  #31  
Old 1/31/12, 4:09 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

deleted................................

Last edited by Jim Port; 1/31/12 at 5:42 PM.. Reason: exception has been removed
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 1/31/12, 4:34 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

Quote:
Originally Posted by Jim Port View Post
There is an exception listed to 210.50(E)(3) in the 08, that exempts this requirement if less than 20 sq. foot. Using the slider as a gauge I would say that balcony looks like about 3' x 3'. I do not remember this changing in the 2011.
I took another look at the 2011 and the 20 sq ft exception has been removed.

Here's the reason why:

Quote:
2-266 Log #1148 NEC-P02 Final Action: Accept
(210.52(E)(3) Exception)
__________________________________________________ _____________
Submitter: Vince Baclawski, National Electrical Manufacturers Association
(NEMA)
Recommendation: Delete the Exception:
Exception to (3): Balconies, decks, or porches with a usable area of less than
1.86 m2 (20 ft2) are not required to have a receptacle installed.
Substantiation: If a porch, deck or balcony is accessible, the safety of having
a receptacle installed should be provided. There should be no distinction
between sizes of these areas. The code rule intent is to avoid cords from
passing through doorways. There is no less chance that this would occur for
small porches, decks or balconies. These smaller areas will have holiday
lighting and small appliances used there. Please reference Mr. King’s
Explanation of Negative in 2008 ROC 2-230.
KING, D.: I disagree with the Panel that a minimum dimension of 20 sq. ft
should be a condition for this requirement. If a porch, deck or balcony is
accessible and intended for use by occupants of the dwelling than a receptacle
should be required regardless of the minimum dimension. The purpose of this
section is to eliminate the use of cords through doorways to supply electrical
equipment at these locations. Cords passed through doorways are a potential
cause for electrical shock and fire due to damage that can easily occur to the
cord where it passes through the doorway. Acceptance of this Comment will
allow this hazardous condition to continue to exist for porches, decks and
balconies that are less than 20 sq. ft.
Panel Meeting Action: Accept
Number Eligible to Vote: 12
Ballot Results: Affirmative: 11 Negative: 1

Last edited by Robert Meier; 1/31/12 at 4:37 PM.. Reason: Added ROP info
Reply With Quote
  #33  
Old 1/31/12, 4:39 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Electrical On Decks

Good info TY Robert
Reply With Quote
  #34  
Old 1/31/12, 5:41 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

Thanks Robert.
Reply With Quote
  #35  
Old 1/31/12, 8:46 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Electrical On Decks

Quote:
Originally Posted by Robert Meier View Post
Mike I'm curious, why wouldn't it pass? Does a balcony require steps?
Where is the means of egress? That is not a balcony but it is a deck. Under the 2011NEC it would require a receptacle inside the footprint of the deck and an in-use cover.
The ICC building code requires a set of steps leaving from the deck

Even if the building was built under the 2011 NEC I would think that the lack of steps would be a bigger hazard than the lack of a receptacle



Mike Whitt
Contractor/Instructor
Reply With Quote
  #36  
Old 1/31/12, 10:27 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

Quote:
Originally Posted by jwhitt View Post
Where is the means of egress? That is not a balcony but it is a deck.

OK so what differentiates the two?
Reply With Quote
  #37  
Old 1/31/12, 10:33 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Electrical On Decks

Quote:
Originally Posted by jwhitt View Post
Where is the means of egress? That is not a balcony but it is a deck. Under the 2011NEC it would require a receptacle inside the footprint of the deck and an in-use cover.
The ICC building code requires a set of steps leaving from the deck
Means of egress is windows, not in photo.

The deck I posted is a minimum (3'x3') requirement of new construction at any walkout openings above ground level in town it's located at.

I questioned it (deck), thought is was insane. The only entrance is at front of home, or through attached garage. There were several similar in this new development.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #38  
Old 2/1/12, 8:24 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

Quote:
Originally Posted by ccurrins View Post
Means of egress is windows, not in photo.

The deck I posted is a minimum (3'x3') requirement of new construction at any walkout openings above ground level in town it's located at.

I questioned it (deck), thought is was insane. The only entrance is at front of home, or through attached garage. There were several similar in this new development.

So from a building standpoint, and since it has no steps, this is considered a balcony?
Reply With Quote
  #39  
Old 2/1/12, 8:28 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Electrical On Decks

Quote:
Originally Posted by ccurrins View Post
Means of egress is windows, not in photo.

The deck I posted is a minimum (3'x3') requirement of new construction at any walkout openings above ground level in town it's located at.

I questioned it (deck), thought is was insane. The only entrance is at front of home, or through attached garage. There were several similar in this new development.

It took me a while but I did find it in the IRC.

This deck meets the minimum code as long as the front door is 36 inches wide. As crazy as it sounds there only has to be one means of egress on a single family dwelling.

Sorry for my mistake



Mike Whitt
Contractor/Instructor
Reply With Quote
  #40  
Old 2/1/12, 10:54 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

I would like to see where you could install the receptacle on the balcony pictured that is only 3x3.
Reply With Quote
  #41  
Old 2/2/12, 7:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical On Decks

Quote:
Originally Posted by Robert Meier View Post
According to the NEC it's 20 sq feet.
Exceptions gone in the 2011 NEC Edition. Sorry I did not read all the thread but wanted to add that for any inspectors that happen to do code compliance inspections under the 2011 National Electrical Code.



Paul W. Abernathy
Reply With Quote
  #42  
Old 2/2/12, 8:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical On Decks

Quote:
Originally Posted by pabernathy View Post
Sorry I did not read all the thread but wanted to add that for any inspectors that happen to do code compliance inspections under the 2011 National Electrical Code.
Yup we covered that in post #32.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 9:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts