For outdoor receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with 426.28. 426.28 Equipment Protection. Ground-fault protection of equipment shall be provided for fixed outdoor electric deicing and snow-melting equipment, except for equipment that employs mineral-insulated, metal-sheathed cable embedded in a noncombustible medium. Section 426-28 requires ground fault protection of equipment for fixed outdoor electric deicing and snow-melting equipment, the trip ratings for these devices are usually in the 30 milliamp and higher range (anything higher than the 6 milliamps for a Class A GFCI device) Last edited by jtedesco1; 2/5/06 at 3:37 PM.. |
Joe. is that to say that, like electric pipe heaters, these items should have there oun dedicated plug that ISN'T gfi, or gfi rated for 30 miliamps?
Jay: Here's some additional information
http://www.ul.com/regulators/ode/0201.pdf http://www.nectec.or.th/courseware/e...its/qo_epd.pdf Last edited by jtedesco1; 2/6/06 at 3:36 AM.. |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 72 | 3/12/08 12:19 AM |