Hey Guys-

I'm replacing my gas water heater with an electric one. I was surprised to read from multiple sources, including the manufacturer diagram, to use only a 10/2 conductor and connect the neutral to the 30 amp double-pole breaker to get the 240 volts. And of course, put a piece of black tape around it to indicate its hot. But I thought it was a violation now to use the white conductor as an ungrounded conductor?

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/12/11, 3:42 PM
RUSSELL SHUEY's Avatar
RUSSELL SHUEY RUSSELL SHUEY is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Central Pennsylvania
Posts: 229
Default Re: Electric Water Heater Wiring

How else would you get 240v?

You are identifying the white as an ungrounded conductor by marking it with black tape in the panel.




https://www.facebook.com/StateCollegeHomeInspector


http://www.centreinspection.com

Centre Inspection Services proudly serves the following towns; State College, PA 16801, Bellefonte, PA 16823, Centre Hall, PA 16828, Spring Mills, PA 16875, Millheim, PA 16854, Boalsburg, PA and the surrounding areas.
Reply With Quote
  #3  
Old 8/12/11, 3:44 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

In a cable assembly it is still code compliant to re-identify the white as a hot conductor. In conduit you would need to use the proper colors for the hots.
Reply With Quote
  #4  
Old 8/12/11, 4:11 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by rshuey1 View Post
How else would you get 240v?
With a 10/3 conductor. But there's no neutral connection on the water heater just a ground. So if you use a 10/3 what do you do with the neutral?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #5  
Old 8/12/11, 4:16 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by Jim Port View Post
In a cable assembly it is still code compliant to re-identify the white as a hot conductor. In conduit you would need to use the proper colors for the hots.
So if running the conductor from the disconnect box to the WH in a conduit, you would need to use 10/3? But again, what do you do with the white neutral since the WH only has 2 hots and a ground?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #6  
Old 8/12/11, 5:06 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by krigler View Post
So if running the conductor from the disconnect box to the WH in a conduit, you would need to use 10/3? But again, what do you do with the white neutral since the WH only has 2 hots and a ground?
Two hots and a ground in any form (within reason).

If you use 10/3 the black and red are the hots, the white or bare is the ground.

Simply snip off the excess wire--or pull it all the way out of the cable--or wrap it in a jar of jelly--anything you want to do with it, so long as you have the three wires.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 8/12/11, 5:37 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by krigler View Post
So if running the conductor from the disconnect box to the WH in a conduit, you would need to use 10/3? But again, what do you do with the white neutral since the WH only has 2 hots and a ground?
You would just use 2 blacks and a green.

Using 10-3 would be a waste of materials. It could be used. The white would just be unused.
Reply With Quote
  #8  
Old 8/12/11, 5:38 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by jwilliams4 View Post
If you use 10/3 the black and red are the hots, the white or bare is the ground.
The bare would be the ground, not the white. Grounding conductors need to follow the color convention required by Article 250.
Reply With Quote
  #9  
Old 8/12/11, 7:03 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Electric Water Heater Wiring

I found this on the iNACHI electrical course under the 240 Volt termination section:

"Since adoption of the 1996 NEC, all 240V circuits are required to be 4-conductor assemblies carrying:
  • two 120V ungrounded (hot) conductors;
  • one grounded (neutral) conductor; and
  • one equipment grounding conductor."

Any thoughts on that?

Also, why doesn't an electric water heater use a neutral?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #10  
Old 8/12/11, 7:27 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by krigler View Post
I found this on the iNACHI electrical course under the 240 Volt termination section:


"Since adoption of the 1996 NEC, all 240V circuits are required to be 4-conductor assemblies carrying:
  • two 120V ungrounded (hot) conductors;
  • one grounded (neutral) conductor; and
  • one equipment grounding conductor."
Any thoughts on that?

Also, why doesn't an electric water heater use a neutral?
That info is only dealing with circuits used for ranges and dryers that are actually 120/240v loads. It would help if it were clarified that it was talking about a 120/240 circuit.

A straight 240v load like a heat pump, AC compressor or a water heater do not require a neutral so 2 hots and a grounding means are all that is needed.
Reply With Quote
  #11  
Old 8/12/11, 10:56 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Electric Water Heater Wiring

Thanks Jim. Why don't those appliances (heat pumps, ACs, electric water heaters) utilize a neutral though? How do their uses of electricity differ from other appliances, like a stove, that are 240V but do use a neutral?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #12  
Old 8/12/11, 10:59 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by krigler View Post
Thanks Jim. Why don't electric water heaters utilize a neutral though? I'm still having a hard time wrapping my mind around that one.

Because they operate at 240 volts. The neutral would only be needed if something were operating at 120 volts.
Reply With Quote
  #13  
Old 8/12/11, 11:03 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric Water Heater Wiring

Items like timers, dryer motors and lights are all 120 volt and need the neutral. Water heaters, AC compressors do not have anything that needs a neutral.
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/13/11, 1:13 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Electric Water Heater Wiring

Kenny you better take the electrical course before Nick sends you an email...!!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 8/13/11, 9:31 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Electric Water Heater Wiring

Quote:
Originally Posted by dandersen View Post
Kenny you better take the electrical course before Nick sends you an email...!!
Thanks David. That was one of the first courses I took when becoming a member and have referred back to it several times.

The NACHI course and the other electrical books I've read all indicate that electricity seeks to complete a continuous circuit. Supply through the hot (ungrounded) conductor, to the fixture where it completes a task, and then back through the neutral (grounded) conductor.

I'm sorry if it's a dumb question. But again, if 120V fixtures need the neutral path to allow current back to the panel why don't 240V fixtures? Or am I just thinking about it wrong?



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 8/13/11 at 11:55 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Yea or Nay- Tankless Electric Water Heater nwagner Plumbing Inspections 17 11/27/08 11:29 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 9:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts