Default Elecrical outlets

Should elecrical outlets in garages be more than 18 inches OFF a garage floor in new construction?

Thanks!
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 3/24/09, 9:37 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Elecrical outlets

Is this a residential garage or a car repair facility?
Reply With Quote
  #3  
Old 3/24/09, 9:45 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Elecrical outlets

Good idea, and you might want to have a standard disclaimer about it, but the only code I'm aware of is specific to ignition sources of gas appliances.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/24/09, 9:56 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Elecrical outlets

This is a NEW residenatal garage it is not GFCI protected. I found in Carson Dunlop, that outlets in garages should be 18 inches off the floor. I cannot find anything in ICC.
Reply With Quote
  #5  
Old 3/24/09, 10:04 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Elecrical outlets

This is all I can find. You'd think if receptacles were included they would have specifically said so.

M1307.3 Elevation of ignition source. Appliances having an
ignition source shall be elevated such that the source of ignition
is not less than 18 inches (457 mm) above the floor in garages.
For the purpose of this section, rooms or spaces that are not part
of the living space of a dwelling unit and that communicate
with a private garage through openings shall be considered to
be part of the garage.

G2408.2 (305.3) Elevation of ignition source. Equipment and
appliances having an ignition source shall be elevated such that
the source of ignition is not less than 18 inches (457 mm) above
the floor in hazardous locations and public garages, private
garages, repair garages, motor fuel-dispensing facilities and
parking garages. For the purpose of this section, rooms or
spaces that are not part of the living space of a dwelling unit and
that communicate directly with a private garage through openings
shall be considered to be part of the private garage.
Exception: Elevation of the ignition source is not required
for appliances that are listed as flammable vapor ignition
resistant.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 3/24/09 at 10:08 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlets with a label rdrangstveit Electrical Inspections 5 10/16/08 1:20 PM
ungrounded outlets! gmaher Electrical Inspections 29 6/10/07 10:58 PM
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 11:19 AM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 6:58 AM


All times are GMT -4. The time now is 8:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts