Default Electrical Defect Recognition

There are a number of defect here, please identify them.

Reply With Quote
  #2  
Old 1/13/08, 2:17 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

I see a generator breaker that might not have an interlock, but it might have been riveted on the panel cover.

www.interlockkit.com
Reply With Quote
  #3  
Old 1/13/08, 4:52 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

I am looking at the photo and one thing it puzzle me where is the AFCI breaker ??

second thing this is a clear sight gross volaiation the netural and ground conductors are under one screw which it is a no no.

for the rest of it I can't really comment unless i see the whole box then i can able tell the rest.

but i will echo's on Marc Shunk comment related to interlock for generator breaker.

if i see the breaker cover with interlock then it will be ok as long it is approved for this breaker box with UL label on it not the homemade chessy stuff.

Merci, Marc
Reply With Quote
  #4  
Old 1/13/08, 6:42 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by Marc Benz
I am looking at the photo and one thing it puzzle me where is the AFCI breaker ??Merci, Marc
AFCI's are only required on homes built after January 2002. What year is this house?

It appears that there are three(3) neutrals and gec's tied together under three different breakers. Am I right?

Also, the double lugging of neutrals, as already mentioned.
Reply With Quote
  #5  
Old 1/13/08, 6:48 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Electrical Defect Recognition

Too much sheathing on the sheathed cable in the panel...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 1/13/08, 7:05 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by lkage
Too much sheathing on the sheathed cable in the panel...
Larry,

Those jackets are purposely inserted onto the branch wire and used to identify the branch location. I don't have a problem with those.
Reply With Quote
  #7  
Old 1/13/08, 7:18 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by dvalley
Larry,

Those jackets are purposely inserted onto the branch wire and used to identify the branch location. I don't have a problem with those.
No, David, the other ones on the left side, white romex, going from top to bottom...at least that's what they look like to me.

I'm with ya on the other ones.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 1/13/08, 7:24 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by lkage
No, David, the other ones on the left side, white romex, going from top to bottom...at least that's what they look like to me.

I'm with ya on the other ones.
Ohhh....Ok. I see em.

Good call.
Reply With Quote
  #9  
Old 1/13/08, 10:03 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by lkage
Too much sheathing on the sheathed cable in the panel...
This is not a violation though.
Reply With Quote
  #10  
Old 1/13/08, 10:10 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

The only thing I see is the EXTREMELY dangerous generator backfeed breaker.


I think this is yet ANOTHER thread started by a certain someone to perpetuate the topic of terminating grounded conductors.
I guess the other six or seven threads (and counting) on this topic in the past few days were not enough.

For reference you can go here:
http://www.nachi.org/forum/f19/grounded-conductors-24201/
http://www.nachi.org/forum/f19/defects-international-association-certified-home-inspectors-gallery-archives-24348/
http://www.nachi.org/forum/f19/netural-and-grounds-tie-together-24329/
http://www.nachi.org/forum/f19/minor-grounding-issues-panel-worth-mentioning-9375/
http://www.nachi.org/forum/f19/need-help-main-panel-board-buss-bar-23978/
http://www.nachi.org/forum/f19/new-2002-national-electrical-code-and-existing-rules-being-violated-here-24175/
Reply With Quote
  #11  
Old 1/13/08, 11:02 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by Speedy Petey
The only thing I see is the EXTREMELY dangerous generator backfeed breaker.


I think this is yet ANOTHER thread started by a certain someone to perpetuate the topic of terminating grounded conductors.
I guess the other six or seven threads (and counting) on this topic in the past few days were not enough.

For reference you can go here:
http://www.nachi.org/forum/f19/grounded-conductors-24201/
http://www.nachi.org/forum/f19/defects-international-association-certified-home-inspectors-gallery-archives-24348/
http://www.nachi.org/forum/f19/netural-and-grounds-tie-together-24329/
http://www.nachi.org/forum/f19/minor-grounding-issues-panel-worth-mentioning-9375/
http://www.nachi.org/forum/f19/need-help-main-panel-board-buss-bar-23978/
http://www.nachi.org/forum/f19/new-2002-national-electrical-code-and-existing-rules-being-violated-here-24175/
Peter:

You mean me no doubt, you have a problem with that and want me to shut up?

I call for NACH TV to alllow me, or any other expert to sit and be interviewed and discuss the issues we face daily.

Peter or Speedy start by being less critical and start by discussing some of the issues.

How about this, let's see your vitae or resume first so we can see when you got started and what areas you are most proficient in.

I am best when I meet someone face to face instead of behind the keyboard.
Reply With Quote
  #12  
Old 1/13/08, 11:38 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by jtedesco1
Peter:

You mean me no doubt, you have a problem with that and want me to shut up?

I call for NACH TV to alllow me, or any other expert to sit and be interviewed and discuss the issues we face daily.

Peter or Speedy start by being less critical and start by discussing some of the issues.

How about this, let's see your vitae or resume first so we can see when you got started and what areas you are most proficient in.

I am best when I meet someone face to face instead of behind the keyboard.
I think we do not need to Belittle each other, all have made many great posts.
Some posts do tend to get a little long and add information that is not really required by Home Inspectors .
HIs are generalists and they are not required to dissect each concern .
If its needs repair we write it up and move on .
Our time on the Job is limited and if we spend too much time in one area then another area could suffer.

...Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #13  
Old 1/13/08, 2:17 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

Joe,Thank you for the red box and the interesting, yet profane, comment you left me. Sorry, but I can assure you we will never meet. I know the real you and that's enough for me.I hope you are ok with this. I know it is a hard concept for you to grasp, but the whole world does not have to love and agree with you.
Reply With Quote
  #14  
Old 1/13/08, 2:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by Speedy Petey
Joe,Thank you for the red box and the interesting, yet profane, comment you left me. Sorry, but I can assure you we will never meet. I know the real you and that's enough for me.I hope you are ok with this. I know it is a hard concept for you to grasp, but the whole world does not have to love and agree with you.
So Sorry to hear this I sure wish these things did not Happen.
Please Do not let this interfeer with your posts ,many are extremly helpfull .

Thanks Cookie

Growing old is Mandatory; Growing up is optional



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #15  
Old 1/13/08, 3:46 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Defect Recognition

Quote:
Originally Posted by Speedy Petey
Joe,Thank you for the red box and the interesting, yet profane, comment you left me. Sorry, but I can assure you we will never meet. I know the real you and that's enough for me.I hope you are ok with this. I know it is a hard concept for you to grasp, but the whole world does not have to love and agree with you.
What are you talking about? I did not do any red box?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 3:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts