Hey Guys-
I'm replacing my gas water heater with an electric one. I was surprised to read from multiple sources, including the manufacturer diagram, to use only a 10/2 conductor and connect the neutral to the 30 amp double-pole breaker to get the 240 volts. And of course, put a piece of black tape around it to indicate its hot. But I thought it was a violation now to use the white conductor as an ungrounded conductor? Kenny Rigler Home Inspections Hays, KS 67601 785-656-0272 |
| Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
How else would you get 240v?
You are identifying the white as an ungrounded conductor by marking it with black tape in the panel. https://www.facebook.com/StateCollegeHomeInspector http://www.centreinspection.com Centre Inspection Services proudly serves the following towns; State College, PA 16801, Bellefonte, PA 16823, Centre Hall, PA 16828, Spring Mills, PA 16875, Millheim, PA 16854, Boalsburg, PA and the surrounding areas. |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
In a cable assembly it is still code compliant to re-identify the white as a hot conductor. In conduit you would need to use the proper colors for the hots.
|
|
#4
|
|||
|
|||
|
With a 10/3 conductor. But there's no neutral connection on the water heater just a ground. So if you use a 10/3 what do you do with the neutral?
Rigler Home Inspections Hays, KS 67601 785-656-0272 |
|
#5
|
|||
|
|||
|
So if running the conductor from the disconnect box to the WH in a conduit, you would need to use 10/3? But again, what do you do with the white neutral since the WH only has 2 hots and a ground?
Rigler Home Inspections Hays, KS 67601 785-656-0272 |
|
#6
|
|||
|
|||
|
Quote:
If you use 10/3 the black and red are the hots, the white or bare is the ground. Simply snip off the excess wire--or pull it all the way out of the cable--or wrap it in a jar of jelly--anything you want to do with it, so long as you have the three wires. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#7
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Using 10-3 would be a waste of materials. It could be used. The white would just be unused. |
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
The bare would be the ground, not the white. Grounding conductors need to follow the color convention required by Article 250.
|
|
#9
|
|||
|
|||
|
I found this on the iNACHI electrical course under the 240 Volt termination section:
"Since adoption of the 1996 NEC, all 240V circuits are required to be 4-conductor assemblies carrying:
Any thoughts on that? Also, why doesn't an electric water heater use a neutral? Rigler Home Inspections Hays, KS 67601 785-656-0272 |
|
#10
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
A straight 240v load like a heat pump, AC compressor or a water heater do not require a neutral so 2 hots and a grounding means are all that is needed. |
|
#11
|
|||
|
|||
|
Thanks Jim. Why don't those appliances (heat pumps, ACs, electric water heaters) utilize a neutral though? How do their uses of electricity differ from other appliances, like a stove, that are 240V but do use a neutral?
Rigler Home Inspections Hays, KS 67601 785-656-0272 |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Because they operate at 240 volts. The neutral would only be needed if something were operating at 120 volts. |
|
#13
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Items like timers, dryer motors and lights are all 120 volt and need the neutral. Water heaters, AC compressors do not have anything that needs a neutral.
|
| Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Kenny you better take the electrical course before Nick sends you an email...!!
"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#15
|
|||
|
|||
|
Quote:
The NACHI course and the other electrical books I've read all indicate that electricity seeks to complete a continuous circuit. Supply through the hot (ungrounded) conductor, to the fixture where it completes a task, and then back through the neutral (grounded) conductor. I'm sorry if it's a dumb question. But again, if 120V fixtures need the neutral path to allow current back to the panel why don't 240V fixtures? Or am I just thinking about it wrong? Rigler Home Inspections Hays, KS 67601 785-656-0272 Last edited by krigler; 8/13/11 at 11:55 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Yea or Nay- Tankless Electric Water Heater | nwagner | Plumbing Inspections | 17 | 11/27/08 11:29 AM |
| Venting an oil-fired water heater | mh718 | Inspecting HVAC Systems | 3 | 11/16/06 9:36 AM |
| Need Help On Chimney Liners | Nick Scibetta | Exterior Inspections | 13 | 1/11/06 9:53 PM |