Default Re: Electical Code Test

The cables were bundled for about 30 feet from the service panel all the way across the basement.

I did a little more research and picked up Wiring Simplified 42nd Edition and on Page 123 there was mention about not being able to put more than 4 cables through a common set of holes based on NEC 310.15(B)(2)(a) and 240.4(B)(1)



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 3/21/11, 4:08 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electical Code Test

Quote:
Originally Posted by gliebig View Post
The cables were bundled for about 30 feet from the service panel all the way across the basement.

I did a little more research and picked up Wiring Simplified 42nd Edition and on Page 123 there was mention about not being able to put more than 4 cables through a common set of holes based on NEC 310.15(B)(2)(a) and 240.4(B)(1)
Well over 8 CCC's and derating could change your OCPD size. Same would apply to bundling for 30'

http://www.nachi.org/forum/f19/elect...tml#post730737
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 10:48 AM


All times are GMT -4. The time now is 9:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts