Default Electrical On Decks

Do you call out the Lack Of any GFCI outlets on a deck ?

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/29/12, 1:39 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: Electrical On Decks

Only if there is an outlet there that is not gfci protected...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 1/29/12, 1:46 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Electrical On Decks

Quote:
Originally Posted by jmckee View Post
Only if there is an outlet there that is not gfci protected...
Yes that is obvious, I am referring to a new deck that was built and there is no outlet. Would you call it out or possibly recommend adding one?

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #4  
Old 1/29/12, 1:55 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: Electrical On Decks

I mention the convenience factor verbally but don't write it's absense in my written report...just what I do...can't speak for others...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 1/29/12, 2:00 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Electrical On Decks

Thanks James..




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #6  
Old 1/29/12, 2:00 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Electrical On Decks

Quote:
Originally Posted by jkeilson View Post
Do you call out the Lack Of any GFCI outlets on a deck ?

Jim

Yes.. I write no plug on rear deck .
To simple I make no recommendations .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 1/29/12, 2:17 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Electrical On Decks

Quote:
Originally Posted by rcooke View Post
Yes.. I write no plug on rear deck .
To simple I make no recommendations .

Thanks Roy, that is what I have been doing, just curious what others do.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #8  
Old 1/29/12, 2:35 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Electrical On Decks

I would mention it. It's now a requirement so if it's new it should be there on older homes it's an upgrade. Here most of the decks are built at the back door so there is already one there.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #9  
Old 1/29/12, 4:03 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Electrical On Decks

I agree with Robert. It is a safety issue most people do not know and even though it is not required I mention the safety issue whenever it is apparent, such as a nice outlet plug right on the inside close to the patio door. It is just too tempting to use as a source for music box, lamp, electric lawnmower ect.
If a plug is there it should be GFCI no questions asked.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 1/29/12, 4:15 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Electrical On Decks

Decks are required to have a outlet by current code.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 1/29/12, 4:20 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Electrical On Decks

Quote:
Originally Posted by mlarson View Post
Decks are required to have a outlet by current code.
Yuppers, hence why I asked.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #12  
Old 1/29/12, 5:05 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Electrical On Decks

Quote:
Originally Posted by jkeilson View Post
Yes that is obvious, I am referring to a new deck that was built and there is no outlet. Would you call it out or possibly recommend adding one?

Jim
You say new Deck 90~% of the deck I inspect are dangerous and need repairs .
How was this one... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #13  
Old 1/29/12, 5:43 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Electrical On Decks

Quote:
Originally Posted by rcooke View Post
You say new Deck 90~% of the deck I inspect are dangerous and need repairs .
How was this one... Roy
Ahh, well this is a fairly new deck , looks around 4-6 years, but never had a permit pulled and it is quite large. It spans the entire length of the home ~125 feet, and no outlet at all.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/29/12, 5:45 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Electrical On Decks

Obviously not built by an Electrician.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #15  
Old 1/29/12, 5:56 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Electrical On Decks

Quote:
Originally Posted by jkeilson View Post
Ahh, well this is a fairly new deck , looks around 4-6 years, but never had a permit pulled and it is quite large. It spans the entire length of the home ~125 feet, and no outlet at all.

Jim
Age has nothing to with it . I have seen 7 done by the builder and every one needed changing .
Every body is an expert and can build a deck just ask them .
I think you would be surprised at all the law suits from bad decks
http://www.deckfailure.com/



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 9:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts