Default Dueling Suretests

120V circuit to detached garage in conduit from load side panel in house.

My 61-165 indicated an open ground (and a correct ground everywhere else I tested inside the house), when further investigation by others indicated a correct ground I went back and retested with my 61-058, which indicated a correct ground.

Defective 165, or ????
Attached Thumbnails
dueling-suretests-suretest.jpg   dueling-suretests-suretest2.jpg  



Michael Thomas
Paragon Property Services Inc., Evanston (Chicago) IL
http://www.paragoninspects.com
Reply With Quote
Find an InterNACHI certified California Home Inspector (and anywhere else in North America)
  #2  
Old 9/24/09, 12:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Dueling Suretests

The 61-165 is more "sensitive" than others. Many times it will show an "open-ground" condition, when the contact/connection is poor.

Next time, check the ground impedance when you get this reading.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 9/24/09, 2:11 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Dueling Suretests

If you are not sure about a circuit being open ground, you can plug in your tester, then use a voltage indicator on the face plate screw to see if it lights up.


Like this:

dueling-suretests-p9243046.jpg



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #4  
Old 9/24/09, 2:36 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Dueling Suretests

OK, bear with me a bit, I clearly don't understand this as well as I should, and if I don't probably a lot of others don't either.

Jeffery,

Across what two points should I measure the impedance, and what should I expect to find?

Ralph,

What result should I expect from your test technique?

Thanks



Michael Thomas
Paragon Property Services Inc., Evanston (Chicago) IL
http://www.paragoninspects.com
Reply With Quote
  #5  
Old 9/24/09, 6:07 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Dueling Suretests

Quote:
Originally Posted by mthomas2 View Post
Ralph,

What result should I expect from your test technique?

Thanks
If the circuit is grounded, the indicator will not light up. It it isn't grounded the indicator will light up.

You should have one of these indictors to test for reverse polarity on open ground and 2-prong receptacles (the smaller slot should be hot, and the other one is not)

I recommend the fluke indicator. The CG el-cheapo's are next to worthless IMHO.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #6  
Old 9/24/09, 8:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Dueling Suretests

Quote:
Originally Posted by mthomas2 View Post
OK, bear with me a bit, I clearly don't understand this as well as I should, and if I don't probably a lot of others don't either.

Jeffery,

Across what two points should I measure the impedance, and what should I expect to find?

Ralph,

What result should I expect from your test technique?

Thanks
I think Jeff means using the SureTest to check that as it has this setting built in.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 9/24/09, 8:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Dueling Suretests

Quote:
Originally Posted by pabernathy View Post
I think Jeff means using the SureTest to check that as it has this setting built in.
The SureTest has this built into the unit. You can check the resistance of all three conductors up to 3.0 ohms. If your reading is >3, you can be sure the ground is no good, or not present.

A "normal" reading is generally in the range of 0.25 ohms. A reading of 1.0 or greater is too high for the EGC, and may show as an "open-ground" on the initial test cycle of the SureTest.

FWIW - If you test the ground impedance on a circuit that is GFCI protected, the GFCI will (should) trip.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 9/24/09, 8:54 PM
Dave Bush's Avatar
Dave Bush Dave Bush is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Joplin, MO
Posts: 137
Default Re: Dueling Suretests

Jeff/Paul, wasn't there a discussion a couple of years ago about a false open ground with an outlet, typically in the garage, that is directly out of the panel box, or am I making this up?



Dave Bush, CMI
Quality Home Inspections

"Always do what's right, not what's popular"
Reply With Quote
  #9  
Old 9/24/09, 9:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Dueling Suretests

I don't recall that particular discussion Dave, however, there have been several discussions regarding "false-ground" readings with the SureTest.

Basically, the SureTest gives this indication when the resistance is to low between the ground (egc) and the neutral (grounded conductor).

It's common to get this indication when the receptacle is close to the service equipment (where the grounds and neutrals are bonded) or near a distribution panel where the neutrals have been grounded (which we know to be improper).

The indicator is intended to help the inspector identify "bootleg" grounds, where the egc has been "grounded" to the circuit-neutral, rather than grounded at the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 9/24/09 at 9:18 PM..
Reply With Quote
  #10  
Old 9/27/09, 12:11 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 831
Send a message via Skype™ to pbolliger
Default Re: Dueling Suretests

Probably loose conduit at a fitting or corrosion at a fitting. Cuz you know EMT is perfect...Right Paul
Reply With Quote
  #11  
Old 10/3/09, 10:10 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Dueling Suretests

lol....Gotta love those Chicago EMT Lovers....lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 10/6/09, 12:57 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Dueling Suretests

Thanks for the information.



Michael Thomas
Paragon Property Services Inc., Evanston (Chicago) IL
http://www.paragoninspects.com
Reply With Quote
  #13  
Old 10/6/09, 1:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,048
Default Re: Dueling Suretests

Quote:
Originally Posted by pabernathy View Post
lol....Gotta love those Chicago EMT Lovers....lol
It belongs in metal conduit the way G-D intended.

Romex is glorified extension cord.(I am sure Edison and Tesla would agree ,if they had not both died touching Romex).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:52 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts