I've sen a few like this over the past few weeks. I write them up, but since I've seen a few now I am second guessing my recommendations.
What do you guys think? Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
No good. Just remember this... when it rains, can rainwater run down the conductors and enter the weatherhead? If yes, it's no good. The conductors should have an uphill run before entering the weatherhead.
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#3
|
||||
|
||||
|
Thanks Jeffrey. That's what I was thinking. For some reason I've just run across several of these recently so I wanted to be sure.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
|
#4
|
||||
|
||||
|
Tell the cable company to quit using the electrical mast as a support for their LV runs.
Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Also it looks like those conductors have an insulation type that is not rated for use in sunlight and the outer nylon jacket is coming off.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Drip loop | labstein | Electrical Inspections | 9 | 1/12/11 12:35 PM |
| Drip Loop Neutral Disconnected | pabrioux | Electrical Inspections | 3 | 10/13/08 2:31 PM |
| Drip Loop | chunt1 | Electrical Inspections | 5 | 1/31/07 6:52 AM |
| Drip loop? | jspringstead | Electrical Inspections | 1 | 7/5/06 9:25 PM |