bkelly2; 6/12/09 at 6:48 PM..
Reply With Quote
  #12  
Old 4/18/09, 7:29 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Double Trouble

Quote:
Originally Posted by bkelly2 View Post
Well, at least they have the stove breaker marked.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #13  
Old 4/23/09, 3:02 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,281
Default Re: Double Trouble

Quote:
Originally Posted by mnorthrup View Post
I see alot of Federal Pacific Panels with stab lock breakers. They are pretty common here and alot of the electricians will state that they are ok. Just make sure your verbage states that:There are many known problems with the panels and the breakers and to have a electrician further evaluate. If the electrician calls it good it is on them. Not You.
There are so many writeups in both of these panels that a electrician should further evaluate the whole system. There is lots of info on line about them as well as Zinsco Panels.
How I write FP's up and leave it up to them:
Federal Pacific Stab-Lok® Electrical panels may be unsafe. See www.google.com (Federal Pacific)
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #14  
Old 4/23/09, 3:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Double Trouble

Quote:
Originally Posted by mroberson View Post
Inspector Lingo "The Main and Sub panels are out of date, and contain recalled parts. The wiring is unprofessionally installed, and will Likely cause problems in the future. Recommend a licensed electrician evaluate" Translation "This panel is crap, Im not sure what they were drinking that day, but whoever did this was a hack. replace it immediately if not sooner."
Which parts are recalled?
Reply With Quote
  #15  
Old 4/24/09, 4:22 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Trouble


Last edited by bkelly2; 6/12/09 at 6:48 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double lugged breakers? dbook Electrical Inspections 7 4/30/08 12:35 AM
Double Mast,Double Trouble? belliott Electrical Inspections 4 7/5/07 11:35 PM
Double Tap Questions jkogel Electrical Inspections 6 6/28/07 9:46 PM
Toronto Convention now just $99! gromicko Canadian Inspectors 36 4/3/07 12:22 PM
Double Taps rwand1 Canadian Inspectors 39 3/29/06 7:16 PM


All times are GMT -4. The time now is 8:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts