Default Drip loop

Would you note this as a missing drip loop?

Also thanks to Jae for the response to just have an electrician evaluate and to not list all the defects. Saves me about 10-15 minutes today.

This house had more subs than subway!!!

Thanks

I just love when the client brings a toddler that requires me to be a baby sitter.

Now junior get out of that sump pit now!!

Quit messing with my radon monitor.

Last edited by dmacy; 2/26/08 at 2:59 PM..
Reply With Quote
  #2  
Old 3/3/06, 12:08 PM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 526
Default Re: Drip loop

no drip loop and appears to be running down hill toward the mast head

nice panel, unreal!
Reply With Quote
  #3  
Old 3/3/06, 12:47 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 4,168
Default Re: Drip loop



What the....Shirley, you jest!!



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 3/3/06, 1:09 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 744
Default Re: Drip loop

Quote:
Originally Posted by dmacy
Would you note this as a missing drip loop?
Yes ... looks like the anchor for the service drop came out of the brick (just below the wires).

I agree ... nice panels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 3/3/06, 1:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Drip loop

Most certainly note the lack of a drip loop....

lol...I am sure you can handle the write up on these panels...thehehe....nasty...



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.

Last edited by pabernathy; 3/3/06 at 2:21 PM..
Reply With Quote
  #6  
Old 3/3/06, 2:24 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip loop

In addition. The electric company service drop, service point, and service entrance conductors are too close to the window. They must be at least three feet from either side, and the bottom of the window if it is a window that can be opened. When located above, at the top of the window, the SEC's are OK.The point of attachment is also missing.The electric utility company should be notified.
Reply With Quote
  #7  
Old 3/3/06, 2:59 PM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 526
Default Re: Drip loop

Hey Joe,
was your avatar photo taken at the convention? Cause you look like
you have a major sunburn!
or was it opening a bad panel

Carla
Reply With Quote
  #8  
Old 3/3/06, 4:41 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip loop

See what happens when you get Old! Repeat post removed.

Last edited by jtedesco1; 3/3/06 at 5:52 PM..
Reply With Quote
  #9  
Old 3/3/06, 4:42 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip loop

http://www.nachi.org/forum/image.php...7&type=profile

I was in the sun!

I changed the Avatar, which one makes me look like a "young" man?

I am an "OLD MAN" now!! he he he he lolololol

Last edited by jtedesco1; 3/3/06 at 4:45 PM..
Reply With Quote
  #10  
Old 3/3/06, 5:45 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Drip loop

Good point about the 3' clearance joe, I think it would be hard pressed for the POCO to update that however in the sale issue and to be honest with you I don't know when the 3' came into effect...as long as I can remember......good to note for the liability of the HI but in practicle terms I don't see that being changed by POCO because of a HI report.

Alot will hinge ( no pun intended ) on if that window actually opens or not....but as you also might have guessed....I am sure it does open.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #11  
Old 3/3/06, 5:58 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip loop

The change for the most recent 2005 NEC is as follows:

230.9 Clearances on Buildings.
Service conductors and
final spans shall comply with 230.9(A), (B), and (C).


(A) Clearances.
Service conductors installed as open conductors
or multiconductor cable without an overall outer
jacket shall have a clearance of not less than 900 mm (3 ft)
from windows that are designed to be opened, doors, porches,
balconies, ladders, stairs, fire escapes, or similar locations.


Exception: Conductors run above the top level of a window
shall be permitted to be less than the 900-mm (3-ft)
requirement.
(B) Vertical Clearance.
The vertical clearance of final
spans above, or within 900 mm (3 ft) measured horizontally
of, platforms, projections, or surfaces from which they might
be reached shall be maintained in accordance with 230.24(B).


(C) Building Openings.
Overhead service conductors
shall not be installed beneath openings through which materials
may be moved, such as openings in farm and commercial
buildings, and shall not be installed where they
obstruct entrance to these building openings.

Reply With Quote
  #12  
Old 3/3/06, 7:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Drip loop

Thats new construction Joe.....do you have any idea when the 3' clearance from windows came into effect...I remember it being that way as long as I can remember...any idea?



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #13  
Old 3/6/06, 10:04 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip loop

Quote:
Originally Posted by pabernathy
Thats new construction Joe.....do you have any idea when the 3' clearance from windows came into effect...I remember it being that way as long as I can remember...any idea?
It was before 75, the oldest book I have
Reply With Quote
  #14  
Old 3/6/06, 10:14 AM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 4,168
Default Re: Drip loop

[quote=pabernathy]Good point about the 3' clearance joe, I think it would be hard pressed for the POCO to update that however in the sale issue quote]

Actually, as home inspectors we don't concern ourselves so.

We merely point out the fact. If the buyer/seller/anybody wants to take issue with PUCO (Public Utilities Commission of Ohio) that would be their's to do.

If we don't point it out, and something--anything--arises later, we haven't covered ourselves very well.

Somethings are good to know...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Drip legs Scott Schultz Plumbing 7 3/31/07 7:46 AM
Drip Loop chunt1 Electrical 5 1/31/07 6:52 AM
Drip loop? jspringstead Electrical 1 7/5/06 9:25 PM
Lack of aluminum drip edge Brenda Exterior 26 6/16/06 7:28 AM
Loop Vent Charles Bottger Plumbing 22 2/19/06 12:32 AM


All times are GMT -4. The time now is 12:40 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts