Use either the Fluke or a voltage sniffer if no dryer present. If the breaker is tripped off I do not reset to test but note it (and any others) in the report. Find a lot of dryer outlets not secured to anything, just hanging or dangling by the cable and often without a NM clamp. Lots of poor workmanship.
Reply With Quote
  #17  
Old 3/27/06, 11:54 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dryer Outlet Testing?

Or you can use a non-contact ticker and be done with it.... if both sides TICK....you are good enough......once you go into the panel you will also be able to ensure it is connected correctly...but about all you can do.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #18  
Old 3/27/06, 2:08 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Dryer Outlet Testing?

Yep Paul,
That's what I mean by voltage sniffer...I use a Greenlee. It is real sensitive so it begins to chirp without having to get that right on top of something. Comes in handy in the narrow attic spaces where sometimes all you can do is stretch out to check a piece of disconnected NM cable.
Reply With Quote
  #19  
Old 3/27/06, 3:58 PM
Rick A. Harrington's Avatar
Rick A. Harrington Rick A. Harrington is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Pickerington, Oh
Posts: 186
Default Re: Dryer Outlet Testing?

What is the model number of the Fluke that is shown in the picture?

Thanks,



Rick A. Harrington

Patch Independent Home Inspections, LLC
Serving Columbus and Central Ohio
Certified Specialist - Infrared Residential Inspections Advanced
Certified Level 1 Thermographer
Certified Mold Inspector
State of Ohio Licensed Radon Tester


http://www.patchhomeinspections.com
http://www.centralohiohomeinspector.com
http://www.columbusohiohomeinspector.com
http://www.thermalimagescanning.com
Reply With Quote
  #20  
Old 3/27/06, 5:38 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Dryer Outlet Testing?

Quote:
Originally Posted by rharrington
What is the model number of the Fluke that is shown in the picture?

Thanks,
Fluke T3 Voltage and Continuity Tester

http://us.fluke.com/usen/products/Ac...ukeProducts%29

$64.81 (including shipping) at: http://store.yahoo.com/tmt/googlefluke.html



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 3/27/06 at 6:01 PM.. Reason: Wanted to include price
Reply With Quote
  #21  
Old 3/27/06, 9:49 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer Outlet Testing?

Quote:
Originally Posted by Greg Fretwell
A more definititive test would be to check across the hots for 240v. It could be wired wrong and get 120v to ground from both sides.
good point Greg, forgot about that. can you quickly describe a situation to me were both legs will read 120, and not have 240 across the hots? not trying to be a wise ***, but i can't think of it.
Reply With Quote
  #22  
Old 3/27/06, 9:54 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Dryer Outlet Testing?

Is the Fluke tester a sniffer?
Doug where did u get the greenlee sniffer? What about cost?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #23  
Old 3/27/06, 10:36 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Dryer Outlet Testing?

Quote:
Originally Posted by Jay Moge
good point Greg, forgot about that. can you quickly describe a situation to me were both legs will read 120, and not have 240 across the hots? not trying to be a wise ***, but i can't think of it.
I worked for an electrician who had another guy hook up a 220v receptacle to two 110v breakers that were not side-by-side. They were across from each other. Both on the same bus bar in the panel. The receptacle had the same 110v to both sides of the receptacle... he might as well had just connected a jumper from one screw to the other. Both sides had 110v but together it didn't add up to 220v only 110v.

Was that clear enough? It's late for me.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #24  
Old 3/27/06, 10:51 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer Outlet Testing?

Quote:
Originally Posted by jsieg
I worked for an electrician who had another guy hook up a 220v receptacle to two 110v breakers that were not side-by-side. They were across from each other. Both on the same bus bar in the panel. The receptacle had the same 110v to both sides of the receptacle... he might as well had just connected a jumper from one screw to the other. Both sides had 110v but together it didn't add up to 220v only 110v.

Was that clear enough? It's late for me.
yeah that does. voltage ontop of voltage vs. voltage next to voltage. that would double the flow, but not the juice right? like parallel vs. series.
Reply With Quote
  #25  
Old 3/27/06, 10:58 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Dryer Outlet Testing?

Gary,
I got the Greenlee at Home Depot for about $15 if I remember. I have a couple of others that work just fine too, both are made by GB but not as sensitive but about $10 each. The only reason I bought the Greenlee was I was on the way to an inspection and the battery was dead as a doornail in one of the GB's and the other had been loaned out. I never go into a crawlspace or an attic without one. It slips right into a pocket or a fannypack for easy access.
Reply With Quote
  #26  
Old 3/28/06, 12:58 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer Outlet Testing?

You can also get a "same phase" problem if someone uses a piggyback breaker instead of a real 2 pole.The reason this strategy is flawed when trouble shooting is you will see 120v to ground on both sides with one open phase, through the load.
Reply With Quote
  #27  
Old 3/28/06, 1:10 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Dryer Outlet Testing?

NACHI SOP ; Not Required To;
Quote:
A. Insert any tool, probe or device into the main or sub-panels.
This is not a panel but...

There is no "tester" for the dryer circuit. Using a meter is not a requirement. Taking the plug apart is not required.

Do you "have to", I don't think so.
Should you? That would be nice if you feel OK with it.
Reply With Quote
  #28  
Old 3/28/06, 1:31 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer Outlet Testing?

Several years ago I was doing an inspection and found a conditon that is like what you are talking about. All the lights and plugs had power but I could not make any of the 240 volt equipment work. When I measured the voltage between ground and each leg I read 120 volts. I measured between legs and I read zero volts. I measured zero volts across each 240 volt breaker in the panel. What is going on ??? On this particular distribution panel the cover which gives access to the meter base lugs was unsecured (these typically are wired shut so only the power company can access). I looked inside and found that the power company had removed one leg (must have been bad) and installed a jumper between the one good leg and the lug that had the bad leg. The house was only being supplied with 120 volts.
Reply With Quote
  #29  
Old 3/28/06, 1:46 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer Outlet Testing?

One other note: I do not make it a practice to enter this area of any distribution panel, but by the time I decided to do it I had spent a long time on the problem and was probably too anxious to figure it out.
Reply With Quote
  #30  
Old 3/28/06, 8:43 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dryer Outlet Testing?

Greg,

Quote:
You can also get a "same phase" problem if someone uses a piggyback breaker instead of a real 2 pole.The reason this strategy is flawed when trouble shooting is you will see 120v to ground on both sides with one open phase, through the load.
This is why about all they can do is check with a "Sniffer" and then make sure it is done correctly in the panel. I would advise the HI's against doing any ACTUAL testing while doing the inspection other than with a Suretest device or simular and visual observation.

If they start "FLUKING" around they could open themselves of to going beyond the SOP...and then someone saying why in the "FLUKING" did you not "FLUKE" them all.....so to speak.

Guys..keep it general......"SNIFF" if and if you think it is ok to "FLUKE" thats up to you....but thats about all the HI's are expected to do on these circuits.

Translation for the younger kids - FLUKING is the use of a FLUKE meter....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 8 9/9/07 8:02 PM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 8:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 11:26 PM
Testing a dryer outlet acox Electrical Inspections 14 7/27/06 11:51 PM
Dryer Outlet sboyd2 Electrical Inspections 5 5/27/06 1:27 PM


All times are GMT -4. The time now is 6:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts