Default Is this doubled

During our CE this year the instructor told us the if the contact under the screw has a slot on both sides of the screw then the breaker is not double tapped. You agree.
Attached Thumbnails
doubled-doubled.jpg  
Reply With Quote
  #2  
Old 10/16/07, 12:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this doubled

Squre D HOM series breakes are rated for 2 conductors.

See LINK
Reply With Quote
  #3  
Old 10/16/07, 12:29 PM
Kenneth Rentz Kenneth Rentz is offline
InterNACHI Member
 
Join Date: May 2006
Location: Cary, NC
Posts: 61
Default Re: Is this doubled

Thanks. HOM does that stand for homeline or something else? Thanks again Michael.
Reply With Quote
  #4  
Old 10/16/07, 12:31 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this doubled

Quote:
Originally Posted by krentz
Thanks. HOM does that stand for homeline or something else? Thanks again Michael.
Yes
Reply With Quote
  #5  
Old 10/16/07, 2:45 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Is this doubled

you did comment on the over spray right



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 10/16/07, 2:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this doubled

Quote:
Originally Posted by bgraham
you did comment on the over spray right
While there is some overspray it looks very minor and I 'm not sure I would make a big deal out of it or even call it out based on what I see in the pic.

How about one of the "Sparkies" give us an opinion on this?
Reply With Quote
  #7  
Old 10/16/07, 3:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this doubled

hmmm..what comment ya want...

I can't see the bussbar and contact points from the breakers to the buss to I wont comment....does not look excessive to me.



Paul W. Abernathy
Reply With Quote
  #8  
Old 10/16/07, 4:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this doubled

Quote:
Originally Posted by pabernathy
hmmm..what comment ya want...

I can't see the bussbar and contact points from the breakers to the buss to I wont comment....does not look excessive to me.
Hi Paul,

How about your professional opinion.

Does that mean you wouldn't comment on this in a report?

My opinion is that while contamination is not permitted within the panel, it is because of the potential to reduce required spacings between parts of differing potential and affect the characteristics of insulation of conductors and components within the enclosure.

So for the pic in question it becomes a judgment call. Other parts of this panel may or may not show additional contamination and may or may not indicate the need for repair by a qualified electrician.

If in doubt call it out.
Reply With Quote
  #9  
Old 10/16/07, 4:24 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Is this doubled

The overspray is not a big deal in this particular panel. I wouldn't write it up.

As for the double tap at the breaker....If it contains a double style retainer like this...

"Click To Enlarge"
doubled-doubletap_allowed.jpg

it's allowed per the manufacturer.
Reply With Quote
  #10  
Old 10/16/07, 6:38 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this doubled

The SqD QO® and the HOM® both are rated for two conductors [ wires ] on the breaker termation clip [ note this is covered both single and double pole breakers from 15 amp to 30 amp size ] larger size breakers [35 amp and up ] are rated for single wire only

the same thing with the CH [ Clutter-Hammer] the CH series and BR is the same thing too they are listed for two wires unless speficed somewhere else

I dont know about other breaker are listed in the same manner what the SqD and CH have in thier products but i really doubt it.

Merci, Marc
Reply With Quote
  #11  
Old 10/17/07, 10:39 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Is this doubled

Quote:
Originally Posted by Marc Benz
The SqD QO® and the HOM® both are rated for two conductors [ wires ] on the breaker termation clip [ note this is covered both single and double pole breakers from 15 amp to 30 amp size ] larger size breakers [35 amp and up ] are rated for single wire only

the same thing with the CH [ Clutter-Hammer] the CH series and BR is the same thing too they are listed for two wires unless speficed somewhere else

I dont know about other breaker are listed in the same manner what the SqD and CH have in thier products but i really doubt it.

Merci, Marc
Some manufacturers OK this, but some AHJ's don't.

and they wonder why the home owner or buyer gets confused



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 10/18/07, 6:07 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this doubled

Paul:

What's the ruling when you have a legal double tapped 15 amp single breaker regarding total number of outlets protected? In Canada, we are allowed 12 outlets per circuit and I assume that (will find out later today) a double tapped 15 amp breaker will be allowed to protect 12 outlets only.
Reply With Quote
  #13  
Old 10/18/07, 6:26 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Is this doubled

Quote:
Originally Posted by Brian A. MacNeish
Paul:

What's the ruling when you have a legal double tapped 15 amp single breaker regarding total number of outlets protected? In Canada, we are allowed 12 outlets per circuit and I assume that (will find out later today) a double tapped 15 amp breaker will be allowed to protect 12 outlets only.
I believe the US Electrical regulations have downgraded it from 12 outlets per circuit breaker down to 8.

You do have a valid point though. Why legally manufacture a breaker that can accept more than one circuit which can cause an overload if not properly calculated. I would assume that the Electrician who connects two circuits to these specific breakers is doing a simple load calculation.

Ya right....I highly doubt it.
Reply With Quote
  #14  
Old 10/18/07, 11:11 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this doubled

Quote:
Originally Posted by dvalley
I believe the US Electrical regulations have downgraded it from 12 outlets per circuit breaker down to 8.

You do have a valid point though. Why legally manufacture a breaker that can accept more than one circuit which can cause an overload if not properly calculated. I would assume that the Electrician who connects two circuits to these specific breakers is doing a simple load calculation.

Ya right....I highly doubt it.
Not true at all. There is no limit to the number of outlets on a residential circuit in the NEC and more conductors feeding that circuit will reduce the chance of overloading it. The total circuit current is limited by the breaker and if you split that across 2 sets of conductors the generous safety factor built into 240.4(D) will be twice as safe.
Reply With Quote
  #15  
Old 10/18/07, 11:13 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Is this doubled

Quote:
Originally Posted by Greg Fretwell
Not true at all. There is no limit to the number of outlets on a residential circuit in the NEC and more conductors feeding that circuit will reduce the chance of overloading it. The total circuit current is limited by the breaker and if you split that across 2 sets of conductors the generous safety factor built into 240.4(D) will be twice as safe.
That's why you're the Electrician...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
www.InspectorMALL.com doubled in size this year. gromicko Miscellaneous Discussion for Inspectors 0 10/4/06 10:07 AM


All times are GMT -4. The time now is 3:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts