Default Dueling Suretests

120V circuit to detached garage in conduit from load side panel in house.

My 61-165 indicated an open ground (and a correct ground everywhere else I tested inside the house), when further investigation by others indicated a correct ground I went back and retested with my 61-058, which indicated a correct ground.

Defective 165, or ????
Attached Thumbnails
dueling-suretests-suretest.jpg   dueling-suretests-suretest2.jpg  
Reply With Quote
Find an InterNACHI certified Illinois Home Inspector (and anywhere else in North America)
  #2  
Old 9/24/09, 11:27 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Dueling Suretests

The 61-165 is more "sensitive" than others. Many times it will show an "open-ground" condition, when the contact/connection is poor.

Next time, check the ground impedance when you get this reading.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 9/24/09, 1:11 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dueling Suretests

If you are not sure about a circuit being open ground, you can plug in your tester, then use a voltage indicator on the face plate screw to see if it lights up.


Like this:

dueling-suretests-p9243046.jpg
Reply With Quote
  #4  
Old 9/24/09, 1:36 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dueling Suretests

OK, bear with me a bit, I clearly don't understand this as well as I should, and if I don't probably a lot of others don't either.

Jeffery,

Across what two points should I measure the impedance, and what should I expect to find?

Ralph,

What result should I expect from your test technique?

Thanks
Reply With Quote
  #5  
Old 9/24/09, 5:07 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dueling Suretests

Quote:
Originally Posted by mthomas2 View Post
Ralph,

What result should I expect from your test technique?

Thanks
If the circuit is grounded, the indicator will not light up. It it isn't grounded the indicator will light up.

You should have one of these indictors to test for reverse polarity on open ground and 2-prong receptacles (the smaller slot should be hot, and the other one is not)

I recommend the fluke indicator. The CG el-cheapo's are next to worthless IMHO.
Reply With Quote
  #6  
Old 9/24/09, 7:13 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dueling Suretests

Quote:
Originally Posted by mthomas2 View Post
OK, bear with me a bit, I clearly don't understand this as well as I should, and if I don't probably a lot of others don't either.

Jeffery,

Across what two points should I measure the impedance, and what should I expect to find?

Ralph,

What result should I expect from your test technique?

Thanks
I think Jeff means using the SureTest to check that as it has this setting built in.



Paul W. Abernathy
Reply With Quote
  #7  
Old 9/24/09, 7:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Dueling Suretests

Quote:
Originally Posted by pabernathy View Post
I think Jeff means using the SureTest to check that as it has this setting built in.
The SureTest has this built into the unit. You can check the resistance of all three conductors up to 3.0 ohms. If your reading is >3, you can be sure the ground is no good, or not present.

A "normal" reading is generally in the range of 0.25 ohms. A reading of 1.0 or greater is too high for the EGC, and may show as an "open-ground" on the initial test cycle of the SureTest.

FWIW - If you test the ground impedance on a circuit that is GFCI protected, the GFCI will (should) trip.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 9/24/09, 7:54 PM
Dave Bush's Avatar
Dave Bush Dave Bush is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Joplin, MO
Posts: 185
Default Re: Dueling Suretests

Jeff/Paul, wasn't there a discussion a couple of years ago about a false open ground with an outlet, typically in the garage, that is directly out of the panel box, or am I making this up?



Dave Bush, CMI
Quality Home Inspections
Serving Joplin, Neosho and Southwest Missouri Area
417-850-9820

"Always do what's right, not what's popular"
Reply With Quote
  #9  
Old 9/24/09, 8:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Dueling Suretests

I don't recall that particular discussion Dave, however, there have been several discussions regarding "false-ground" readings with the SureTest.

Basically, the SureTest gives this indication when the resistance is to low between the ground (egc) and the neutral (grounded conductor).

It's common to get this indication when the receptacle is close to the service equipment (where the grounds and neutrals are bonded) or near a distribution panel where the neutrals have been grounded (which we know to be improper).

The indicator is intended to help the inspector identify "bootleg" grounds, where the egc has been "grounded" to the circuit-neutral, rather than grounded at the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 9/24/09 at 8:18 PM..
Reply With Quote
  #10  
Old 9/26/09, 11:11 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Dueling Suretests

Probably loose conduit at a fitting or corrosion at a fitting. Cuz you know EMT is perfect...Right Paul
Reply With Quote
  #11  
Old 10/3/09, 9:10 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Dueling Suretests

lol....Gotta love those Chicago EMT Lovers....lol



Paul W. Abernathy
Reply With Quote
  #12  
Old 10/6/09, 11:57 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dueling Suretests

Thanks for the information.
Reply With Quote
  #13  
Old 10/6/09, 12:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Dueling Suretests

Quote:
Originally Posted by pabernathy View Post
lol....Gotta love those Chicago EMT Lovers....lol
It belongs in metal conduit the way G-D intended.

Romex is glorified extension cord.(I am sure Edison and Tesla would agree ,if they had not both died touching Romex).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts