Arrow Electric Snow Melting or Deicing Receptacle

For outdoor receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with 426.28.







426.28 Equipment Protection.





Ground-fault protection of equipment shall be provided for fixed outdoor electric deicing and snow-melting equipment, except for equipment that employs mineral-insulated, metal-sheathed cable embedded in a noncombustible medium. Section 426-28 requires ground fault protection of equipment for fixed outdoor electric deicing and snow-melting equipment, the trip ratings for these devices are usually in the 30 milliamp and higher range (anything higher than the 6 milliamps for a Class A GFCI device)






Last edited by jtedesco1; 2/5/06 at 2:37 PM..
Reply With Quote
  #2  
Old 2/5/06, 9:17 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Snow Melting or Deicing Receptacle

Joe. is that to say that, like electric pipe heaters, these items should have there oun dedicated plug that ISN'T gfi, or gfi rated for 30 miliamps?
Reply With Quote
  #3  
Old 2/6/06, 2:20 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Snow Melting or Deicing Receptacle

Jay: Here's some additional information


http://www.ul.com/regulators/ode/0201.pdf

http://www.nectec.or.th/courseware/e...its/qo_epd.pdf

Last edited by jtedesco1; 2/6/06 at 2:36 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM


All times are GMT -4. The time now is 3:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts