Exclamation Electrical Guru Question? Breaker lock outs

Mechanically speaking, do breaker throw arms (switch) have to "move" for the breaker to actually trip? I see/ find these new lock outs in new panels lying behind the breaker often and wondered if the breaker will trip if needed because I can't manually switch the breaker off till I lift up (away) the lock out device. Any insight?
Attached Thumbnails
electrical-guru-question-breaker-lock-outs-070821-02-005-2-.jpg.JPG
Views:	302
Size:	48.5 KB
ID:	14347  



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #2  
Old 9/7/07, 12:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Guru Question? Breaker lock outs

Virtually every breaker you will see is "trip free". The handle has nothing to do with the contacts opening
Reply With Quote
  #3  
Old 9/7/07, 1:23 PM
kmiller1 kmiller1 is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Berkley, MI
Posts: 259
Default Re: Electrical Guru Question? Breaker lock outs

The electrical inspector in my city told me when he finaled my addition that I had to put the lockout on the breaker for my electric water heater. His reasoning is that the breaker is out of site of the heater. He told me they were a safety device to prevent someone from just reenergizing the circuit while it's being worked on. According to him, they will be required on all breakers over 30A. as the panels are worked on and on new construction. He said the breaker will still be able to trip. May just be a MI or municiple code, though



Kenneth Miller
Jordan Hill Home Services,LLC
Vice-President Great Lakes - East Chapter
248-398-2438
Reply With Quote
  #4  
Old 9/7/07, 1:32 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Guru Question? Breaker lock outs

That would only be necessary if there was no local disconnect within sight of the equipment (a far better option in any place without documented LoTo procedures)
Reply With Quote
  #5  
Old 9/7/07, 2:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Guru Question? Breaker lock outs

Agree 100% with everything Greg stated ( as usual ).....I will add that the debate is wide spread on IF those lock outs at the breaker are considered " perminent " or not....if you remove the cover that makes it NOT perminent so we will see how the NEC works within that but it is a concern of many because of the way the NEC is written in regards to perminent device.

The magnetic contracts or bi-metal versions work the contact points and for the most part the switch itself is a manual function only....which is why you can have common ties on specfic applications ( best example I would have is multi-circuit...)...tied together to ensure both are turned off...but trip individually.....regardless of the tie....UNLESS of course you get into more detail and deal with a " common trip" tied breaker which explains itself really.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Nice Little Electrical Question...lol pabernathy Electrical Inspections 2 2/4/06 1:31 AM


All times are GMT -4. The time now is 3:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts