Default Electric panel bonding & grounding

OK, this is Chicago, the land of conduit, this is a condo, with main breaker at meter in close with sub panel with a main breaker in panel, the neutral bus bar on the right side of the panel is floating, the on on the left side is not with a steel strap connection each.
Attached Thumbnails
electric-panel-bonding-and-grounding-100_8894.jpg   electric-panel-bonding-and-grounding-100_8895.jpg   electric-panel-bonding-and-grounding-100_8896.jpg  
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/20/11, 9:01 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric panel bonding & grounding

Does the horizontal bar connect the terminal bar on the right with the one on the left? It should be insulated from the enclosure, is it?
Reply With Quote
  #3  
Old 4/20/11, 9:27 PM
Jeff Merritt Jeff Merritt is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,162
Default Re: Electric panel bonding & grounding

Yes they appear too, the bar runs under the main bus, I am racking my brain to remember if I have ever seen this
Reply With Quote
  #4  
Old 4/21/11, 1:34 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Electric panel bonding & grounding

It doesn't look to me like the left-side terminal bar is properly isolated. It also appears that both terminal bars are bonded by the "strap."

You only lend to confusion when you refer to a disconnect in a sub panel as a "main breaker."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/21/11, 5:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric panel bonding & grounding

Quote:
Originally Posted by jpope View Post
You only lend to confusion when you refer to a disconnect in a sub panel as a "main breaker."
I had to think about this for a minute because your answer seemed obvious at first.

So what would you call that breaker in the subpanel? Panelboards usually come in two versions MLO (main lug only) and MAIN breaker. I would call the breaker at the meter the service disconnect and the breaker in the sub a main breaker.
Reply With Quote
  #6  
Old 4/22/11, 10:03 AM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: Electric panel bonding & grounding

If the neutral is floating like you said, then then neutrals on the left side are in the wrong location. It looks to me that there is a lug on the right side of that ground strap, for a ground wire, if it were run with the other feeder conductors. It looks like they are using the conduit for the equipment ground.
Reply With Quote
  #7  
Old 4/22/11, 10:43 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Electric panel bonding & grounding

Quote:
Originally Posted by Robert Meier View Post
I had to think about this for a minute because your answer seemed obvious at first.

So what would you call that breaker in the subpanel? Panelboards usually come in two versions MLO (main lug only) and MAIN breaker. I would call the breaker at the meter the service disconnect and the breaker in the sub a main breaker.
As an electrician, this stuff is academic to you Robert, and calling this the "main breaker" is quite reasonable. However, for some reason, it seems that many inspectors have a difficult time making the differentiation between "service equipment" and "other equipment."

Using the term "main" when referencing panels or breakers seems to perpetuate this confusion among inspectors, which is why I suggest using the the terms "service" and "other" when referring to equipment/panels and breakers/disconnects.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/28/11, 1:07 AM
Richard L. Overton Richard L. Overton is offline
InterNACHI Member
 
Join Date: Apr 2009
Posts: 16
Default Re: Electric panel bonding & grounding

Seems to me breaker or not, this is a sub panel and the neutral (grounded conductor) should float. White wires should all be on the right and the bonding jumper(flat cooper strap running behind the bus bars) should be removed from the right bus. The left bus would be reserved for ground wires.
Some jurisdictions require main disconnect to be accessible to the condo occupant, hence second "main breaker" in this panel. ITE panel?
Reply With Quote
  #9  
Old 4/28/11, 2:10 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Electric panel bonding & grounding

I would still call it the main breaker to the remote distribution panel.
Looks like they mixed neutral and ground at the sub which is a no no since the box is grounded and also bonded to the neutral bar.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts