Question Dryer with 3 wire feed and ground to water pipe

In my personal residence if have a dryer in the basement with a 3 wire feed. The neutral in bonded to the dryer frame as it should be under the code at the time. There is also a ground wire run from the back of the dryer to a nearby water pipe. I realized the other day that this puts the water pipe in parallel with the neutral in the feed. I pulled out my trusty clamp on ammeter and put it on the bond to the water pipe and measured 1.6 amps with the dryer running. This would likely be a portion of any unbalance on the two hot legs. So, all that said, is the bond to the water pipe a bad thing or a good thing? Or am I giving everyone a headache and I should go post this at Mike Holt? I realize that a 4 wire feed is what should be there. On my list for future improvements.




Carl Nagy
CENTech Property Inspections LLC
cnagy@oh.nachi.org
Jeromesville, Ohio 44840
419-368-5814

Serving Ashland, Mansfield, Wooster, Akron, Canton and Surrounding Areas
Reply With Quote
  #2  
Old 1/30/10, 12:08 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Dryer with 3 wire feed and ground to water pipe

It is not good, you could have or develop a bad connection at another water pipe bond or something wrong with the neutral going to the dryer somewhere. I would upgrade the whole circuit for the dryer and make sure the water piping was bonded elsewhere as it should be.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 3:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts