Default Electric ceiling heat

Hi Gize . . .
I have an inspection coming up next week which has ceiling mounted radiant electric heat. I assume if it gets warm it is working but beyond that, anything special I should look out for? What is the useful life of a system like that? We don't find many of them here in MI but I have run across a couple.
As always . . . the wisdom of this organization is accepted most graciously.

Best regards
TS
Reply With Quote
  #2  
Old 4/2/08, 5:53 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric ceiling heat

They take a good long time before you'll feel the warm, even with your hand, but an IR gun will help. Yes, as long as they start to get warm, they work.

They're a garbage system, and they always were. Homes with ceiling radiant heat will typically have cracks in them. When the fail, the only repair option short of tearing the ceiling down and starting over, is to install electric baseboard heat.
Reply With Quote
  #3  
Old 4/2/08, 5:54 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric ceiling heat

I can only think of 2 ways to check if this works.

1. spray the ceiling lightly with water from a spray bottle and watch it evaporate when heated. Probably won't happen due to possible staining.

2. Turn the heat on and view with a thermal imager camera.
Reply With Quote
  #4  
Old 4/2/08, 6:01 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Electric ceiling heat

Most everyone would agree that today the easiest way to check these is to use thermal imaging. We have tons of these in the Idaho area, before thermal imaging we just cranked it up waited 15 min and came back and checked it with our laser thermometer.
My dad had the same thing and last year it finally failed he now has a full furnace (finally) after years of telling him this.
Surprisingly enough my dads ceiling was in excellent condition no signs of deterioration, coils just finally failed. Just check the ceiling like you normally would and write it up.

Also NEVER SPRAY A CEILING WITH WATER BAD NEWS



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #5  
Old 4/2/08, 6:02 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: Electric ceiling heat

Quote:
Originally Posted by Marc D. Shunk
They take a good long time before you'll feel the warm, even with your hand, but an IR gun will help. Yes, as long as they start to get warm, they work.

They're a garbage system, and they always were. Homes with ceiling radiant heat will typically have cracks in them. When the fail, the only repair option short of tearing the ceiling down and starting over, is to install electric baseboard heat.
Ditto what Marc said and watch for add-on (not original) penetrations through the ceiling that may have pierced the cables like plant hangers or ceiling lights.

You can usually pick up the thermal signatures between the grids with an IR thermometer but an IR camera is great for seeing them operate instantly!

electric-ceiling-heat-th780014.jpg

electric-ceiling-heat-th780015.jpg

electric-ceiling-heat-th780033.jpg

electric-ceiling-heat-th780041.jpg

these images will give you a good idea of how they can be laid out

Last edited by wwarner; 4/2/08 at 6:20 PM..
Reply With Quote
  #6  
Old 4/2/08, 6:18 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: Electric ceiling heat

I inspected a home in January 2005 with ceiling radiant heat. The floor was over a crawlspace and was uninsulated. The outdoor temperature was 0 degrees.

My face was warm...my feet were cold. My temp gun gave me 123 degrees at the ceiling, and 40 degrees on the carpet.

They are crap for comfort as well as wear-and-tear.
Reply With Quote
  #7  
Old 4/2/08, 6:29 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Electric ceiling heat

Sounds like the main problem with the MO house was the uninsulated crawl space. Any type of heat would look bad in that situation.

Jim King
Reply With Quote
  #8  
Old 4/2/08, 8:57 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric ceiling heat

Quote:
Originally Posted by tspeerstra
Hi Gize . . .
I have an inspection coming up next week which has ceiling mounted radiant electric heat. I assume if it gets warm it is working but beyond that, anything special I should look out for? What is the useful life of a system like that? We don't find many of them here in MI but I have run across a couple.
As always . . . the wisdom of this organization is accepted most graciously.

Best regards
TS
There was another thread just about 2 weeks ago about electric radiant ceiling heat. Was in Electrical or maybe Interior.
Reply With Quote
  #9  
Old 4/2/08, 10:24 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Electric ceiling heat

Cannot help my self the old HVAC comes out in me if I want to know if something is working that I can not physically see, out comes the amp meter check it at the breaker. Geez what did I just say hope Roy doesn't see this post </IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 4/3/08, 1:43 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Electric ceiling heat

About 25% of my inspections have radiant heating in the ceilings. They seem to be prevalent in the neighborhoods here that were build between 1945 and the late 1960s. They actually work quite well, which surprised me because logic and physics tell me that they shouldn't. I always take a temperature reading the ceiling prior to turning the thermostat on. I let them run for one hour and then take a reading again. Usually I find about a 30°F temperature rise.

Contrary to an earlier poster, I have not found the ceilings to be extensively cracked when radiant heating is in use. In fact, I think it's the opposite, possibly because of the extra steps needed to make the ceiling able to handle this type of heating system.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 4/3/08, 5:54 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric ceiling heat

Quote:
Originally Posted by cbottger
Cannot help my self the old HVAC comes out in me if I want to know if something is working that I can not physically see, out comes the amp meter check it at the breaker. Geez what did I just say hope Roy doesn't see this post </IMG></IMG>
Why wouldn't you pull the t'stat from the wall box, check the amps and then calculate the watts installed or working? Thermaray panels sold in the late 1980's had some problems with parallel wired resistive heating wires breaking, reducing the working wattage as time went on.
Reply With Quote
  #12  
Old 4/3/08, 5:57 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric ceiling heat

Quote:
Originally Posted by rray
About 25% of my inspections have radiant heating in the ceilings. They seem to be prevalent in the neighborhoods here that were build between 1945 and the late 1960s. They actually work quite well, which surprised me because logic and physics tell me that they shouldn't. I always take a temperature reading the ceiling prior to turning the thermostat on. I let them run for one hour and then take a reading again. Usually I find about a 30°F temperature rise.

Contrary to an earlier poster, I have not found the ceilings to be extensively cracked when radiant heating is in use. In fact, I think it's the opposite, possibly because of the extra steps needed to make the ceiling able to handle this type of heating system.
Agreed! Except most of the radiant ceiling heat I've seen was installed in the 1970's and 80's.
Reply With Quote
  #13  
Old 4/3/08, 10:58 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Electric ceiling heat

Quote:
Originally Posted by Brian A. MacNeish
Agreed! Except most of the radiant ceiling heat I've seen was installed in the 1970's and 80's.
Yes, I corrected a typo from my VRS and introduced another typo at the same time. That "1960s" in my post should have been "1980s."

About 75% of the radiant heating systems I inspect are no longer working. They were disconnected during the Enron power manipulation fraud of 2000-2001.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 4/3/08, 11:07 PM
GARY L. RUSK GARY L. RUSK is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 143
Default Re: Electric ceiling heat

I have radiant ceiling heat in my home; was installed in 1952 still working. As stated in other posts turn the heat on 30 - 60 minutes us a laser thermometer check the ceiling of each room from end to end and side to side, you may have areas that are no longer functioning.

Gary
http://www.hsspropertyinspection.com/
Reply With Quote
  #15  
Old 4/7/08, 9:23 PM
Thomas E. Speerstra's Avatar
Thomas E. Speerstra Thomas E. Speerstra is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Battle Creek, MI
Posts: 84
Default Re: Electric ceiling heat

Once again the old MB comes through as I knew it would. Thanks to all who offered their two cents worth. I doubt that there will be any surprises here . . . as I figured, it either works or it doesn"t.

Many thanks to all,
TS
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Safety Media Center jtedesco1 Electrical 1 3/15/08 9:18 AM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Radiant Ceiling Heat hhull Interior 6 7/26/07 9:19 AM
Radiant Heat Transfer rmyers1 Structural 0 6/1/06 12:21 AM


All times are GMT -4. The time now is 1:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts